<table cellspacing="0" cellpadding="0" border="0" ><tr><td valign="top" style="font: inherit;">Hello Bill,<br><br>I'm curious to know what the array STC DC rating to Fronius inverter AC rating you typically had? Thanks.<br><br>Peter Talmage<br><br>--- On <b>Tue, 5/7/13, William Miller <i>&lt;william@millersolar.com&gt;</i></b> wrote:<br><blockquote style="border-left: 2px solid rgb(16, 16, 255); margin-left: 5px; padding-left: 5px;"><br>From: William Miller &lt;william@millersolar.com&gt;<br>Subject: [RE-wrenches] Enphase / Inverter failures<br>To: "RE-wrenches" &lt;re-wrenches@lists.re-wrenches.org&gt;<br>Date: Tuesday, May 7, 2013, 5:37 PM<br><br><div class="plainMail">BobO:<br><br>I too was hesitant to install micro inverters for the reasons you cite:&nbsp; why should I have to go on a roof to replace electronics? and, should electronic components even be on a roof?<br><br>I am converted.&nbsp; We have had a few failures, but a manageable
 percentage.&nbsp; It does suck to go on the roof and to require two people in most cases, to replace an inverter, but we have managed.&nbsp; I get $150.00 per inverter.&nbsp; Not great, but better than nothing.&nbsp;&nbsp;&nbsp;I add a few dollars to each Enphase install to build up a fund that, added to the manufacturer's reimbursement, covers my costs.&nbsp; Consider this:&nbsp; to replace most 5Kw or above inverters requires two people anyway because of the weight of the inverter.&nbsp; Furthermore, when a 5kw inverter fails you've got to get out there, stat, but when a 215 watt inverter fails, you can put it on your schedule for when you are next in the neighborhood.<br><br>I don't enjoy the PLC interference problems, which are rare. When they have occurred, Enphase provided continuous technical support, including factory evaluation of line filters and enhanced system analysis.&nbsp; Did you know that each Enphase system has a built in spectrum
 analyzer? Tech support can provide a printout of interfering signals to help in troubleshooting.&nbsp; Installing a separate AC load center to accept the AC return breakers helps with solving these problems.&nbsp; I understand that the next release of Enphase inverters will be Wi-fi, eliminating the PLC protocol entirely.&nbsp; When the communication works, (which it does most of the time) it is a very valuable resource.<br><br>Micro inverters have added a degree of flexibility in system design hitherto unavailable:&nbsp; The Enphase has allowed us to retrofit a few older GTBB installations, for example tieing two SR100 modules to one M190 inverter.&nbsp; We have also added a few micro inverters to string inverter systems that needed a few more watts but had no room for expansion either in existing strings into existing inverters, or no room on any wall for more string inverters.<br><br>I would encourage you to try an Enphase installation.&nbsp; I have
 nothing to gain for saying that, I just like the product and I want my fellow wrenches to have all the resources to provide the best design for a given challenge.<br><br>We installed Fronius for awhile, but we had a greater than 300% failure rate (not a typo, every inverter failed at least 3 times).&nbsp; There is not enough reimbursement in the world to compensate for that failure rate.&nbsp; Most Fronius employees have been great to work with but two of them defamed me to an important client, and that has left me feeling less than supportive about Fronius.<br><br>I am curious, what is your failure rate with Fronius inverters?&nbsp; What climactic environment are you in?&nbsp; Do you have coastal influences?<br><br>Sincerely,<br><br>William Miller<br><br>At 01:21 PM 5/7/2013, you wrote:<br>&gt; I'm one of the many installers who still won't touch a micro yet. It's not so much that there were failures early on, it's how companies like Enphase HANDLED
 them. My understanding is that you basically got a replacement inverter and got stuffed for your time and travel.<br><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a ymailto="mailto:RE-wrenches@lists.re-wrenches.org" href="/mc/compose?to=RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Change email address &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></div></blockquote></td></tr></table>