Are you sure you can't?&nbsp; Since the bus has a rating of 150 A and is
protected by a 100 A breaker, there is plenty of room to not over amp the
bus from the two sources of power.<br><br>
The amperage from the inverter will cancel amperage coming from the
utility in the feeder.&nbsp; The wire will never supply over the 100
A.&nbsp; The theoretical max the inverter could backfeed would be 40 Amps
in the 100 Amp cable if no loads were being supplied.&nbsp; It would
certainly not be a safety issue.&nbsp; Am I missing something in the
code?<br><br>
<br>
At 12:51 AM 9/28/2012, you wrote:<br>
<blockquote type=cite class=cite cite="">Mac:<br><br>
Nope.<br><br>
<br>
William Miller<br><br>
PS:&nbsp; It's pretty straight forwards, the code says &quot;bus or
conductor.&quot;<br><br>
wm<br><br>
PPS:<br><br>
Can&nbsp; you customer live with a smaller feeder breaker, say 125
amps?&nbsp; If so, your gold.<br><br>
wm<br><br>
<br><br>
At 06:43 PM 9/27/2012, you wrote:<br>
<blockquote type=cite class=cite cite="">Hello wrenches,<br><br>
I am looking for advice on how the 120% rule applies to feeders for a
subpanel.&nbsp; I have this scenario:<br>
150A bus rating on subpanel with main breaker of 100A.&nbsp; The
conductors feeding this subpanel are 100A rated conductors.&nbsp; Can I
backfeed with a 40A breaker?<br><br>
Thanks<br><br>
-- <br><br>
<font color="#305A78"><br>
</font><br>
Mac Lewis<br><br>
<font face="Verdana"><b>&quot;Yo solo s que no s nada.&quot;
-Scrates<br>
</b></font><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a><br><br>
<br>
Internal Virus Database is out of date.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 8.5.455 / Virus Database: 271.1.1/5272 - Release Date: 09/16/12
18:34:00</blockquote><br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">
http://millersolar.com</a><br>
License No. C-10-773985<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>