    Chris<br>
    Yes some charge controllers regulate pretty slow. So if the battery
    goes away on them they can skyrocket in voltage on there battery
    side before they can catch themselves. This may only be for 2-3
    seconds or so but that is all it takes to send an inverter up in
    smoke. <br>
    <br>
    This is also the reason you here people complain of small AGM
    battery banks going over voltage from time to time. These same
    slower controllers will take that same 2-3 seconds to catch
    themselves if a big load is turned off. <br>
    <br>
    Ryan<br>
    <span class="moz-txt-tag">--&nbsp;<br>
    </span>Ryan Stankevitz
    <br>
    Technical Support Manager
    <br>
    MidNite Solar Inc.
    <br>
    <a class="moz-txt-link-abbreviated"
      href="mailto:ryan@midnitesolar.com">ryan@midnitesolar.com</a>
    <br>
    360-403-7207 XT 151
    <br>
    Skype ID ryan.midnite
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/16/2013 10:28 AM, Chris Mason
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAG6C1qmFdnpUs5hr=GY4UCtWU9tOkWyn-Qt-VDAV5mhL3oCUdA@mail.gmail.com"
      type="cite">I want to understand the issue if you don't mind. Are
      you saying that an MPPT charge controller has no voltage limits? I
      would have presumed a CC would know that there is no batteries
      attached.
      <div>From your email, you want a device that will measure the CC
        output voltage, and shut it down if it exceeds a limit. For the
        48V systems I normally install, that would be ...65V?&nbsp;</div>
      <div>It would be trivial to setup an Arduino with a voltage input
        to monitor the CC output voltage. The harder part would be to
        turn off the CC when there was excessive voltage. Unless the CC
        had an Aux input, you would need a contact rated for the DC
        Current. Other than, it's very simple to do.<br>
        <div>
          <div><br>
            <br>
            <div class="gmail_quote">On Fri, Mar 15, 2013 at 11:05 PM,
              Dan Fink <span dir="ltr">&lt;<a moz-do-not-send="true"
                  href="mailto:danbob88@gmail.com" target="_blank">danbob88@gmail.com</a>&gt;</span>
              wrote:<br>
              <blockquote class="gmail_quote" style="margin:0 0 0
                .8ex;border-left:1px #ccc solid;padding-left:1ex">
                This has been happening all too frequently here. We live
                in a big area<br>
                of off grid homes, dozens of systems.<br>
                Lost a customers Trace 2624 this morning; One L-16 in
                older 24v bank<br>
                opened internally. PV array/MPPT control zorched
                inverter as soon as<br>
                the sun came up. First indication of problems last nite
                when customer<br>
                hit microwave to warm up dinner and inverter went crazy.
                This morning<br>
                the bad battery showed 3.2v (yes, I would expect 2 or 4
                also) the rest<br>
                the usual 6+v. Turned on PV array, bad battery
                immediately up to 11v<br>
                (yes, 6v L16).<br>
                <br>
                Somebody needs to build a "battery condom" with big
                stacked diodes on<br>
                a big heat sink or some such solution. A voltage brick
                wall for system<br>
                charging inputs. MPPT PV controllers do NOT protect a
                inverter from<br>
                input overvoltage if all or part of the battery bank
                disappears! And<br>
                last year we saw a nice battery box fire and zorched
                inverters due to<br>
                similar -- dual 48v L16 strings, one cell failed and
                opened, other<br>
                string dumped everything into the bad one, smoke and
                flames. Parallel<br>
                fusing would have stopped that......but not stopped the
                loss of dual<br>
                stacked XW inverters from PV overvoltage.<br>
                <br>
                Or am I missing something here?<br>
                <br>
                Dan Fink,<br>
                Executive Director;<br>
                Otherpower<br>
                Buckville Energy Consulting<br>
                Buckville Publications LLC<br>
                NABCEP / IREC accredited Continuing Education Providers<br>
                970.672.4342<br>
                _______________________________________________<br>
                List sponsored by Home Power magazine<br>
                <br>
                List Address: <a moz-do-not-send="true"
                  href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change email address &amp; settings:<br>
                <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                  target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                <br>
                List rules &amp; etiquette:<br>
                <a moz-do-not-send="true"
                  href="http://www.re-wrenches.org/etiquette.htm"
                  target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out participant bios:<br>
                <a moz-do-not-send="true"
                  href="http://www.members.re-wrenches.org"
                  target="_blank">www.members.re-wrenches.org</a><br>
                <br>
              </blockquote>
            </div>
            <br>
            <br clear="all">
            <div><br>
            </div>
            -- <br>
            Chris Mason
            <div>President, Comet Systems Ltd</div>
            <div><a moz-do-not-send="true"
                href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>
            <div>Cell: 264.235.5670</div>
            <div>Skype: netconcepts</div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>