Hello Wrenches,<br><br>
I had an unexpected glitch in AC coupling a Magnum 4024 PAE
inverter.&nbsp; The system utilizes AGM batteries, which (according to
Concorde tech support) have a very strict upper voltage limit.<br><br>
The relay used to stop the current input from the direct grid tie
inverter, when battery voltage is high, is controlled by a Morningstar
Relay Driver.&nbsp; The relay driver is set to shut off the charge at
28.8 volts.<br><br>
The charger on the Magnum is set to charge the batteries to&nbsp; 28.6
volts.&nbsp; <br><br>
The plan was to be able to charge batteries from the Magnum without
tripping the AC connection between the grid tie inverter to the
grid.&nbsp; The Magnum should charge to 28.6 volts, 0.2 volts below the
relay driver's programmed trigger point. <br><br>
There is one catch to using this approach. The Magnum inverter has a
remote temperature sensor in the battery bank. The relay driver is not
temperature corrected. Therefore, when the batteries are cold, the
charging voltage goes up in the Magnum.&nbsp; This higher voltage trips
the relay controlled by the driver, and disconnects the grid tie inverter
from the grid.&nbsp; <br><br>
I've played with the voltage set points, but the charge voltage on the
Magnum would be too low for good battery maintenance.&nbsp; If these were
liquid electrolyte batteries, I'd crank up the voltage on the relay
driver.&nbsp; Since they are AGM batteries, it doesn't seem like a good
idea to do that. <br><br>
The work around for this at present is to;
<ul>
<li>Charge batteries at night in the winter
<li>No problem is expected in the summer
</ul>The batteries are in an insulated box in a shed connected to the
house. The inside of the battery box has a screened hole that is supposed
to allow heated air into the box.&nbsp; This vent doesn't keep the
batteries warm enough to prevent the problem. <br><br>
Is there a temperature sensitive, voltage controlled relay or diver
available?&nbsp; Has anyone used a temperature bulb with the relay driver
in a way that could solve this problem? Has anyone else come up against
this issue, and if so, what was your solution?<br><br>
Thanks,<br><br>
Drake <br><br>