    <div class="moz-cite-prefix">Allen,<br>
      <br>
      I agree with Kirpal's comments. In fact, because the 300-volt
      breakers take up so much extra space, I'd stay with the
      three-modules-in-series design even if using the Classic charge
      controller; unless the PV array was so far away that you need the
      extra voltage to reduce wiring losses. But, for the example you
      are talking about with four modules in series you would want a
      Classic 200 not the Classic 150 because the Classic 150 would goes
      into non-operational hyper-Voc mode at 28&deg;C (82&deg;F), measured at
      the cell. <br>
      <br>
      The fact that the FM charge controller will talk to the Mate has
      advantages: 1) Only one temperature sensor is needed, 2) Voltage
      adjustment for grid-tie mode, and 3) Synchronization of equalize,
      absorb, and float modes. Not one of these is a significant enough
      issue to merit choosing the FM, and suffering from it's lower
      efficiency and poor MPPT tracking, over the Midnite Classic or
      Morningstar TriStar MPPT charge controllers.<br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>


</pre>
      On 12/16/2012 10:51 AM, Kirpal Khalsa wrote:<br>
    </div>
    <blockquote
cite="mid:CAM5ziKc4wUL8-eeCge4_eZZ65o4=BUzPK20TjGbHNu-o6gne0Q@mail.gmail.com"
      type="cite">Allan...indeed this is a limitation....and yes i agree
      with you that a higher voltage charge controller would be a
      welcome update to Outbacks line up.....Looking at the DPW top of
      pole list, i would suggest to you a design using 15 255 watt
      modules with the FM80 charge controller which would both meet your
      total wattage requirements, would still only &nbsp;need one charge
      controller, as well as conform to the 3 module multiplication
      requirement....additionally it would require less
      foundation/excavation work, but would in fact be a honker of an
      array....just an idea! Locally in your area I know Focused Energy
      has a good price and availability of the US made SolarWorld 255's
      which we use often...
      <div>
        Good luck.</div>
      <div>Kirpal<br>
        <br>
        <div class="gmail_quote">On Sun, Dec 16, 2012 at 10:41 AM, Allan
          Sindelar <span dir="ltr">&lt;<a moz-do-not-send="true"
              href="mailto:allan@positiveenergysolar.com"
              target="_blank">allan@positiveenergysolar.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div text="#000000" bgcolor="#FFFFFF"> Wrenches,<br>
              Please tell me if I'm overlooking something, in what
              appears to be a design weakness:<br>
              <br>
              I would like to use an Outback Radian system for a
              standard GTBB system. In order to take full advantage of
              the system's capabilities, I have to use all of Outback's
              main components; in this case the FM60 or FM80 charge
              controller. The problem is that the most common (and
              lower-cost) modules today are 60-cell, meaning 20
              Vnominal. Given the 150V DC hard maximum voltage limit of
              the FM-series charge controller, in our cold climate I can
              only use these 20V modules in 60 Vnominal series strings;
              that is, in multiples of three modules. As the Radian is
              (wisely) offered in 48V only, pairs of modules would
              provide too low a voltage, and series strings of four
              modules would exceed 150 Voc in cold weather. <br>
              <br>
              The base Midnite Classic 150 will safely operate to 198
              VDC in this application, but it won't communicate with the
              Mate3.<br>
              <br>
              Is this a fundamental design limitation in the Radian
              system, suggesting that Outback is due for a controller
              upgrade, or am I missing something obvious? It appears
              that arrays and racks have to be sized in ~720-watt sets
              of three-module series strings, which can be problematic
              in some designs. In the design in question I would like to
              use 16 240W modules on two 8-module pole-top racks (for
              seasonal adjustability); nothing in sets of three meets
              the customer's output and aesthetic needs. <br>
              <br>
              Any solutions would be welcome.<br>
              Thank you,<br>
              Allan<span class="HOEnZb"><font color="#888888"><br>
                  <div>-- <br>
                    <font face="Times New Roman, Times, serif"><b>Allan
                        Sindelar</b></font><br>
                    <small><a moz-do-not-send="true"
                        href="mailto:Allan@positiveenergysolar.com"
                        target="_blank"><font color="#000099"
                          face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
                      face="Times New Roman, Times, serif"><br>
                      <span style="font-size:10pt">NABCEP Certified
                        Photovoltaic Installer<br>
                        NABCEP Certified Technical Sales Professional<br>
                        New Mexico EE98J Journeyman Electrician<br>
                        Founder and Chief Technology Officer<br>
                        <b>Positive Energy, Inc.</b><br>
                        3209 Richards Lane (note new address)<br>
                        Santa Fe, New Mexico 87507<br>
                        <b><a moz-do-not-send="true"
                            href="tel:505%20424-1112"
                            value="+15054241112" target="_blank">505
                            424-1112</a></b><br>
                        <a moz-do-not-send="true"
                          href="http://www.positiveenergysolar.com/"
                          target="_blank"><u>www.positiveenergysolar.com</u></a></span></font>
                    <p class="MsoNormal" style="margin-right:722.25pt"><span
                        style="font-size:10pt"><b><br>
                        </b></span></p>
                    <span style="font-size:10pt"></span>