Happy Friday, all~<br><br>Allan &amp; Todd were discussing the issue where a &quot;reset type&quot; amp hour battery monitor (such as TriMetric) never gets to &quot;reset to full&quot; when operating on a GTWBB &quot;grid tie with battery backup&quot; system...because the battery stays in float and the monitor never sees a bulk charge voltage. <br>

<br>The problem here seems to reside more with the chicken than with the egg. A battery in &quot;float&quot; for long intervals will actually still undergo some self discharge, so it needs an occasional &quot;rebulk&quot; charge to restore full state of charge. <br>

<br><b>Inverter manufacturers please take note that a simple addition to your code base could cause a GTWBB inverter to rev up the battery charge voltage back through the bulk/absorption phase on a calendar basis such as once per month. </b>Victron Energy already does this with their inverter/chargers but Victron is not certified for US terrestrial and it&#39;s not set up for grid tie.<br>

<br>If the inverter system would do an occasional &quot;rebulk&quot;, that would also cause the battery capacity monitor to reset. Until that function becomes automatic within the inverter(s), the next best suggestion is for the client to manually simulate a power company blackout once per month by cycling the input AC breaker off, then on. This kicks up a bulk cycle, ensures good SOC on the battery, stirs up the electrolyte if the batteries are floodies, and resets the battery capacity monitor all with a single intervention. <br>

<br>The same manual intervention might also serve as a good time for the owner to check water levels on a flooded pack, near the end of the charge cycle. <br><br>The Wrench List is the bomb! Jolliness,<br><br clear="all">

Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br><br>Voice: 970-731-4675<br>