The separately derived issue aside, enphase inverters have an internal DC system ground and a marked point from which a DC GEC must be installed. Typically grounding is being done in the manner stated in 690.47(C)(3) - a single conductor as both the DC GEC and EGC, meaning it has to be the larger of the two sizes required; for most enphase systems, based on the interconnection breaker size, the minimum EGC would typically be #12 (Table 250.122), but the minimum size for a DC EGC is #8. A #6 may be preferable under the array due to interpretations about the conductor being subject to damage.<br clear="all">
<div><br></div><div>Brian Mehalic <br>NABCEP Certified Solar PV InstallerR031508-59<div>IREC ISPQ Certified Affiliated Instructor/PV US-0132<br><div><br></div><div>PV Curriculum Developer and Instructor<div>Solar Energy International<br>
<a href="http://www.solarenergy.org" target="_blank">http://www.solarenergy.org</a></div></div></div></div><br>
<br><br><div class="gmail_quote">On Wed, Nov 28, 2012 at 10:56 PM, mac Lewis <span dir="ltr">&lt;<a href="mailto:maclewis1@gmail.com" target="_blank">maclewis1@gmail.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hello wrenches,<div><br></div><div>What constitutes a separately derived system? Would you consider a breaker tied enphase system a separately-derived system? Suddenly, inspectors in our AHJ are considering all PV systems separately derived systems and thus requiring applying GEC sizing (as opposed to EGC sizing) from the inverter(s) to the tie in point. This does not jive with my understanding. Would like to hear other thoughts about this.</div>

<div><br></div><div>Here is the definition of a separately derived system as per 2008 NEC Article 100 Definitions:</div><div><br></div><div><u>Separately Derived System</u>: <i>A premises wiring system whose power is derived from a source of electric energy or equipment other than a service. Such systems have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system.</i></div>

<div><br></div><div>For your enphase systems do you size your ground from roof to the breaker panel as an EGC or a GEC?</div><div><br></div><div><br></div><div>Thanks in advance for your thoughts.<span class="HOEnZb"><font color="#888888"><br clear="all">
<div><br>
</div>-- <br><div><br></div><div><font color="#305A78" face="&#39;times new roman&#39;, serif"><br></font></div><div><br></div>Mac Lewis<br><br><span style="font-family:&#39;Times New Roman&#39;;font-size:medium;color:rgb(255,153,0)"><b><font face="Arial, Helvetica, sans-serif" size="3"><p align="left">

<font color="#000000" face="Verdana, Arial, Helvetica, sans-serif"><span style="font-size:small"><span style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font face="&#39;times new roman&#39;, serif">&quot;Yo solo s que no s nada.&quot;</font><span style="font-weight:700;color:rgb(104,104,104)"><font face="&#39;times new roman&#39;, serif">-Scrates</font></span></span></span></font></p>

</font></b></span><br>
</font></span></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br>