Gary:<br><br>
I think you are a little confused about the operating modes of the XW
inverter:<br><br>
In the AC Passthru mode, no battery charging occurs.&nbsp; Below is the
passage from the manual that describes this:<br><br>
<i>The AC connected to the AC1 or AC2 input is passing directly through
the Xantrex XW<br>
Series Inverter/Charger to the loads. The batteries are not being charged
in this state.<br><br>
</i>In the normal transfer mode, battery charging does occur.&nbsp; It is
my clear understanding that the Xantrex SW and XW inverters and the
Outback FX and Radian inverters will regulate battery charging so that
the charger circuit uses only excess amperage available.&nbsp; For
example:&nbsp; If the input breaker size is programmed for 60 amps and
there is 60 amps of load, 0 amps of AC will be used for battery
charging.&nbsp; If the load decreases to 50 amps, 10 amps of AC will be
used for battery charging, etc..&nbsp; Therefore, the OCPD does
<u>not</u> need to be sized to accommodate both uses of input
AC.<br><br>
Below is a passage from the XW Operating Manual that describes
this:<br><br>
<i>In addition, the battery charger can reduce its charging current to
the batteries<br>
so the combined charge AC current and total load current does not exceed
the<br>
capacity of the generator or trip its output breakers or fuses.<br><br>
</i>Extending this discussion beyond the current topic (pun intended), we
need to understand what happens if the connected loads exceed the input
breaker rating.&nbsp; Here the game changes.&nbsp; The FX inverter can
not prevent the overload from passing to the input breaker, possibly
tripping it.&nbsp; The SW, XW and Radian inverters can provide
&quot;Generator Support.&quot;&nbsp; Do not confuse Generator Support
with Generator Remote start functions.&nbsp; Generator Support allows the
inverter to sync to, and assist the AC input source in powering
loads.&nbsp; To use the example above:&nbsp; If the load rises to 70
amps, the inverter draws energy from the batteries to provide the last 10
amps. <br><br>
Below is the passage from the XW manual that describes this:<br><br>
<i>AC2 Breaker:&nbsp; Sets the AC2 (Gen) breaker size, based on the size
of the installed AC breaker. The<br>
breaker size must not exceed the capacity of the generator. The Xantrex
XW Series<br>
Inverter/Charger limits the maximum input current to this setting by
derating its charging<br>
current to an equivalent of 80% of the AC breaker size. If the connected
loads exceed the<br>
AC2 breaker setting, the AC breaker trips. The breaker may not trip if
Gen Support is<br>
enabled and Gen Amps is configured not to exceed the generator\u2019s rated
output current.<br><br>
</i>I hope this information is relevant, correct and helpful.<br><br>
Sincerely,<br><br>
William Miller<br><br>
<br><br>
<br>
At 08:24 AM 3/1/2013, you wrote:<br>
<blockquote type=cite class=cite cite>Larry:<br><br>
In the case of the Xantrex XW Series, while in the &quot;AC
Pass-Thru&quot; Mode, the internal transfer switch relay connects the
protected loads directly to the AC1 grid input. The XW internal battery
charger is then activated to recharge the battery bank.<br><br>
The OCPD(s) through which the protected load amps and charging amps are
passing must be sized to accommodate both at the same time.<br><br>
Regards,<br><br>
Gary Willett<br>
Icarus Solar</blockquote></body>