    RIch;<br>
    <br>
    I think you're exactly right on your interpretation.&nbsp; Mike Holt's&nbsp;
    "Guide to 2011 NEC requirements for PV..." has an 'author's comment'
    on page 305, that the 120% buss bar rule of article 705 only applies
    if there are loads in the panel.&nbsp; If all slots are filled with PV
    breakers, you're off the hook, at least according to Mike Holt, and
    my self for the little that matters <span class="moz-smiley-s3"><span>
        ;-) </span></span><br>
    Now you have to convince the AHJ, so you might want to show them
    Mike's book on the subject.<br>
    <br>
    Ray Walters<br>
    <br>
    On 1/22/2012 2:13 PM, Rich Nicol wrote:
    <blockquote cite="mid:001a01ccd94a$c1f72a70$45e57f50$@com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1F497D">My
            take on it in that respect is a 200 amp panel, with no
            additional slots other than those for the 4 inverters with
            clear signage that no load circuits are permitted in this
            panel. A second small panel would then be employed if any
            load circuits were required for lighting or monitoring
            devices.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1F497D">Thanks<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;color:#1F497D">Rich<o:p></o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;">From:</span></b><span
style="font-size:10.0pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;">
                <a moz-do-not-send="true"
                  href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
                <a moz-do-not-send="true"
                  href="mailto:[mailto:re-wrenches-bounces@lists.re-wrenches.org]">[mailto:re-wrenches-bounces@lists.re-wrenches.org]</a>
                <b>On Behalf Of </b>William Miller<br>
                <b>Sent:</b> Sunday, January 22, 2012 2:28 PM<br>
                <b>To:</b> RE-wrenches<br>
                <b>Subject:</b> Re: [RE-wrenches] Paralleling Multiple
                Inverter<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p>&nbsp;</o:p></p>
        <p class="MsoNormal">Mark:<br>
          <br>
          I would respectfully disagree, based on my reading.&nbsp; If you
          have code citations that inform me otherwise, I would be very
          grateful to expand my knowledge.<br>
          <br>
          Pending hearing otherwise from you, here is what I know, based
          on 2008 code, and assuming load side connection&nbsp; (2008
          citations in italics):<br>
          <br>
          1. <i>690.64(B)(1) Dedicated Overcurrent and Disconnect. Each
            source<br>
            interconnection shall be made at a dedicated circuit breaker<br>
            or fusible disconnecting means.<br>
            <br>
          </i>Each inverter will require a 40 amp circuit breaker.&nbsp; The
          value of that breaker is calculated by adding a 25% continuous
          duty rating to the maximum AC output, which is 25 amps: 25 *
          1.25 = 31.25.&nbsp; The next breaker size up is 40 amps, so you
          need 40 amp breakers.<br>
          <br>
          <i>2. 690.64(B)(2) Bus or Conductor Rating. The sum of the
            ampere<br>
            ratings of overcurrent devices in circuits supplying power<br>
            to a busbar or conductor shall not exceed 120 percent of the<br>
            rating of the busbar or conductor.<br>
            <br>
          </i>The designer must add the values of the circuit breakers
          to determine the back-feed value.&nbsp; We just calculated the
          circuit breaker size in step 1, above.&nbsp; Four inverters means
          four 40 amp circuit breakers, therefore: 4 * 40 = 160.&nbsp; <br>
          <br>
          3. <i>In systems with panelboards<br>
            connected in series, the rating of the first overcurrent<br>
            device directly connected to the output of a utility
            interactive<br>
            inverter(s) shall be used in the calculations for<br>
            all busbars and conductors.<br>
            <br>
          </i>Therefore the designer must use 160 amps as the total
          back-feed value for all panels and feeders in series all the
          way back to the service.<br>
          <br>
          Mark, I would really appreciate it if you could reply today
          with any information I am missing.&nbsp; I could use my new-found
          knowledge to modify the permit application I am submitting
          tomorrow morning.<br>
          <br>
          Sincerely,<br>
          <br>
          William Miller<br>
          <br>
          PS:&nbsp; I used to think, erroneously, that I need only consider
          the actual maximum AC amperage from a given inverter.&nbsp; Some
          time ago I bid on and started a job based on that fallacy.&nbsp;
          Mid-way into the job the AHJ informed me that my calculations
          were incorrect, that I needed to use the breaker value.&nbsp; This
          job used SB6000 inverters and the value required was 40 amps.&nbsp;
          I researched this thoroughly and discovered they were right.&nbsp;
          In order to comply with 690.640(B), I had to downgrade the
          main breaker at my own expense.&nbsp; The breaker was not
          inexpensive, so this is a lesson I learned the hard way.<br>
          <br>
          This is why I am very interested in any knowledge that might
          prove otherwise in this scenario.<br>
          <br>
          Wm<br>
          <br>
          <br>
          At 10:36 AM 1/22/2012, you wrote:<br>
          <br>
          <o:p></o:p></p>
        <p class="MsoNormal">William,<br>
          <br>
          The SMA6000 @ 240V has an AC output rating of 25A. 4 times 25
          times 1.25<br>
          equals 125 A. If the solar accumulation panel is a dedicated
          load center,<br>
          then the load center, feeder and feeder breaker need only be
          rated to 125 A.<br>
          If the dedicated load center is located in the same building
          as the service,<br>
          then the dedicated load center can be main lug without main
          breaker. If the<br>
          dedicated load center is located on a buidling remote from the
          the service,<br>
          then it will need a main breaker rated at 125A.<br>
          <br>
          &nbsp;<br>
          Mark Frye<br>
          Berkeley Solar Electric Systems<br>
          303 Redbud Way<br>
          Nevada City,&nbsp; CA 95959<br>
          (530) 401-8024<br>
          <a moz-do-not-send="true" href="http://www.berkeleysolar.com/">www.berkeleysolar.com</a>
          <br>
          <br>
          -----Original Message-----<br>
          From: <a moz-do-not-send="true"
            href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a><br>
          [<a moz-do-not-send="true"
            href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]
          On Behalf Of William<br>
          Miller<br>
          Sent: Sunday, January 22, 2012 10:20 AM<br>
          To: RE-wrenches<br>
          Subject: Re: [RE-wrenches] Paralleling Multiple Inverter<br>
          <br>
          Rich:<br>
          <br>
          Here is the first consideration you might want to make:&nbsp; You
          state a value<br>
          of 100 Amps for this system, which I assume is the maximum AC
          output at 240<br>
          VAC (25 Amps) times four inverters.&nbsp; The value of 25 amps per
          inverter is<br>
          irrelevant to your design, however.&nbsp; You must take the 25 amps
          times 1.25<br>
          (for continuous duty) which means your required breaker is 40
          amps (unless<br>
          you can find 35 amps breakers).&nbsp; 40 Amps is the relevant
          value.&nbsp; 40 times 4<br>
          equals 160 amps.&nbsp; Therefore, for purposes of 690.64(B)
          calculations, you<br>
          have a 160 amp system.<br>
          <br>
          Others on this list will no doubt provide advise on how to
          deal with that<br>
          160 amps.<br>
          <br>
          William Miller<br>
          <br>
          _______________________________________________<br>
          List sponsored by Home Power magazine<br>
          <br>
          List Address: <a moz-do-not-send="true"
            href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Options &amp; settings:<br>
          <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a moz-do-not-send="true"
            href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out participant bios:<br>
          <a moz-do-not-send="true"
            href="http://www.members.re-wrenches.org/">www.members.re-wrenches.org</a><br>
          <br>
          No virus found in this incoming message.<br>
          Checked by AVG - <a moz-do-not-send="true"
            href="http://www.avg.com/">www.avg.com</a> <br>
          Version: 8.5.454 / Virus Database: 271.1.1/4158 - Release
          Date: 01/21/12 19:34:00<o:p></o:p></p>
        <p>Miller Solar<br>
          Voice :805-438-5600<br>
          email: <a moz-do-not-send="true"
            href="mailto:william@millersolar.com">william@millersolar.com</a><br>
          <a moz-do-not-send="true" href="http://millersolar.com/">http://millersolar.com<br>
          </a>License No. C-10-773985<o:p></o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>