<html><body><div style="color:#000; background-color:#fff; font-family:Courier New, courier, monaco, monospace, sans-serif;font-size:12pt"><div><pre style="white-space: pre-wrap; ">What size is the conduit? Can you re-pull conductors at a higher ampacity?</pre><pre style="white-space: pre-wrap; ">Nick Vida</pre><pre style="white-space: pre-wrap; "><br></pre><pre style="white-space: pre-wrap; "><br></pre><pre style="white-space: pre-wrap; ">Mac:

Nope.


William Miller

PS:  It's pretty straight forwards, the code says "bus or conductor."

wm

PPS:

Can  you customer live with a smaller feeder breaker, say 125 amps?  If so, 
your gold.

wm



At 06:43 PM 9/27/2012, you wrote:
&gt;<i>Hello wrenches,
</i>&gt;<i>
</i>&gt;<i>I am looking for advice on how the 120% rule applies to feeders for a 
</i>&gt;<i>subpanel.  I have this scenario:
</i>&gt;<i>150A bus rating on subpanel with main breaker of 100A.  The conductors 
</i>&gt;<i>feeding this subpanel are 100A rated conductors.  Can I backfeed with a 
</i>&gt;<i>40A breaker?
</i>&gt;<i>
</i>&gt;<i>Thanks</i></pre></div></div></body></html>