<html><body><span style="font-family:Verdana; color:#000000; font-size:10pt;"><div>Boy, I'm haunted with the notion that we've seen this before.. years ago. I want to say it was a simple fix. might have been something to do with NiCad batteries. Maybe low battery voltage and high start currents. I just don't remember.. maybe I wasn't here then.</div><div><br></div><div>db<br></div><div><br></div><div><br>Dan Brown<br>Foxfire Energy Corp.<br>Renewable Energy Systems<br>(802)-483-2564<br><a href="http://www.Foxfire-Energy.com">www.Foxfire-Energy.com</a><br>NABCEP #092907-44</div><div><br><br></div>
<blockquote id="replyBlockquote" webmail="1" style="border-left: 2px solid blue; margin-left: 8px; padding-left: 8px; font-size:10pt; color:black; font-family:verdana;">
<div id="wmQuoteWrapper">
-------- Original Message --------<br>
Subject: Re: [RE-wrenches] Overcurrent error SW4024<br>
From: Dan Fink &lt;<a href="mailto:danbob88@gmail.com">danbob88@gmail.com</a>&gt;<br>
Date: Thu, March 29, 2012 3:04 pm<br>
To: RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
<br>
Turning on other loads around the shop seems to work here. But we need<br>
to have over 100 watts on (we are using lights) to prevent the<br>
problem. It's a PITA, as it crashes the satellite internet, which<br>
takes 20-60 minutes to boot back up.<br>
<br>
DAN FINK<br>
<br>
On Thu, Mar 29, 2012 at 12:12 PM,  &lt;<a href="mailto:penobscotsolar@midmaine.com">penobscotsolar@midmaine.com</a>&gt; wrote:<br>
&gt; We've seen this type of problem twice with well pumps. Both times, the<br>
&gt; problem was with a short in the load side close to the pump. One was<br>
&gt; occasional, the other constant. Interestingly, running a large generator<br>
&gt; seemed to "fix" the situation to the customer. In both cases, we found the<br>
&gt; short, repaired it and both systems are still working well to this day.<br>
&gt; One used a transformer, the other was a single 4024SW.<br>
&gt;<br>
&gt; Daryl<br>
&gt;<br>
&gt;<br>
&gt;<br>
&gt;&gt; Hi Mac;<br>
&gt;&gt;<br>
&gt;&gt; We are having a similar problem at our metal shop with two stacked<br>
&gt;&gt; SW4024s. They are stacked so that inverter #2 idles until something<br>
&gt;&gt; 240V is turned on -- well pump and welder are the only 240 VAC loads.<br>
&gt;&gt; We are getting an overcurrent error and shutdown by just turning the<br>
&gt;&gt; welder's power switch on -- NOT when starting to weld.<br>
&gt;&gt;<br>
&gt;&gt; Any help from the list appreciated!<br>
&gt;&gt;<br>
&gt;&gt; --<br>
&gt;&gt; Dan Fink,<br>
&gt;&gt; Executive Director;<br>
&gt;&gt; Otherpower<br>
&gt;&gt; Buckville Energy Consulting<br>
&gt;&gt; Buckville Publications LLC<br>
&gt;&gt; NABCEP / IREC accredited Continuing Education Providers<br>
&gt;&gt; 970.672.4342 (voicemail)<br>
&gt;&gt;<br>
&gt;&gt; On Thu, Mar 29, 2012 at 8:25 AM, mac Lewis &lt;<a href="mailto:maclewis1@gmail.com">maclewis1@gmail.com</a>&gt; wrote:<br>
&gt;&gt;&gt; Hello wrenches,<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; I have a customer that I have been working with over the phone. &nbsp;He has<br>
&gt;&gt;&gt; a SW<br>
&gt;&gt;&gt; 4024, with a T240 transformer feeding a 2 HP well pump on a timer. &nbsp; The<br>
&gt;&gt;&gt; system has worked well for years, but recently, he has been getting<br>
&gt;&gt;&gt; overcurrent errors when the well pump starts. &nbsp;It's not every time, but<br>
&gt;&gt;&gt; about every other time. &nbsp;He also did an experiment where he turned off<br>
&gt;&gt;&gt; the<br>
&gt;&gt;&gt; well pump, and gets the overcurrent error just energizing the<br>
&gt;&gt;&gt; transformer.<br>
&gt;&gt;&gt; &nbsp;Does this indicate the transformer is failing? &nbsp;What are other<br>
&gt;&gt;&gt; explanations<br>
&gt;&gt;&gt; for this behavior?<br>
&gt;&gt;&gt;<br>
&gt;&gt;&gt; Thanks for any advice<br>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
<br>

</div>
</blockquote></span></body></html>