    Not necessarily. NEC 2008, 250.32 (B), Exception allows you to use
    the neutral conductor for existing structure so long as several
    requirements are met.<br>
    <br>
    Check it out.<br>
    <br>
    On 4/11/2012 8:41 AM, Aladdin Solar wrote:
    <blockquote cite="mid:40DC5CF8697A48A4B709B912D358A00D@Dell530"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <meta name="GENERATOR" content="MSHTML 8.00.6001.19190">
      <div><font face="Arial" size="2">I meant the question largely to
          be a generic one but I can give you an example:</font></div>
      <div>&nbsp;</div>
      <div><font face="Arial" size="2">Buried conductors are&nbsp;6AWG.
          No&nbsp;additional grounding conductor exists between the main and
          detached building. As Brian Mehalic already responded, the 60A
          subpanel would tough to deal with for inverter sizing. Assume
          the AC disconnect is required near the main meter and so would
          have to disconnect all circuits in the subpanel.</font></div>
      <div>&nbsp;</div>
      <div><font face="Arial" size="2">So say we put a 50A main breaker
          in the 60A subpanel to allow a Fronius IG 3.0 (3000 watt) and
          a string of 12 Sharp ND240s or similar.</font></div>
      <div>&nbsp;</div>
      <div><font face="Arial" size="2">The PV ground would have to hit a
          ground rod at the garage&nbsp;and a grounding conductor would need
          to be buried back&nbsp;for bonding at the main building--right?</font>
      </div>
    </blockquote>