At 12:53 PM 1/16/2013, you wrote:<br>
<blockquote type=cite class=cite cite=""><font size=2>Finally got through
to Outback. They said the GVFX could be wired with a genny line-side of
the inverter in order for the genny to charge the batteries and that this
configuration could potentially cause problems for the genny. The
likelihood of the PV sending power to the generator is extremely small as
the inverter needs to see 5 minutes of perfect power in addition to
sensing a near full battery bank before it will attempt to
&quot;sell&quot; power back to the AC source.</blockquote>
<x-sigsep><p></x-sigsep>
A few years back, in a similar situation, Outback Tech Support told me
that&nbsp; if the inverter tried to sell to the generator, the voltage
would go out of f tolerance and the Outback&nbsp; GVFX would disconnect. 
</font></body>