    William,<br>
    <br>
    There have been too many fires where GFP failed to operate correctly
    to argue that they are really good at what they are supposed to do.
    But, I think it is inappropriate to say they don't really work at
    all. How many fires could have or would have happened without the
    GFP devices? Does anyone have stats?<br>
    <br>
    In every PV system I've installed, and since you do high quality
    work, I'm confident that in every one that you have installed, the
    mounting framework is securely grounded. The GFP device does not
    change that circumstance. Every junction box, conduit, mounting
    rail, and PV module is grounded and safe to touch regardless of what
    the GFP does. If someone removes <i>the </i>module grounding while
    looking for a ground fault, then it is possible to have an energized
    module frame, but the GFP didn't create this risk. The system could
    be solidly grounded with no GFP device and the module frame would be
    just as energized. It's important that every PV installer understand
    that risk and also understand that every properly grounded component
    of the system is still perfectly safe.<br>
    <br>
    My major complaint about the GFP is that, in battery systems, they
    expose the homeowner to unsafe conditions. 690.5(C) requires that a
    GFP hazard warning be located within site of the batteries.
    Unfortunately, the person servicing the 12-volt or 24-volt
    refrigerator or lights isn't going to see that warning. In the event
    of a ground fault that opens the GFP device, the negative wire going
    to the lights or refrigerator or any other dc load may be energized
    to -150-volts to ground. Or maybe -300 volts or -600 volts with some
    of the new charge controllers. Ground, the green wire running
    everywhere, is connected to the positive PV wire someplace in the
    array and the negative wire is connected to every negative wire in
    the system. If the unexpected voltage isn't a bad enough risk, the
    current may be worse. There is nothing to stop the arc from the
    shorted PV array if someone accidently connects negative to ground.
    This is actually a preventable circumstance: the GFP simply needs to
    open both PV+ and PV-. The manufacturers need to step up and correct
    this. The NEC needs to be changed to require it. This won't reduce
    the risks at the PV array, but it is certainly worth it to design
    components that don't but homeowners at unnecessary risk.<br>
    <br>
    <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
    <br>
    On 4/17/2012 6:42 PM, William Miller wrote:
    <blockquote
      cite="mid:6.0.1.1.2.20120417180352.02904358@millersolar.com"
      type="cite">
      Friends:<br>
      <br>
      Here is a related problem:&nbsp; If we use an 80 amp GFD (ground fault
      detection) breaker, even for a very small array, we have to use
      3AWG CU
      wire from the battery buss to the breaker and from the breaker to
      the FM
      or MX60.&nbsp; This seems like a big hassle for 5 or 10 amps of
      charging.&nbsp; A variety of sizes of GFD breakers would be
      helpful.<br>
      <br>
      Here is a bigger problem:&nbsp; GFD breakers don't really work.&nbsp; All
      they do is turn off the charge function in hopes that someone will
      find
      the problem.&nbsp; In the meantime, the negative-to-ground bond is
      removed and module mounting framework could be energized.&nbsp; PV GFD
      breakers are completely different from standard AC GFDI (ground
      fault
      detection and interruption) receptacles and circuit breakers.&nbsp; The
      AC versions interrupt power upstream, the PV versions interrupt
      power
      <i>downstream</i> from the fault.<br>
      <br>
      See:&nbsp;
      <a moz-do-not-send="true"
href="http://millersolar.com/MillerSolar/case_studies/ground_fauilt/_ground_fault.html"
        eudora="autourl">http://millersolar.com/MillerSolar/case_studies/ground_fauilt/_ground_fault.html</a>
      for some musings on the subject.<br>
      <br>
      As they say on TV: "There had to be a better way!"<br>
      <br>
      William Miller<br>
      <br>
      <br>
      <br>
      <br>
      <br>
      At 05:54 PM 4/17/2012, Kent Osterberg wrote:<br>
      <blockquote type="cite" class="cite" cite="">Nathan,<br>
        <br>
        I don't think anyone makes a 100-amp PV GFP. The panel mount
        breaker model that's being used for the PV GFP doesn't include a
        100-amp breaker.<br>
        <br>
        The Classic has a built-in GFP so you shouldn't need an external
        GFP for it. You will need to add a GFP for the FM60 - a single
        80-amp GFP would work.<br>
        <br>
        You can use the dual 80-amp GFP and shut down both PV arrays at
        the same time if the GFP is wired to disconnect the PV array
        from the charge controller input. That's where Outback's
        instructions used to show the GFP, and it is a better place for
        it than on the charge controller output anyway. Midnite's
        instructions show the GFP on the charge controller input, but
        their 80-amp GFP is a single.<br>
        <br>
        <pre>Kent Osterberg
Blue Mountain Solar, Inc.
<a moz-do-not-send="true" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
        <br>
        On 4/17/2012 11:08 AM, Nathan Stumpff wrote: <br>
        <blockquote type="cite" class="cite" cite="">Wrenches,<br>
          &nbsp;<br>
          In a job coming up I have a customer with an existing FM60
          controller,&nbsp; 520 watt (!!) array. We are doing a ton of work,
          including adding a 4 kW solar array with Classic 150 charge
          controller. I am trying to figure out how to handle the GFP.<br>
          &nbsp;<br>
          For the Classic, I need a 90 or 100 A output breaker minimum.
          80 A is not an option. The OutBack dual GFP is 80 A, and so it
          not an option.<br>
          &nbsp;<br>
          Is there a 100 A GFP breaker assembly I have just never seen?
          Is there a way to use the Classic&#8217;s GFP to run an external
          relay via AUX (to trip the FM60 output breaker at the same
          time)? Any ideas?<br>
          &nbsp;<br>
          Thanks,<br>
          -Nathan<br>
          &nbsp;<br>
          --<br>
          Nathan J. Stumpff - Arctic Sun, LLC<br>
          NABCEP Ceritified PV Installer #091209-175<br>
          <a moz-do-not-send="true"
            href="mailto:nathan@arcticsun-llc.com">nathan@arcticsun-llc.com</a><br>
          Office: 907/457-1297<br>
        </blockquote>
        <br>
      </blockquote>
      <x-sigsep>
        <p>Miller Solar<br>
          Voice :805-438-5600<br>
          email: <a class="moz-txt-link-abbreviated" href="mailto:william@millersolar.com">william@millersolar.com</a><br>
          <a moz-do-not-send="true" href="http://millersolar.com/"
            eudora="autourl">http://millersolar.com<br>
          </a>License No. C-10-773985<br>
          <br>
        </p>
      </x-sigsep></blockquote>
  </body>
</html>