    Phil,<br>
    <br>
    While using a dual GFDI to open both positive and negative array
    conductors is the safest thing to do in battery systems, and it is
    clearly compliant with 690.5 to do so, it is not consistent with the
    manufacturer's instructions or the device listing. So that leads
    back to a violation of 110.3(B). I find the present situation very
    disturbing.<br>
    <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
t: 541-568-4882</pre>
    <br>
    On 4/18/2012 8:28 PM, Philip wrote:
    <blockquote
      cite="mid:833BC721-4252-4F01-850B-755C8FA4645F@gmail.com"
      type="cite">
      <div>Hi Kent,&nbsp;</div>
      <div><br>
      </div>
      <div>I wanted to add a little more re positive grounding.
        OutBack's communication structure, like many other
        manufacturers, is referenced to Negative. If you install
        multiple devices in a positive ground system and connect them
        together via a Hub and add disconnects/overcurrent protection
        like normal in the ungrounded (this time negative) conductor,
        any time the breaker opens current will try to return to the
        battery by any means possible, and that means through the comm
        cables. That pretty much takes out all the connected devices, it
        aint pretty. &nbsp;Therefore, OutBack recommends using double pole
        breakers, in both positive and negative conductors, when using
        multiple connected current-generation devices in positive
        grounded systems. &nbsp;Not a perfect solution, but it is what it
        is.&nbsp;</div>
      <div><br>
      </div>
      <div>To answer your question about upgrading older systems, if I
        were working on my mother's house and I had the option, I would
        not install any of the current generation GFDI devices. That
        might be heresy and not technically Code compliant, but on a
        battery based system I believe it to be the safer option. &nbsp;If I
        had to install one, it could go on either the battery or the
        array side of the controller. &nbsp;Once there is a better solution I
        would go back and retrofit Mom's system, because it's worth it.&nbsp;</div>
      <div><br>
      </div>
      <div>BTW, OutBack's double and quad GFDI can be used to
        simultaneously disconnect both positive and negative, per your
        desire. That's another advantage of a multi-pole device.&nbsp;</div>
      <div><br>
      </div>
      <div>Phil<br>
        <br>
        <br>
        <div><br>
        </div>
      </div>
      <div><br>
        On Apr 18, 2012, at 2:21 PM, Kent Osterberg &lt;<a
          moz-do-not-send="true" href="mailto:kent@coveoregon.com">kent@coveoregon.com</a>&gt;
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div>
          <meta content="text/html; charset=ISO-8859-1"
            http-equiv="Content-Type">
          William,<br>
          <br>
          Square D used to make a QO breaker body without the
          overcurrent trip mechanism. Internally it just had the switch
          contacts and it was intended for use as a disconnect in
          locations where overcurrent protection was already provided.
          The reason I mention this is that the 80-amp PV GFP should not
          be thought of as overcurrent protection. In fact it would be
          most appropriate if the 80-amp side of the GFP didn't have an
          overcurrent trip mechanism. It <i>should</i> only be
          sensitive to ground faults. If it is sensitive to overcurrent,
          then it may be activated when there isn't a ground fault and
          unnecessarily disconnect the negative conductor from ground. <br>
          <br>
          Code prohibits the use of a GFP as a disconnect for the PV
          array. I believe that's because they intend the power system
          to remain bonded to ground except in the event of ground
          fault. It follows that the GFP should not be used as a
          disconnect between the batteries and charge controller either.
          That's my interpretation. The Code doesn't mention the
          possibility of putting the GFP between the batteries and
          charge controller as Outback's instructions for the GFDI
          require. So, even though Outback's instructions for the GFDI
          don't show it, put an appropriate breaker for overcurrent
          protection between the battery and the GFDI, then use wire
          that's appropriate for the charge controller and overcurrent
          protection. <br>
          <br>
          In my opinion putting the GFDI between the batteries and
          charge controller is a really bad idea. Nearly all charge
          controllers warn that the battery should be turned on first
          and turned off last. It puts much more stress on the charge
          controller when the battery circuit is opened under load than
          it does when the PV circuit is opened. In fact opening the
          battery circuit may well cause the charge controller to fail.
          Outback warns that if their charge controllers are connected
          to a positive ground system, the communication port of the
          charge controller or the Hub may be damaged. If there is a
          fault in the PV array that causes the GFDI to open, it very
          well may leave the system in a positive ground condition. <br>
          <br>
          When upgrading an older PSDC Outback system which instructions
          are more appropriate to follow? The ones for the PSDC that
          show the GFP before the charge controller. Or the newer
          instructions for the GFDI that show it after the charge
          controller. Except the the label and instructions the GFP and
          the GFDI are identical. In case you don't remember, the PSDC
          came with a schematic showing all possible options attached to
          the back of the front panel. When it comes time to
          troubleshoot sometime in the future, that schematic is still
          going to be there.<br>
          <br>
          <pre class="moz-signature" cols="72">Kent Osterberg
Blue Mountain Solar, Inc.
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
t: 541-568-4882</pre>
          <br>
          On 4/17/2012 6:42 PM, William Miller wrote:
          <blockquote
            cite="mid:6.0.1.1.2.20120417180352.02904358@millersolar.com"
            type="cite"> Friends:<br>
            <br>
            Here is a related problem:&nbsp; If we use an 80 amp GFD (ground
            fault detection) breaker, even for a very small array, we
            have to use 3AWG CU wire from the battery buss to the
            breaker and from the breaker to the FM or MX60.&nbsp; This seems
            like a big hassle for 5 or 10 amps of charging.&nbsp; A variety
            of sizes of GFD breakers would be helpful.<br>
            <br>
            Here is a bigger problem:&nbsp; GFD breakers don't really work.&nbsp;
            All they do is turn off the charge function in hopes that
            someone will find the problem.&nbsp; In the meantime, the
            negative-to-ground bond is removed and module mounting
            framework could be energized.&nbsp; PV GFD breakers are
            completely different from standard AC GFDI (ground fault
            detection and interruption) receptacles and circuit
            breakers.&nbsp; The AC versions interrupt power upstream, the PV
            versions interrupt power <i>downstream</i> from the fault.<br>
            <br>
            See:&nbsp; <a moz-do-not-send="true"
href="http://millersolar.com/MillerSolar/case_studies/ground_fauilt/_ground_fault.html"
              eudora="autourl">http://millersolar.com/MillerSolar/case_studies/ground_fauilt/_ground_fault.html</a>
            for some musings on the subject.<br>
            <br>
            As they say on TV: "There had to be a better way!"<br>
            <br>
            William Miller<br>
            <br>
            <br>
            <br>
            <br>
            <br>
            At 05:54 PM 4/17/2012, Kent Osterberg wrote:<br>
            <blockquote type="cite" class="cite" cite="">Nathan,<br>
              <br>
              I don't think anyone makes a 100-amp PV GFP. The panel
              mount breaker model that's being used for the PV GFP
              doesn't include a 100-amp breaker.<br>
              <br>
              The Classic has a built-in GFP so you shouldn't need an
              external GFP for it. You will need to add a GFP for the
              FM60 - a single 80-amp GFP would work.<br>
              <br>
              You can use the dual 80-amp GFP and shut down both PV
              arrays at the same time if the GFP is wired to disconnect
              the PV array from the charge controller input. That's
              where Outback's instructions used to show the GFP, and it
              is a better place for it than on the charge controller
              output anyway. Midnite's instructions show the GFP on the
              charge controller input, but their 80-amp GFP is a single.<br>
              <br>
              <pre>Kent Osterberg
Blue Mountain Solar, Inc.
<a moz-do-not-send="true" href="http://www.bluemountainsolar.com">www.bluemountainsolar.com</a>
</pre>
              <br>
              On 4/17/2012 11:08 AM, Nathan Stumpff wrote: <br>
              <blockquote type="cite" class="cite" cite="">Wrenches,<br>
                &nbsp;<br>
                In a job coming up I have a customer with an existing
                FM60 controller,&nbsp; 520 watt (!!) array. We are doing a
                ton of work, including adding a 4 kW solar array with
                Classic 150 charge controller. I am trying to figure out
                how to handle the GFP.<br>
                &nbsp;<br>
                For the Classic, I need a 90 or 100 A output breaker
                minimum. 80 A is not an option. The OutBack dual GFP is
                80 A, and so it not an option.<br>
                &nbsp;<br>
                Is there a 100 A GFP breaker assembly I have just never
                seen? Is there a way to use the Classic&#8217;s GFP to run an
                external relay via AUX (to trip the FM60 output breaker
                at the same time)? Any ideas?<br>
                &nbsp;<br>
                Thanks,<br>
                -Nathan<br>
                &nbsp;<br>
                --<br>
                Nathan J. Stumpff - Arctic Sun, LLC<br>
                NABCEP Ceritified PV Installer #091209-175<br>
                <a moz-do-not-send="true"
                  href="mailto:nathan@arcticsun-llc.com">nathan@arcticsun-llc.com</a><br>
                Office: 907/457-1297<br>
              </blockquote>
              _______________________________________________<br>
              List sponsored by Home Power magazine<br>
              <br>
              List Address: <a moz-do-not-send="true"
                class="moz-txt-link-abbreviated"
                href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Options &amp; settings:<br>
              <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
              <br>
              List rules &amp; etiquette:<br>
              <a moz-do-not-send="true"
                href="http://www.re-wrenches.org/etiquette.htm"
                eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out participant bios:<br>
              <a moz-do-not-send="true"
                href="http://www.members.re-wrenches.org/"
                eudora="autourl">www.members.re-wrenches.org</a><br>
              <br>
              <br>
              No virus found in this incoming message.<br>
              Checked by AVG - <a moz-do-not-send="true"
                href="http://www.avg.com/" eudora="autourl">www.avg.com</a>
              <br>
              Version: 8.5.455 / Virus Database: 271.1.1/4341 - Release
              Date: 04/16/12 18:34:00</blockquote>
            <x-sigsep>
              <p>Miller Solar<br>
                Voice :805-438-5600<br>
                email: <a moz-do-not-send="true"
                  class="moz-txt-link-abbreviated"
                  href="mailto:william@millersolar.com">william@millersolar.com</a><br>
                <a moz-do-not-send="true" href="http://millersolar.com/"
                  eudora="autourl">http://millersolar.com<br>
                </a>License No. C-10-773985<br>
                <br>
              </p>
              <fieldset class="mimeAttachmentHeader"></fieldset>
            </x-sigsep></blockquote>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>List sponsored by Home Power magazine</span><br>
          <span></span><br>
          <span>List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Options &amp; settings:</span><br>
          <span><a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List rules &amp; etiquette:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out participant bios:</span><br>
          <span><a moz-do-not-send="true"
              href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>