Al:<br><br>
If I understand this correctly, you are attempting something that should
not be done.&nbsp; Once you combine sources you can not separate
them.&nbsp; How can you control the feed so only half goes into each
fused switch?&nbsp; This defies physics and is faulty design.&nbsp; You
have to run the feeder required.<br><br>
William Miller<br><br>
PS:&nbsp; You did say all feedback is appreciated....<br><br>
Wm<br><br>
<br>
At 02:27 AM 1/26/2013, you wrote:<br>
<blockquote type=cite class=cite cite>Fellow Wrencher's,<br>
I have a project that I will be installing 4 string inverters on a roof
and combining the output into a 3 phase Load center.&nbsp;&nbsp; Once in
the basement I would like to de-combine the output so I can utilize two
available 100A fused switches that are part of the buildings existing
service (Siemens Vacu-Break Fusible Units).&nbsp;&nbsp; I am trying to
avoid running two sets of conduit &amp; conductors or having to upsize
the conductors for # of current carrying conductors in a single
raceway.&nbsp; What off the shelf products are available for de-combining
the AC output I describe?&nbsp;&nbsp;&nbsp;&nbsp; Can I use a junction
box with polaris lugs? <br><br>
All feedback is appreciated.<br><br>
<i>Al Frishman</i><br>
AeonSolar<br><br>