I really don&#39;t understand what your problem with this arrangement is.<div>How would this be different from a house on phase A-B installing an inverter and the next house on Phase B-C installing an inverter? Or, installing two single phase 240V A/C units in a three phase building? Electricians have no issue with installing single phase equipment in three phase buildings so why should small inverters be any more a problem.<div>
While it is always neat to install three inverters n a three phase configuration, 4,500 watts of imbalance is trivial.</div></div><div class="gmail_extra"><br><br><div class="gmail_quote">On Tue, Nov 27, 2012 at 3:59 PM,  <span dir="ltr">&lt;<a href="mailto:holtek@sbcglobal.net" target="_blank">holtek@sbcglobal.net</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><u></u>





<div bgcolor="#ffffff">
<div>We were asked to inspect a GT system installed by others. Service is 
208 3ph with two (?)Fronius IG 4500 208v inverters. The inverter panel is 
3ph with two 2pole breakers - one each side of the buss bar in a A/B, B/C 
configuration (??). Called Fronius and they said it would work, but they &quot;don&#39;t 
recommend it&quot;. No other information was given as to why they don&#39;t. My 
electrician is very uncomfortable with doing work on this system as is (ME 
TOO!), so I am wondering if I might be able get some ammo to convince system 
owner to add a third inverter to get the system right. What problems might/will 
be encountered in this system if not modified? BTW - inverter LCD screens were 
crapped out, so we couldn&#39;t readily see if system was functioning 
properly....from metering, we think not.</div>
<div></div>
<div></div>
<div>Holt E. Kelly<br>Holtek Fireplace &amp; Solar Products<br>500 Jewell 
Dr.<br>Waco TX. 76712<br><a href="tel:254-751-9111" value="+12547519111" target="_blank">254-751-9111</a><br><a href="http://www.holteksolar.com" target="_blank">www.holteksolar.com</a><br></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>
Cell: 264.235.5670</div><div>Skype: netconcepts</div><br>
</div>