Is there a document available on how this world?<br><br>On Friday, July 20, 2012, Phil Undercuffler &lt;<a href="mailto:solarphil@gmail.com">solarphil@gmail.com</a>&gt; wrote:<br>&gt; Hi all, I just got a correction from Darren - global charge control is in the Mate3, and therefore works with any FM or MX controller that has the GT mode. It uses the current sense from the FN-DC and the GT mode signal to control the output of the controllers.<br>
&gt;<br>&gt; Sorry for any confusion<br>&gt;<br>&gt; Phil<br>&gt;<br>&gt; On Jul 20, 2012 4:11 PM, &quot;Chris Mason&quot; &lt;<a href="mailto:cometenergysystems@gmail.com">cometenergysystems@gmail.com</a>&gt; wrote:<br>&gt;<br>
&gt; Phil,<br>&gt; Good explanation of the feature. When did GCC make it into the firmware, and can the older ones be updated? It sounds like a perfect solution for some of my installations.<br>&gt;<br>&gt; On Fri, Jul 20, 2012 at 12:34 AM, Phil Undercuffler &lt;<a href="mailto:solarphil@gmail.com">solarphil@gmail.com</a>&gt; wrote:<br>
&gt;<br>&gt; OutBack implemented Global Charge Control in the FM charge controllers<br>&gt; a while back, based on the input of the good folk at SELF who worked<br>&gt; to power a number of hospitals and clinics in Haiti after the<br>
&gt; earthquake. In some of those systems, the PV array was based on the<br>&gt; typical running consumption of the hospital, in the 30 - 100 kW if I<br>&gt; remember right, and the battery bank was relatively modest. However,<br>
&gt; on the weekends and holidays without the normal AC loads the PV input<br>&gt; was considerably more than the battery could absorb without<br>&gt; destructive heating, something like a C2 or C5 rate.<br>&gt;<br>&gt; Global Charge Control is implemented using the MATE3, a FN-DC and FM<br>
&gt; charge controllers set to GT mode. You set a high charge current<br>&gt; limit in the M3, and then it monitors the charge current going to the<br>&gt; batteries. In normal operating mode the controllers stay in wide open<br>
&gt; mode, harvesting as much power as possible. However if the loads drop<br>&gt; and the total current from the charging sources begin exceed the<br>&gt; global charge limit, the system compensates and the controllers back<br>
&gt; off to prevent sending too much current to the batteries.<br>&gt;<br>&gt; In today&#39;s world of PV modules being cheaper than diesel, we&#39;re seeing<br>&gt; a lot more systems that can use this tool.<br>&gt;<br>&gt; Hope this helps,<br>
&gt;<br>&gt; Phil<br>&gt;<br>&gt;<br>&gt;<br>&gt; On Thu, Jul 19, 2012 at 7:56 PM, <a href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a><br>&gt; &lt;<a href="mailto:boB@midnitesolar.com">boB@midnitesolar.com</a>&gt; wrote:<br>
&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; I didn&#39;t see that Brian T had the same idea until after I sent that email<br>&gt;&gt; off to Allan...<br>&gt;&gt; boB<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt;<br>&gt;&gt; On 7/19/2012 7:53 PM, Allan Sindelar wrote:<br>
&gt;&gt;<br>&gt;&gt; Wrenches,<br>&gt;&gt; I forwarded Brian&#39;s post on to Robin at Midnite, as I thought it was an<br>&gt;&gt; interesting idea. Below is his response, as well as boB&#39;s.<br>&gt;&gt; Allan<br>&gt;&gt;<br>
&gt;&gt; Allan Sindelar<br>&gt;&gt; <a href="mailto:Allan@positiveenergysolar.com">Allan@positiveenergysolar.com</a><br>&gt;&gt; NABCEP Certified Photovoltaic Installer<br>&gt;&gt; NABCEP Certified Technical Sales Professional<br>
&gt;&gt; New Mexico EE98J Journeyman Electrician<br>&gt;&gt; Founder and Chief Technology Officer<br>&gt;&gt; Positive Energy, Inc.<br>&gt;&gt; 3209 Richards Lane (note new address)<br>&gt;&gt; Santa Fe, New Mexico 87507<br>
&gt;&gt; 505 424-1112<br>&gt;&gt; <a href="http://www.positiveenergysolar.com">www.positiveenergysolar.com</a><br>&gt;&gt;<br>&gt;&gt; Allan, It is simpler than what is being suggested. The reason they want to<br>&gt;&gt; limit to 20 amps is because the battery doesnt need anymore than that. The<br>
&gt;&gt; controller will automatically limit the charge current as the battery gets<br>&gt;&gt; full. If a large load is turned on, the controller will try to refill the<br>&gt;&gt; battery up to its capacity. The 80 amps will quickly be reduced because the<br>
&gt;&gt; voltage will rise to the point where the charge tapers off.<br>&gt;&gt;<br>&gt;&gt; There is nothing else that needs to be done. If the problem is that the<br>&gt;&gt; battery bank is too small for a big controller, the best answer is to get<br>
&gt;&gt; more batteries. A 80 amp charger into a 200 amp hour battery is going to<br>&gt;&gt; raise the battery voltage so quick, it will not affect the battery at all.<br>&gt;&gt; By the way, discharging a battery at 60 or 80 amps is probably going to do<br>
&gt;&gt; damage to a small battery also. We do have an input on the Classic that<br>&gt;&gt; could probably be programmed to do as requested. That input feature has yet<br>&gt;&gt; to be implemented. Im sure we will have discussions about this when the<br>
&gt;&gt; time comes to write the input code. Maybe this feature will be designed in,<br>&gt;&gt; but it doesnt sound like it is a very good feature to spend a bunch of time<br>&gt;&gt; on. After all, the main problem is that the battery bank is just too darned&lt;<br>
<br>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>Cell: 264.235.5670</div><div>Skype: netconcepts</div><br>