How do you flash your L feet without using a standoff? <br><br>
At 07:49 AM 7/2/2012, you wrote:<br>
<blockquote type=cite class=cite cite="">I've found that the Flashed
L-Foot connection costs about $0.10/w on a typical residential system,
and only adds about 1/4-1/2&quot; to the height, which can be minimized
using the slotted holes in a typical L-Foot. We need a lot of attachments
for 172 mph design wind speeds around here. Flashings at $500 for a 5kW
seems high, especially now as the percentage of the system price
increases. That being said, I would install L-Foot flashings on my own
roof - no exceptions.<br><br>
On the other hand, I've seen sealed lag screw connections work with solar
pool heating systems for decades without indication of problems. A
variety of sealants were used in the &quot;old days&quot; but most
recently Sikaflex 1A (which incidentally is not indicated for asphaltic
roofs) and Geocell 2300 have worked great.<br><br>
My 10 cents, :)<br><br>
Jason Szumlanski<br>
Fafco Solar<br><br>
<br>
On Fri, Jun 29, 2012 at 10:49 AM, jay peltz
&lt;<a href="mailto:jay@asis.com">jay@asis.com</a>&gt; wrote:<br>

<dl>
<dd>I have had&nbsp; the opportunity in the past few years to learn a lot
about good roofing waterproofing practices according to the national
roofers association.<br><br>

<dd>They don't agree that caulk works as the primary means of sealant,
which is what you are doing with an L foot.<br><br>

<dd>And given that we have really good off the shelf approved flashed
feet, why would you use anything else?<br><br>

<dd>My 2 cents,<br><br>

<dd>Jay<br><br>

<dd>peltz power<br><br>
<br>

<dd>On Jun 29, 2012, at 5:16 AM, Glenn Burt wrote:<br><br>
<blockquote type=cite class=cite cite="">
<dd>We have used a variety of sealants over the years, and determined
simple Henry roofing cement is the best product for use on comp
roofing.<br>

<dd>&nbsp;<br>

<dd>We also used to bend our own L-foot flashing, which we cut from
standard Al coil stock (before all the manufactured options were
available). This might be a good option for you in this case.<br>

<dd>&nbsp;<br>

<dd>&nbsp;<br>

<dd>&nbsp;<br>

<dd>Glenn<br>

<dd>&nbsp;<br>

<dd>From:</b>
<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">
re-wrenches-bounces@lists.re-wrenches.org</a>
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org">
re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of
</b>Drake<br>

<dd>Sent:</b> Thursday, June 28, 2012 6:40 PM<br>

<dd>To:</b> RE-wrenches<br>

<dd>Subject:</b> [RE-wrenches] L feet no flashing in shingle roof<br>

<dd>&nbsp;<br>

<dd>I'm quoting a job that has an existing array with L feet bolted down
to a shingle roof with no flashings.&nbsp; I want to match the height of
the existing array.&nbsp; Also some modules are being worked in around
skylights where it is unlikely that room would be available for flashings
to center over rafters.<br><br>

<dd>I've always used flashings.&nbsp; Would it be completely crazy to
follow suit of the existing array and bolt L feet straight to the shingle
roof with good roof sealant?&nbsp; If so, how would you seal it?<br><br>

<dd>Thanks,<br><br>

<dd>Drake <br><br>

<dd>Drake Chamberlin&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
<br>

<dd>ATHENS ELECTRIC LLC<br>

<dd>OH License 44810&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; <br>

<dd>CO license 3773<br>

<dd>NABCEP Certified PV<br>
</blockquote><br><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Home Power magazine<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Options &amp; settings:<br>

<dd>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>

<dd>List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>

<dd>List rules &amp; etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a><br><br>
<br>

</dl><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote>
<x-sigsep><p></x-sigsep>
<font size=2>Drake
Chamberlin<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab>
<br>
ATHENS ELECTRIC LLC<br>
OH License
44810<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab><br>
CO license 3773<br>
NABCEP Certified PV<br>
</font></body>
</html>