Yes, I expect they can. The greater issue is going to be whether the other inverters are going to react also. Have you had any experience with other inverters in this scenario?<div>I don't undertand why the meter manufacturer can't ensure the burst is filtered out of the load connections. They have to know it can mess up devices behind the meter.</div>
<div>Large capacitors on the load side should not stop the utility reading the meter. If it does, any consumer with a large UPS will kill it.</div><div><br></div><div>In the SMA firmware, there is the ability to adjust some of the parameters such as the Vmax to adjust the system to local variations, which we often have to do here. Can you adjust the size of the frequency window in the Enphase system settings? If you can make the inverters look at a longer window of cycles that may eliminate the problem.</div>
<div><br></div><div>Chris<br><br><div class="gmail_quote">On Sun, Jul 8, 2012 at 8:40 PM, Kent Osterberg <span dir="ltr"><<a href="mailto:kent@coveoregon.com" target="_blank">kent@coveoregon.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div bgcolor="#FFFFFF" text="#000000">
<div>Chris,<br>
<br>
SCRs are capable of creating voltage spikes that cause noise well
into the radio frequencies. But with TWACS there is an inductor in
series with the SCR that is tuned such that the pulse caused when
it fires is 0.5 ms to 1.0 ms wide with very little high frequency
content. Because the frequency content is very low, it difficult
to filter out. Ferrite toroids are of no help and large capacitors
will prevent the utility from reading the meter too. The pulse
location is near the zero crossing so it makes for a dirty looking
waveform for about 8 seconds while the meter is sending data.
Never-the-less, it's actually easy to make a reliable frequency
measurement by shifting the measurement threshold off zero far
enough that the TWACS signal doesn't interfere. The Enpase folks
should be able to do that with a firmware change.<div class="im"><br>
<pre cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a href="http://www.bluemountainsolar.com" target="_blank">www.bluemountainsolar.com</a>
t: <a href="tel:541-568-4882" value="+15415684882" target="_blank">541-568-4882</a></pre></div><div><div class="h5">
On 7/8/2012 4:47 PM, Chris Mason wrote:<br>
</div></div></div><div><div class="h5">
<blockquote type="cite">Kent,
<div>I haven't any direct experience with the smart meters
tripping inverters, but the issue of SCRs and generators is well
known. I suspect you understand the problem, but to recap it,
the problem revolves around the way SCRs make a sine wave.</div>
<div>A motor driven generator controls the alternator output by
increasing or decreasing the DC excitation level. It does that
by sensing the "zero crossing", or point in the sine wave at
which the voltage is zero. This happens 120 times a second on a
60Hz system.</div>
<div>When the source of the electricity is electronic, the
waveform will sometimes be messy around the zero crossing. That
gives the voltage control circuit problems to detect the zero
crossing We see this a lot when trying to drive a UPS from a
generator, it can drive the generator crazy.</div>
<div><br>
</div>
<div>I suspect your problem is the same. The SCR in the meter
disturbs the waveform and the inverter thinks it is a faulty
waveform.</div>
<div>I would try a low pass filter between the meter and the
inverter. A properly sized capacitor ought to remove any noise
above 60hz and present a clean waveform to the inverter.</div>
<div><br>
</div>
<div><br>
<div class="gmail_quote">On Sun, Jul 8, 2012 at 7:06 PM, Kent
Osterberg <span dir="ltr"><<a href="mailto:kent@coveoregon.com" target="_blank">kent@coveoregon.com</a>></span>
wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Wrenches,<br>
<br>
There weren't very many replies to my question about
grid-connected inverter compatibility with utility remote
meter reading systems so I'll explain my recent experience
with hope that this information may be of assistance
sometime.<br>
<br>
Last fall I installed an Ephase system for a customer. Soon
after it was on line he complained that the inverters were
dropping off line frequently. Since we had a lot of cloudy
weather in northeast Oregon all winter, it wasn't easy to
see what was going on. In the spring we had some clear days
and noticed that the inverters were dropping off line
several times a day at exactly the same time every day. It
didn't take very long for our suspicion to turn to the
utilities new remote meter reading equipment. Because our
weather has been so cloudy it took a while to find clear
days where the utility could provide assistance. But with
their help by reading the meter on demand and temporarily
disabling the meter communications we were able to finally
prove the remote meter reading system is tripping the
inverters offline for five minutes every time the meter
sends a data packet.<br>
<br>
Recently the remote meter reading system has expanded to
more areas so we have now observed this problem with both
Enphase M190 and M215 inverters. The system we've observed
that is in town is seeing many more dropouts, so we think
every kWh meter on the same service transformer and maybe
some beyond it are causing trouble too.<br>
<br>
The remote meter reading equipment is made by Aclara and
uses their TWACS technology. This isn't new technology and
with more remote meter reading systems going in all the time
there will be more occurrences of incompatibility. Certainly
more between Enphase and TWACS. And possibly more between
other inverters and other communications systems.<br>
<br>
At present I'm really dissatisfied with Enphase's support on
this issue. All they've done is point out that only a few
systems have been affected and put us in the position of
telling customers that they'll just have to live with the
lost production time. Until Enphase comes up with a fix, I
won't install any more Enphase inverters.<br>
<br>
-- <br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br>
<a href="http://www.bluemountainsolar.com" target="_blank">www.bluemountainsolar.com</a><br>
t: <a href="tel:541-568-4882" value="+15415684882" target="_blank">541-568-4882</a><br>
<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote>
</div>
<br>
<br clear="all">
<div><br>
</div>
-- <br>
Chris Mason
<div>President, Comet Systems Ltd</div>
<div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div>
<div>Cell: <a href="tel:264.235.5670" value="+12642355670" target="_blank">264.235.5670</a></div>
<div>Skype: netconcepts</div>
<br>
</div>
<br>
<fieldset></fieldset>
<br>
<pre>_______________________________________________
List sponsored by Home Power magazine
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>
Options & settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>
Check out participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
<br>
</div></div></div>
<br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Chris Mason<div>President, Comet Systems Ltd</div><div><a href="http://www.cometenergysystems.com" target="_blank">www.cometenergysystems.com</a></div><div>
Cell: 264.235.5670</div><div>Skype: netconcepts</div><br>
</div>