<div dir="ltr"><div><div><div><div><div><div>This is an interesting thread, Wrenches~<br><br></div>May I suggest looking through the opposite end of the telescope? I hasten to add that I have not had suitable clients to try this suggestion, but:<br>


<br></div>Instead of using a &quot;synchronous wound&quot; generator (to which grid tie inverters &gt;might&lt; sync), consider using battery based inverters to establish the AC parameters, then match in an engine generator which is intended for grid tie. <br>


<br></div>Grid-tie engine generators tend to be found in the &quot;combined heat and power&quot; world which includes jolly features such as heat reclamation and long life engines. The Marathon Ecopower is worth a look and also the Freewatt system from ECR...and maybe there are others these days as I haven&#39;t checked up on this for years now. Scaling these &quot;cogeneration&quot; machines down to modest residential size wattages has been a major hangup, it seems. <br>


<br></div>One would need a good way to protect the battery from overcharge, as this is &quot;AC Coupling&quot; with various Murphy possibilities.<br><br></div>The only other obstacle would be political. One would need to convince the &quot;grid tie&quot; generator guys to allow use of their machine in a &quot;synthetic grid&quot; installation. They may be busy enough without having to think about AC coupling into a battery based inverter system.<br>


<br></div>Intrepid researchers are encouraged to report back so we can all learn.<br><div><br>Jolliness,<br><div><div><div><div><div><br clear="all"><div><div>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br>