<html><head></head><body bgcolor="#FFFFFF"><div>Hi Bill</div><div><br></div><div>One possible fix is to use the other AC input.</div><div>They use separate internal metering, and I have seen one work but the other not.</div><div><br></div><div>If you are not using AGS, then this might work.</div><div><br></div><div>Good luck,</div><div><br></div><div>Jay</div><div><br></div><div>Peltz power<br><br>Sent from my iPad</div><div><br>On Apr 14, 2012, at 6:21 PM, "frenergy" &lt;<a href="mailto:frenergy@psln.com">frenergy@psln.com</a>&gt; wrote:<br><br></div><div></div><blockquote type="cite"><div>

<meta http-equiv="Content-Type" content="text/html; charset=iso-8859-1">
<meta content="MSHTML 6.00.2900.6197" name="GENERATOR">
<style></style>


<div>Wrenches,</div>
<div>&nbsp;</div>
<div>&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp; I have a customer that may be having 
some issues with the reliability of his 11 year old Trace4024.&nbsp; If my 
current fix doesn't solve the problem, I have suggested having the unit fixed, 
which I think still happens on these puppies. I have also suggested replacing it 
with either an Outback 3524 or a Magnum MS 4024.&nbsp; He is now running a 1 HP 
Submersible pump ala autoformer along with the usual array of&nbsp; house 
loads.</div>
<div>&nbsp;</div>
<div>&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp; The issue is the inverter accepting 
and then rejecting the generator power, which I have been watching recent 
comments here regarding this issue.&nbsp; I have not thoroughly checked out pump 
wiring (was apparently already done by the well/pump guy, whom&nbsp;is 
reputable), but have checked the output of the Kohler 8.5 genny and Hz and 
voltage appear stable with and without load.&nbsp; So far I've gone the route 
of&nbsp;programming in a few less&nbsp;amps on the "battery charging" and 
"AC2&nbsp;IN" functions.&nbsp;&nbsp; The inverter&nbsp;seems to be&nbsp;happy 
with new settings, this new programming was just done a few hours ago.</div>
<div>&nbsp;</div>
<div>&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp; So this may be a more generic 
question for those with more experience than I: Are both the OB and Magnum 
inverters considered equally capable of replacing the Trace? I guess I'm 
thinking mainly of that pump, but are there other considerations?</div>
<div>&nbsp;</div>
<div>&nbsp;&nbsp;&nbsp; &nbsp;&nbsp;&nbsp; Thanks Folks</div>
<div>&nbsp;</div>
<div>Bill</div>
<div>Feather River Solar Electric<br>4291 Nelson St.<br>Taylorsville, CA&nbsp; 
95983<br>530-284-7849/6544 fax</div>
<div><font size="1"><em>solar powered since 1982</em></font></div>
</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>List sponsored by Home Power magazine</span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Options &amp; settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out participant bios:</span><br><span><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></body></html>