Hi Wrenches,<br><br>I inherited an off-grid PV system that seems to be significantly under producing. I have:<br><br>12 KC120&#39;s (~17V 7A each) paired up 2 in series, for 6 strings terminated on new 15A breakers in a new Midnite combiner,<br>
Output of combiner passes through a 60A breaker then into a SolarBoost 50 charge controller. An SW4024 ties in the CC, a Kohler 8.5 Gen set, and a Yuasa 24V battery bank.<br><br>My problem is that I never see more than about 5A (displayed at charge controller) coming off the array, even in full sun, regardless of the state of charge of the batteries. I figure I should see, at least once in a while, closer to between 20-30A. Batteries are, admittedly, passed their life expectancy as the system was installed in &#39;02 and I am sure this is part of the problem. I&#39;m thinking that if the batteries are at about 1/2 capacity (don&#39;t own a hydrometer...yet), the controller senses the batteries are near full SOC even at lower voltage (~24V) and is therefore attempting to trickle charge even in the bulk stage. Though this is not how the CC is supposed to function in bulk, obviously, I&#39;m assuming the old batteries are altering the standard operating conditions of the system. I&#39;ve adjusted the Bulk set point on the CC but that doesn&#39;t seem to make a difference.<br>
<br>I doubt this is part of the problem but the generator is problematic as well (it has it&#39;s own array of maladies).<br><br>Any insight is greatly appreciated. Thanks!<br><br>-- <br>Eric Stikes<br>Owner<br>SunHarvest Solar<br>