Kent,<div>Typically the manufacturer is not to anxious to change the parameters outside those set out in the UL 1742 standard. However, for this, I suspect that is what is needed. They will probably need you to sign a waiver first, which is what we had to do with SMA.</div>
<div><br></div><div>Do you have a scope to look at the waveform of the signal? With a scope and a few capacitors, you could see what it took to clean up the waveform reaching the inverters.<br><br><div class="gmail_quote">
On Mon, Jul 9, 2012 at 10:46 AM, Kent Osterberg <span dir="ltr">&lt;<a href="mailto:kent@coveoregon.com" target="_blank">kent@coveoregon.com</a>&gt;</span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <div>Chris,<br>
      <br>
      Enphase has the ability to remotely adjust the voltage and
      frequency operating windows. They have adjusted them as far as
      they can, or will.<br>
      <br>
      I have some SMA Sunny Boy inverters in locations that recently
      have TWACS remote reading systems installed. Most don&#39;t have
      remote data monitoring. At least one does but the TWACS meter was
      just installed there last week. I&#39;ll know more about that one
      after I have a chance to confirm that the TWACS system has been
      activated. <br>
      <br>
      I agree with you that the TWACS signal shouldn&#39;t be sent to the
      customer, but it is generated in the utility meter so it&#39;s going
      to both the customer and the substation. Also, the TWACS signal
      can be adjusted if necessary to generate a bigger signal. I guess
      that would be their first step in handling a site with a large
      capacitive load.<div class="im"><br>
      <br>
      <pre cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a href="http://www.bluemountainsolar.com" target="_blank">www.bluemountainsolar.com</a>
t: <a href="tel:541-568-4882" value="+15415684882" target="_blank">541-568-4882</a></pre></div><div><div class="h5">
      On 7/9/2012 6:05 AM, Chris Mason wrote:<br>
    </div></div></div><div><div class="h5">
    <blockquote type="cite">Yes, I expect they can. The greater issue is going to
      be whether the other inverters are going to react also. Have you
      had any experience with other inverters in this scenario?
      <div>I don&#39;t undertand why the meter manufacturer can&#39;t ensure the
        burst is filtered out of the load connections. They have to know
        it can mess up devices behind the meter.</div>
      <div>Large capacitors on the load side should not stop the utility
        reading the meter. If it does, any consumer with a large UPS
        will kill it.</div>
      <div><br>
      </div>
      <div>In the SMA firmware, there is the ability to adjust some of
        the parameters such as the Vmax to adjust the system to local
        variations, which we often have to do here. Can you adjust the
        size of the frequency window in the Enphase system settings? If
        you can make the inverters look at a longer window of cycles
        that may eliminate the problem.</div>
      <div><br>
      </div>
      <div>Chris<br>
        <br>
        <div class="gmail_quote">On Sun, Jul 8, 2012 at 8:40 PM, Kent
          Osterberg <span dir="ltr">&lt;<a href="mailto:kent@coveoregon.com" target="_blank">kent@coveoregon.com</a>&gt;</span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div bgcolor="#FFFFFF" text="#000000">
              <div>Chris,<br>
                <br>
                SCRs are capable of creating voltage spikes that cause
                noise well into the radio frequencies. But with TWACS
                there is an inductor in series with the SCR that is
                tuned such that the pulse caused when it fires is 0.5 ms
                to 1.0 ms wide with very little high frequency content.
                Because the frequency content is very low, it difficult
                to filter out. Ferrite toroids are of no help and large
                capacitors will prevent the utility from reading the
                meter too. The pulse location is near the zero crossing
                so it makes for a dirty looking waveform for about 8
                seconds while the meter is sending data. Never-the-less,
                it&#39;s actually easy to make a reliable frequency
                measurement by shifting the measurement threshold off
                zero far enough that the TWACS signal doesn&#39;t interfere.
                The Enpase folks should be able to do that with a
                firmware change.
                <div><br>
                  <pre cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a href="http://www.bluemountainsolar.com" target="_blank">www.bluemountainsolar.com</a>
t: <a href="tel:541-568-4882" value="+15415684882" target="_blank">541-568-4882</a></pre>
                </div>
                <div>
                  <div> On 7/8/2012 4:47 PM, Chris Mason
                    wrote:<br>
                  </div>
                </div>
              </div>
              <div>
                <div>
                  <blockquote type="cite">Kent,
                    <div>I haven&#39;t any direct experience with the smart
                      meters tripping inverters, but the issue of SCRs
                      and generators is well known. I suspect you
                      understand the problem, but to recap it, the
                      problem revolves around the way SCRs make a sine
                      wave.</div>
                    <div>A motor driven generator controls the
                      alternator output by increasing or decreasing the
                      DC excitation level. It does that by sensing the
                      &quot;zero crossing&quot;, or point in the sine wave at
                      which the voltage is zero. This happens 120 times
                      a second on a 60Hz system.</div>
                    <div>When the source of the electricity is
                      electronic, the waveform will sometimes be messy
                      around the zero crossing. That gives the voltage
                      control circuit problems to detect the zero
                      crossing We see this a lot when trying to drive a
                      UPS from a generator, it can drive the generator
                      crazy.</div>
                    <div><br>
                    </div>
                    <div>I suspect your problem is the same. The SCR in
                      the meter disturbs the waveform and the inverter
                      thinks it is a faulty waveform.</div>
                    <div>I would try a low pass filter between the
                      meter and the inverter. A properly sized capacitor
                      ought to remove any noise above 60hz and present a
                      clean waveform to the inverter.</div>
                    <div><br>
                    </div>
                    <div><br>
                      <div class="gmail_quote">On Sun, Jul 8, 2012 at
                        7:06 PM, Kent Osterberg <span dir="ltr">&lt;<a href="mailto:kent@coveoregon.com" target="_blank">kent@coveoregon.com</a>&gt;</span>
                        wrote:<br>
                        <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"> Wrenches,<br>
                          <br>
                          There weren&#39;t very many replies to my question
                          about grid-connected inverter compatibility
                          with utility remote meter reading systems so
                          I&#39;ll explain my recent experience with hope
                          that this information may be of assistance
                          sometime.<br>
                          <br>
                          Last fall I installed an Ephase system for a
                          customer. Soon after it was on line he
                          complained that the inverters were dropping
                          off line frequently. Since we had a lot of
                          cloudy weather in northeast Oregon all winter,
                          it wasn&#39;t easy to see what was going on. In
                          the spring we had some clear days and noticed
                          that the inverters were dropping off line
                          several times a day at exactly the same time
                          every day. It didn&#39;t take very long for our
                          suspicion to turn to the utilities new remote
                          meter reading equipment. Because our weather
                          has been so cloudy it took a while to find
                          clear days where the utility could provide
                          assistance. But with their help by reading the
                          meter on demand and temporarily disabling the
                          meter communications we were able to finally
                          prove the remote meter reading system is
                          tripping the inverters offline for five
                          minutes every time the meter sends a data
                          packet.<br>
                          <br>
                          Recently the remote meter reading system has
                          expanded to more areas so we have now observed
                          this problem with both Enphase M190 and M215
                          inverters. The system we&#39;ve observed that is
                          in town is seeing many more dropouts, so we
                          think every kWh meter on the same service
                          transformer and maybe some beyond it are
                          causing trouble too.<br>
                          <br>
                          The remote meter reading equipment is made by
                          Aclara and uses their TWACS technology. This
                          isn&#39;t new technology and with more remote
                          meter reading systems going in all the time
                          there will be more occurrences of
                          incompatibility. Certainly more between
                          Enphase and TWACS. And possibly more between
                          other inverters and other communications
                          systems.<br>
                          <br>
                          At present I&#39;m really dissatisfied with
                          Enphase&#39;s support on this issue. All they&#39;ve
                          done is point out that only a few systems have
                          been affected and put us in the position of
                          telling customers that they&#39;ll just have to
                          live with the lost production time. Until
                          Enphase comes up with a fix, I won&#39;t install
                          any more Enphase inverters.<br>
                          <br>
                          -- <br>
                          Kent Osterberg<br>
                          Blue Mountain Solar, Inc.<br>
                          <a href="http://www.bluemountainsolar.com" target="_blank">www.bluemountainsolar.com</a><br>
                          t: <a href="tel:541-568-4882" value="+15415684882" target="_blank">541-568-4882</a><br>
                          <br>
_______________________________________________<br>
                          List sponsored by Home Power magazine<br>
                          <br>
                          List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
                          <br>
                          Options &amp; settings:<br>
                          <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                          <br>
                          List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                          <br>
                          List rules &amp; etiquette:<br>
                          <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
                          <br>
                          Check out participant bios:<br>
                          <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
                          <br>
                        </blockquote>
                      </div>
                      <br>
                      <br clear="all">
                      <div><br>
                      </div>
                      -- <br>
                      Chris Mason
                      <div>President, Comet Systems Ltd</div>
                      <div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>
                      <div>Cell: <a href="tel:264.235.5670" value="+12642355670" target="_blank">264.235.5670</a></div>
                      <div>Skype: netconcepts</div>
                      <br>
                    </div>
                    <br>
                    <fieldset></fieldset>
                    <br>
                    <pre>_______________________________________________
List sponsored by Home Power magazine

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
                  </blockquote>
                  <br>
                  <br>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options &amp; settings:<br>
            <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
            <br>
            <br>
          </blockquote>
        </div>
        <br>
        <br clear="all">
        <div><br>
        </div>
        -- <br>
        Chris Mason
        <div>President, Comet Systems Ltd</div>
        <div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>
        <div>
          Cell: <a href="tel:264.235.5670" value="+12642355670" target="_blank">264.235.5670</a></div>
        <div>Skype: netconcepts</div>
        <br>
      </div>
      <br>
      <fieldset></fieldset>
      <br>
      <pre>_______________________________________________
List sponsored by Home Power magazine

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
    <br>
  </div></div></div>

<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>
Cell: 264.235.5670</div><div>Skype: netconcepts</div><br>
</div>