Greetings, All~<br><br>My client&#39;s string of SunXtender two volt AGM&#39;s won&#39;t hold a charge...after only two years! The prior AGM batteries also turned to toast prematurely. There must be a better way, so could we review the Outback charge setpoints? <br>


<br>Side note: Delta-v from the highest 2v cell to the lowest shows a gap of only .148v during a charge cycle so cell imbalance is not the likely problem. I think they&#39;re all working together equally bad. <br><br>A small amount of dry powder--light green color resembling verdegris finish on copper--can be seen around 30% of the +/- posts, in an amount smaller than 1/8 teaspoon. From this sign, I suspect that the cells have vented and dried out. The property is vacant 90% of the time so I am mostly focused on the MX60 solar charge controller as the culprit.<br>


<br>This is an early vintage Outback controller, firmware version 5.11. Temperature compensation is in place; automatic EQ is defeated. Bulk &amp; absorption setpoints exactly match those requested by Concorde/SunXtender: 28.8 volts bulk/absorption &amp; 26.4 volts Float. The controller does regulate at these voltage points so it&#39;s technically &quot;working&quot;--just grinding up batteries on a regular basis.<br>


<br>The Concorde people do not furnish suggestions regarding absorption time or &quot;rebulking&quot; so that may be the source of trouble. Controller setpoints have the Absorption Time Limit set for &quot;0 minutes minimum &amp; 1 hour maximum&quot;. The controller is also set to &quot;rebulk&quot; the battery at a 23 volt trigger and there&#39;s an inscrutable setpoint called &quot;End&quot; that&#39;s set for 45 amps. I have a theory about the meaning of that but I&#39;ll keep the noise level down...<br>


<br>If I recall correctly, the Outback end of charge routine in early days was to start a clock &amp; see how long it takes to move the battery to the bulk/absorption voltage then apply an equal amount of time for an absorption charge before shifting to float. Steve Higgins may confirm if that is indeed the protocol for a version 5.11 controller but: has that method now been changed in the newer version Flexmax controllers? It seems those now have an absorption duration value that can be changed so maybe that&#39;s what we need--a replacement controller along with good information on the absorption duration and/or float setpoints, etc. <br>


<br>I see that some controllers can even be set to not Float at all. Maybe that&#39;s better: run the charge then stop it all for the rest of the day. OR: thinking outside the box here...what about a controller that won&#39;t initiate charge cycle at all unless the battery voltage crests down to a trigger point. All I know for sure is that two sets of valuable batteries have now been ruined so &quot;normal&quot; charge setpoints are not working well in this situation.<br>

<br>If some better electronics (such as blending in the Outback capacity monitor gizmo) might help, I&#39;m all ears. Next time maybe I&#39;ll suggest flooded cells to the client instead of AGM&#39;s, but the cells are in a crawlspace that gets freezing cold at times. <br>

<br>Thanks in advance for advice &amp; suggestions. A second off grid client has a similar setup so I need to hotfoot it out there and tweak that (more recent) Outback controller to match the suggested setpoint revisions...before bad things happen again. <br>

<br>Jolliness,<br><br clear="all">Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br>