<html>
<body>
Are AC coupled systems with no DC loads exempted from the grounding rules
of DC coupled, battery based systems and the rules of DC grounding?
<br><br>
<br><br>
<blockquote type=cite class=cite cite="">This is from the Sunny Island
Manual:<br>
"External grounding of the negative pole of the batteries is
possible, because the batteries <br>
and the grid side are galvanically isolated within the Sunny Island.
<br>
Dimenssion the cross\u2011section of the protective conductor
sufficiently. Thus you are <br>
ensuring that in the event of a fault the high currents occurring can be
discharged with <br>
an external grounding.<br>
If groounding of the negative pole of the battery is necessary,
assemble this outside of <br>
the Sunny Island. <br>
<br>
As far as I am aware, the NEC code is kind of vague on grounding battery
banks (please correct me if I am wrong), it is more of a AHJ
requirement.<br>
<br>
There is no reference to ground (DC side) inside the SI.<br>
<br>
SMA America, LLC<br>
Steve Jefferson<br>
<i>Supervisor, Service Line<br>
</i>6020 West Oaks Blvd, Suite 300<br>
Rocklin, CA 95765 - 3714<br>
U.S.A.<br>
Tel: +1 916 625 0870<br>
Fax: +1 916 624-2445<br>
Service Line +1 877 697 6283 (Toll Free)<br>
Email: steve.jefferson@sma-america.com<br>
<a href="http://www.sma-america.com/">www.SMA-America.com</a><br>
<br>
This email and any attachments thereto may contain SMA America, LLC
confidential, privileged and private material for the sole use of the
intended recipient. Any review, copying, or distribution of this email
(or any attachments thereto) by others is strictly prohibited. If you are
not the intended recipient, please contact the sender immediately and
permanently delete the original and any copies of this email and any
attachments thereto. Thank you.<br>
<br>
<b>From:</b> re-wrenches-bounces@lists.re-wrenches.org
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of
</b>August Goers<br>
<b>Sent:</b> Wednesday, April 10, 2013 2:13 PM<br>
<b>To:</b> RE-wrenches<br>
<b>Subject:</b> Re: [RE-wrenches] Fuse sizing in battery circuits<br>
<br>
Steve,<br>
<br>
So if we wanted to ground the negative would we literally run a ground
wire to one of the battery terminals? Is there anything in the NEC that
governs this? What are the deciding factors when deciding to ground the
negative or not?<br>
<br>
As a separate note, I've noticed that the negative battery terminals
measure 0 volts to ground on a Sunny Island setup once everything is
connected without any extra grounding added. I thought that there must be
some reference to ground happening in the Sunny Island but apparently I'm
wrong.<br>
<br>
Thanks, August<br>
<br>
<b>From:</b>
<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">
re-wrenches-bounces@lists.re-wrenches.org</a>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] <b>On Behalf Of
</b>Steve Jefferson<br>
<b>Sent:</b> Wednesday, April 10, 2013 9:56 AM<br>
<b>To:</b> RE-wrenches<br>
<b>Subject:</b> Re: [RE-wrenches] Fuse sizing in battery circuits<br>
<br>
If the Batt negative is not bonded to ground, then yes SMA recommends
fusing both Positive and Negative.<br>
<br>
Also, the negative is not bonded to ground internally in the Sunny
Island.<br>
<br>
SMA America, LLC<br>
Steve Jefferson<br>
<i>Supervisor, Service Line<br>
</i>6020 West Oaks Blvd, Suite 300<br>
Rocklin, CA 95765 - 3714<br>
U.S.A.<br>