    <div class="moz-cite-prefix">Funny that the good old SW inverters
      still have features that new inverters haven't topped:&nbsp; the (as
      mentioned) AC current input setting, still the best gen autostart
      menu, dual AC inputs, and excellent reliability.&nbsp; I'm currently
      working on a project with an SW4024 that is 17 years old, and
      still working fine.&nbsp; We're adding batteries, modules, MPPT
      controllers, etc. but the inverter is not on the upgrade list
      right now.<br>
      The SW plus however does not regulate AC input current as well,
      and I've had the same issues with overloading small generators as
      with the Outbacks.&nbsp; Magnums also are hard to set, and I finally
      had to give up using small (under 4 kw) generators with any of the
      newer larger inverters.&nbsp; Small genies seem to only work well with
      old SWs, or small inverters with low charger draw.<br>
      Using a separate Iota charger (as some pointed out) is definitely
      an option, but last time I used one, they were not UL listed or
      set up to wire in a code compliant manor.<br>
      <br>
      Ray Walters<br>
      <br>
      On 1/31/2013 3:13 PM, Allan Sindelar wrote:<br>
    </div>
    <blockquote cite="mid:510AEC92.50906@positiveenergysolar.com"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <div class="moz-cite-prefix">William,<br>
        Yes, that's my understanding. Outback acknowledged this to me
        years ago.<br>
        Allan<br>
        <br>
        <div class="moz-signature">
          <meta http-equiv="content-type" content="text/html;
            charset=ISO-8859-1">
          <title></title>
          <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
          <small><a moz-do-not-send="true"
              href="mailto:Allan@positiveenergysolar.com"><font
                face="Times New Roman, Times, serif" color="#000099"><u>Allan@positiveenergysolar.com</u></font></a></small><font
            face="Times New Roman, Times, serif"><br>
            <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
              Installer<br>
              NABCEP Certified Technical Sales Professional<br>
              New Mexico EE98J Journeyman Electrician<br>
              Founder and Chief Technology Officer<br>
              <b>Positive Energy, Inc.</b><br>
              3209 Richards Lane (note new address)<br>
              Santa Fe, New Mexico 87507<br>
              <b>505 424-1112</b><br>
              <a moz-do-not-send="true"
                href="http://www.positiveenergysolar.com/"
                target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
          <p class="MsoNormal" style="margin-right: 722.25pt;"><span
              style="font-size: 10pt;"><font face="Times New Roman,
                Times, serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                    w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
                style=""><br>
              </b></span></p>
          <span style="font-size: 10pt;"><br>
          </span> </div>
        On 1/29/2013 9:28 PM, William Miller wrote:<br>
      </div>
      <blockquote
        cite="mid:6.0.1.1.2.20130129202714.02f7bea0@millersolar.com"
        type="cite"> Allan:<br>
        <br>
        Could it be that the SW systems are protecting the generator
        with Generator Support, and the Outback inverters are not?<br>
        <br>
        William Miller<br>
        <br>
        <br>
        <br>
        At 07:18 PM 1/29/2013, you wrote:<br>
        <blockquote type="cite" class="cite" cite="">This is going back
          several years...<br>
          <br>
          The Outback VFX series lacks the tight input current
          regulation of the SW series, so the max AC amps in is really
          just a suggestion. In many cases (and especially with these
          small generators) we want to set the max amps in as high as
          possible to minimize charging time and maximize C/rate. Yet a
          surge load can momentarily exceed the max amps setting. <br>
          <br>
          I have observed that the Honda inverter/generators have a
          quite sensitive AC output breaker, that will sometimes trip if
          a surge load (such as a refrigerator) comes on during a charge
          cycle set close to the generator's capacity. This incident was
          specific to a Honda 3000i. In contrast, Yamaha's EF3000iSE
          will lug when overloaded - not good for the generator, but
          also not likely to trip the output breaker.<br>
          <br>
          This is a different issue than was being discussed, but fits
          your question.<br>
          Allan<br>