<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; ">Hi William,<div><br></div><div>I agree with you on the GFP.</div><div><br></div><div>There is a work around for the larger breaker size and that is to install a prebreaker from the array then to the GFP breaker then to the CC.</div><div>You then get to work on the smallest breaker size for wiring, if my understanding of the code is correct.</div><div><br></div><div>jay</div><div><br></div><div>peltz power</div><div><br></div><div><br><div><div>On Apr 17, 2012, at 6:42 PM, William Miller wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite">
<div>
Friends:<br><br>
Here is a related problem:&nbsp; If we use an 80 amp GFD (ground fault
detection) breaker, even for a very small array, we have to use 3AWG CU
wire from the battery buss to the breaker and from the breaker to the FM
or MX60.&nbsp; This seems like a big hassle for 5 or 10 amps of
charging.&nbsp; A variety of sizes of GFD breakers would be
helpful.<br><br>
Here is a bigger problem:&nbsp; GFD breakers don't really work.&nbsp; All
they do is turn off the charge function in hopes that someone will find
the problem.&nbsp; In the meantime, the negative-to-ground bond is
removed and module mounting framework could be energized.&nbsp; PV GFD
breakers are completely different from standard AC GFDI (ground fault
detection and interruption) receptacles and circuit breakers.&nbsp; The
AC versions interrupt power upstream, the PV versions interrupt power
<i>downstream</i> from the fault.<br><br>
See:&nbsp;
<a href="http://millersolar.com/MillerSolar/case_studies/ground_fauilt/_ground_fault.html" eudora="autourl">http://millersolar.com/MillerSolar/case_studies/ground_fauilt/_ground_fault.html</a>
for some musings on the subject.<br><br>
As they say on TV: "There had to be a better way!"<br><br>
William Miller<br><br><br></div></blockquote></div><br></div></body></html>