    <div class="moz-cite-prefix">These code references should be all
      that is necessary to put the inspector on the right path. His
      requirement that the source be capable of 100 amps clearly
      conflicts with the intent of 690.10(A); it makes clear that the
      inverter system only needs to be large enough to operate the
      single largest load that it is intended to operate. Thus it is
      permissible for combinations of loads to overload the inverter and
      cause a nuisance shutdown.<br>
      <br>
      You might also ask if he'd be happy with a utility service
      provided by a 15-kVA transformer. While capable of substantial
      overloads, it is only rated to provide 63 amps continuously. Most
      200-amp service panels don't really have 200 amps available except
      for short durations.<br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
t: 541-568-4882</pre>
      On 12/12/2012 4:43 AM, Jason Szumlanski wrote:<br>
    </div>
    <blockquote
cite="mid:CAJJtG3oA6KNYu6avGDBSqQbYJ_0rnGsykttmiEiuR6Lq8euL_g@mail.gmail.com"
      type="cite">See 690.10, 690.1, and 690.3.<br>
      <br>
      <br>
      <div id="WISESTAMP_SIG_6184">
        <div
          style="font-size:13px;font-family:Verdana,Arial,Helvetica,sans-serif">
          <div style="margin:0 0 8px 0">
            <p style="margin:0"><span style="color:#808080"><strong>Jason
                  Szumlanski</strong><em>&nbsp;</em></span></p>
            <p style="margin:0"><span style="color:#808080"><em>Fafco
                  Solar</em></span></p>
          </div>
        </div>
      </div>
      <div class="gmail_extra"><br>
        <br>
        <div class="gmail_quote">On Wed, Dec 12, 2012 at 1:00 AM,
          William Miller <span dir="ltr">&lt;<a moz-do-not-send="true"
              href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Jeff:<br>
            <br>
            There is a code passage that specifically states that one
            does not need to provide full rated ampacity to a service.
            &nbsp;I am sure you can find it.<br>
            <br>
            Find a way to prove, mathematically, that the system planned
            will provide adequate power. &nbsp;Create or find a spreadsheet
            listing all appliances and wattages and system watt hours
            provided. &nbsp;Dress it up, put your logo on it and sell it to
            the building department.<br>
            <br>
            William Miller<br>
            <br>
            <br>
            <br>
            <br>
            At 07:52 PM 12/11/2012, you wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              Content-Type: multipart/alternative;<br>
              &nbsp; &nbsp; &nbsp; &nbsp; boundary="----=_NextPart_000_0006_01CDD7F2.373D3CB0"<br>
              Content-Language: en-us
              <div>
                <div class="h5"><br>
                  <br>
                  We have a client that just had assembled on his rural
                  property a pre-fab modular home with &nbsp;"normal" wiring
                  and 200 amp main panel and meter base. &nbsp;However,
                  landowners around his property will not grant access
                  for electric utility to cross and he needs to move in
                  ASAP. &nbsp;He realizes that some day he should be able to
                  resolve this utility access but until then he wants us
                  to do an off-grid "basic" solar system with generator
                  backup so he can at least power lights, well pump, and
                  basic appliances. &nbsp; His budget will not allow a fully
                  off-grid solar system so we wanted to do reduced solar
                  and battery system with larger generator to fill in on
                  bad solar days. &nbsp;He does have good solar exposure and
                  lots of cleared land, but figures one day the solar
                  and generator will become a backup system to a future
                  grid connection so does not want to spend any more
                  than absolutely necessary.<br>
                  <br>
                  However ,this local inspector for this rural county
                  has no experience with solar and is expecting to see a
                  200 amp service connection from the utility before
                  allowing occupancy. &nbsp;He did hint that a 100 amp
                  service connection may be allowed but nothing less. &nbsp;I
                  know NEC does mention that a panel does not have to be
                  supplied with the amount of service capacity it is
                  rated for, but what other code issues can I point out
                  to get this accepted without getting into a pis-----
                  contest?<br>
                  <br>
                  Thanks,<br>
                  <br>
                  Jeff Yago<br>
                </div>
              </div>
            </blockquote>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org"
              target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options &amp; settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm"
              target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>