    <div class="moz-cite-prefix">I agree with Jason that the panel, as
      described, would be capable of supplying multiple branch circuits
      and could be deemed non-compliant, but I've found inspectors here
      to be reasonable about this practice. It's perfectly safe to add a
      branch circuit, even multiple ones, to an ac combiner. As long as
      it is for operating associated equipment such as communications
      devices like the Envoy, or data loggers, or power to operate a
      tracker controller and motor, it should be allowed.<br>
      <br>
      Consider a 100-amp panel being used as an ac combiner with four
      20-amp circuit breakers being backfed with micro-inverters. A few
      small loads on this panel just lowers the current on the bus bars.
      The risk that the 120% rule is supposed to address is the
      possibility of overloading the bus bars. In the case of the ac
      combiner that could happen if someone were to add some very large
      loads to it.<br>
      <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
t: 541-568-4882</pre>
      <br>
      On 7/1/2012 6:46 AM, Jason Szumlanski wrote:<br>
    </div>
    <blockquote
cite="mid:CAJJtG3rvU4K1UR6zk9CYHFjoH28acoiF7KV5K1f9GXUqzfYS6w@mail.gmail.com"
      type="cite">Well, if you install a bunch of 2-pole breakers for
      the.inverters, and then add a single pole breaker for the Envoy,
      there is definitely one space left and the panel would be
      "capable" of supplying additional branch circuits.
      <div>
        <br>
      </div>
      <div>
        <div>Just being devil's advocate here... I'm with you, but we
          need more clarity and less room for interpretation on this
          matter.&nbsp;</div>
        <div><br clear="all">
          Jason Szumlanski
          <div>Fafco Solar</div>
          <div>
            <br>
          </div>
          <br>
          <br>
          <br>
          <div class="gmail_quote">On Sat, Jun 30, 2012 at 5:09 PM, Kirk
            <span dir="ltr">&lt;<a moz-do-not-send="true"
                href="mailto:kirk@vtsolar.com" target="_blank">kirk@vtsolar.com</a>&gt;</span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <div bgcolor="#FFFFFF">
                <div>I would argue a single dedicated load circuit for
                  the Enphase Envoy, in a dedicated inverter combiner
                  panel, is code legal. Why? Because 705.12 states the
                  distribution equipment must be capable of supplying
                  "multiple branch circuits" for the 120% rule to apply.
                  A single &nbsp;dedicated circuit for the Envoy appears to
                  comply. Use a load center with a lockable cover if
                  there are extra slots and you have done due
                  diligence.&nbsp;<span class="HOEnZb"><font color="#888888"><br>
                      <br>
                      Kirk Herander
                      <div>VSE</div>
                    </font></span></div>
                <div>
                  <div class="h5">
                    <div><br>
                      On Jun 27, 2012, at 11:51 AM, Jason Szumlanski
                      &lt;<a moz-do-not-send="true"
                        href="mailto:jason@fafcosolar.com"
                        target="_blank">jason@fafcosolar.com</a>&gt;
                      wrote:<br>
                      <br>
                    </div>
                    <blockquote type="cite">
                      <div>If you install a combiner panel that can
                        supply additional branch circuits, it becomes
                        part of the building distribution system. Note
                        that Enphase recommends you install a branch
                        circuit to supply power to the Envoy device
                        right from the combiner panel. If that is the
                        case, the panel is certainly part of the
                        building distribution system and is obviously
                        capable of supplying branch circuits, in which
                        case the 120% rule would apply. I don't like it
                        and I don't necessarily agree with it, but based
                        on my strict interpretation of the code I can
                        see why an AHJ would require application of this
                        section in this case.
                        <div>
                          <div><br clear="all">
                            Jason Szumlanski
                            <div>Fafco Solar</div>
                            <div><br>
                            </div>
                            <br>
                            <br>
                            <br>
                            <div class="gmail_quote">On Wed, Jun 27,
                              2012 at 10:59 AM, Chris Mason <span
                                dir="ltr">&lt;<a moz-do-not-send="true"
href="mailto:cometenergysystems@gmail.com" target="_blank">cometenergysystems@gmail.com</a>&gt;</span>
                              wrote:<br>
                              <blockquote class="gmail_quote"
                                style="margin:0 0 0 .8ex;border-left:1px
                                #ccc solid;padding-left:1ex">
                                I don't think this is expressed in the
                                code, but in my opinion, the 120%
                                applies to the building distribution
                                equipment, not to parts of the solar
                                system. In the case where a panel is
                                being used to combine multiple inverter
                                outputs, the panel is part of the solar
                                system only. The 120% rule was an
                                accommodation to allow solar to feed a
                                building distribution panel and is not
                                applicable to solar system components.
                                It would be good if the code could
                                indicate this more clearly.
                                <div>
                                  <div><br>
                                    <br>
                                    <div class="gmail_quote">On Wed, Jun
                                      27, 2012 at 8:29 AM, Jason
                                      Szumlanski <span dir="ltr">&lt;<a
                                          moz-do-not-send="true"
                                          href="mailto:jason@fafcosolar.com"
                                          target="_blank">jason@fafcosolar.com</a>&gt;</span>
                                      wrote:<br>
                                      <blockquote class="gmail_quote"
                                        style="margin:0 0 0
                                        .8ex;border-left:1px #ccc
                                        solid;padding-left:1ex">
                                        Kirk,
                                        <div><br>
                                        </div>
                                        <div>That's basically what I
                                          said. Unfortunately, your
                                          opinion holds no weight with
                                          my local AHJ's. I've argued
                                          the point till blue in the
                                          face. Although, I have never
                                          had the instance where all
                                          available slots were filled in
                                          the combiner panel - I might
                                          be able to argue that case
                                          successfully.</div>
                                        <span><font color="#888888">
                                            <div><br>
                                            </div>
                                          </font></span>
                                        <div><span><font color="#888888">Jason
                                              Szumlanski
                                              <div>Fafco Solar</div>
                                              <div><br>
                                              </div>
                                              <br>
                                              <br>
                                              <br>
                                            </font></span>
                                          <div class="gmail_quote">
                                            <div>
                                              <div>On Tue, Jun 26, 2012
                                                at 4:53 PM, Kirk
                                                Herander <span
                                                  dir="ltr">&lt;<a
                                                    moz-do-not-send="true"
href="mailto:kirk@vtsolar.com" target="_blank">kirk@vtsolar.com</a>&gt;</span>
                                                wrote:<br>
                                              </div>
                                            </div>
                                            <blockquote
                                              class="gmail_quote"
                                              style="margin:0 0 0
                                              .8ex;border-left:1px #ccc
                                              solid;padding-left:1ex">
                                              <div>
                                                <div>
                                                  <div link="blue"
                                                    vlink="purple"
                                                    lang="EN-US">
                                                    <div>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">Jason,</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal">
                                                        <span
                                                          style="color:#1f497d">In
                                                          your email
                                                          below you
                                                          state:</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">&#8220;</span>You DO need to observe the 120% rule for
                                                        the combining
                                                        subpanel,
                                                        regardless of
                                                        whether there
                                                        are loads
                                                        present, at
                                                        least in
                                                        jurisdictions
                                                        where I have
                                                        worked. I've
                                                        heard that some
                                                        inspectors will
                                                        allow you to
                                                        ignore it if it
                                                        is labeled as a
                                                        PV combiner with
                                                        "add no loads"
                                                        notation.<span
                                                          style="color:#1f497d">&#8221;</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">NEC 705.12 (D) states that the distribution
                                                          equipment (in
                                                          this case the
                                                          combiner
                                                          panel, fed by
                                                          multiple
                                                          inverters and
                                                          a utility
                                                          source) must
                                                          be &#8220;capable of
                                                          supplying
                                                          multiple
                                                          branch
                                                          circuits or
                                                          feeders or
                                                          both&#8221; for
                                                          (D)(1) through
                                                          (7) to apply.
                                                          If you fully
                                                          populated a
                                                          combiner panel
                                                          with inverter
                                                          breakers,
                                                          leaving no
                                                          slots for load
                                                          breakers, it
                                                          is not capable
                                                          of supplying
                                                          branch
                                                          circuits or
                                                          feeders, and
                                                          IMO the 120%
                                                          rule does not
                                                          apply to the
                                                          combiner buss
                                                          or the
                                                          conductors
                                                          back to its
                                                          point of
                                                          utility
                                                          interconnect.
                                                          I have argued
                                                          this point as
                                                          well as label
                                                          combiners
                                                          &#8220;load circuits
                                                          prohibited&#8221;
                                                          (with or
                                                          without
                                                          available
                                                          slots) and
                                                          received AHJ
                                                          approval.</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">You could also just lock shut a combiner that had
                                                          spare slots as
                                                          a deterrent to
                                                          adding load
                                                          breakers.</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">Kirk
                                                          Herander</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">VT
                                                          Solar, LLC</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">dba
                                                          Vermont Solar
                                                          Engineering</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">NABCEP<sup>TM
                                                          </sup>Certified
                                                          installer
                                                          Charter Member</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">NYSERDA-eligible
                                                          Installer</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">VT
                                                          RE Incentive
                                                          Program
                                                          Partner</span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d"><a
moz-do-not-send="true" href="tel:802.863.1202" value="+18028631202"
                                                          target="_blank">802.863.1202</a></span><span
style="font-size:18.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d"></span></p>
                                                      <p
                                                        class="MsoNormal"><span
style="font-size:14.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1f497d">&nbsp;</span></p>
                                                      <p
                                                        class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;">From:</span></b><span
style="font-size:10.0pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;">
                                                          <a
                                                          moz-do-not-send="true"
href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>
                                                          [mailto:<a
                                                          moz-do-not-send="true"
href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>]
                                                          <b>On Behalf
                                                          Of </b>Jason
                                                          Szumlanski<br>
                                                          <b>Sent:</b>
                                                          Tuesday, June
                                                          26, 2012 8:28
                                                          AM<br>
                                                          <b>To:</b>
                                                          RE-wrenches<br>
                                                          <b>Subject:</b>
                                                          Re:
                                                          [RE-wrenches]
                                                          Enphase grid
                                                          tie question</span></p>
                                                      <p
                                                        class="MsoNormal">&nbsp;</p>
                                                      <p
                                                        class="MsoNormal">I'll
                                                        email you
                                                        off-list a
                                                        1-line diagram
                                                        from a system
                                                        with 164
                                                        microinverters
                                                        broken down into
                                                        8 strings in a
                                                        208V system.
                                                        This particular
                                                        system used two
                                                        subpanels to
                                                        accumulate PV,
                                                        but that was
                                                        only because we
                                                        had to backfeed
                                                        two existing
                                                        subpanels due to
                                                        the size of
                                                        existing
                                                        480/208V
                                                        transformers.
                                                        You will have to
                                                        look at the
                                                        utility service
                                                        and all existing
                                                        equipment.</p>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">&nbsp;</p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">Regarding
                                                          the breakers
                                                          in the
                                                          subpanel, you
                                                          will only need
                                                          a maximum of a
                                                          20A breaker
                                                          for each
                                                          string. The
                                                          max inverters
                                                          per string is
                                                          25 and the
                                                          calculation
                                                          for OCPD is:</p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">&nbsp;</p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">215W
                                                          / 208V x 25
                                                          inverters /
                                                          1.732 x 1.25 =
                                                          18.65A</p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">&nbsp;</p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">
                                                          <span
                                                          style="color:#1f497d">&#8220;</span>You
                                                          DO need to
                                                          observe the
                                                          120% rule for
                                                          the combining
                                                          subpanel,
                                                          regardless of
                                                          whether there
                                                          are loads
                                                          present, at
                                                          least in
                                                          jurisdictions
                                                          where I have
                                                          worked. I've
                                                          heard that
                                                          some
                                                          inspectors
                                                          will allow you
                                                          to ignore it
                                                          if it is
                                                          labeled as a
                                                          PV combiner
                                                          with "add no
                                                          loads"
                                                          notation.<span
style="color:#1f497d">&#8221;</span></p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">&nbsp;</p>
                                                      </div>
                                                      <div>
                                                        <p
                                                          class="MsoNormal">Use
                                                          a MLO panel
                                                          with a fusible
                                                          disconnect
                                                          between the
                                                          subpanel and
                                                          the
                                                          interconnection
                                                          point. If you
                                                          use a 225A
                                                          panel, you can
                                                          feed it with
                                                          270A. With
                                                          eight 20A
                                                          backfed PV
                                                          circuits, you
                                                          would need to
                                                          protect the
                                                          line side of
                                                          the panel with
                                                          a 100A fusible
                                                          disconnect.
                                                          That probably
                                                          isn't going to
                                                          work. You may
                                                          be best off
                                                          from a cost
                                                          perspective
                                                          using two 225A
                                                          subpanels and
                                                          two 60A
                                                          fusible
                                                          disconnects.
                                                          Anything
                                                          larger than a
                                                          60A 3P
                                                          disconnect and
                                                          the price
                                                          skyrockets. It
                                                          all depends on
                                                          your circuit
                                                          calculations
                                                          and the
                                                          existing
                                                          equipment. Of
                                                          course, you
                                                          would need two
                                                          spaces for
                                                          your
                                                          interconnection
                                                          point.</p>
                                                      </div>
                                                      <div>
                                                        <div>
                                                          <div>
                                                          <p
                                                          class="MsoNormal">&nbsp;</p>
                                                          </div>
                                                          <div>
                                                          <p
                                                          class="MsoNormal">Jason
                                                          Szumlanski</p>
                                                          <div>
                                                          <p
                                                          class="MsoNormal">Fafco
                                                          Solar</p>
                                                          </div>
                                                          </div>
                                                        </div>
                                                        <p
                                                          class="MsoNormal"
style="margin-bottom:12.0pt">&nbsp;
                                                          <br>
                                                        </p>
                                                      </div>
                                                    </div>
                                                  </div>
                                                </div>
                                              </div>
                                            </blockquote>
                                          </div>
                                        </div>
                                      </blockquote>
                                    </div>
                                  </div>
                                </div>
                              </blockquote>
                            </div>
                          </div>
                        </div>
                      </div>
                    </blockquote>
                  </div>
                </div>
              </div>
            </blockquote>
          </div>
        </div>
      </div>
    </blockquote>
    <br>
    <br>
  </body>
</html>