At 01:48 PM 1/3/2012, you wrote:<br><br>
<blockquote type=cite class=cite cite="">This is a very common way to
install this conduit, so I&nbsp; really would like to know how this
inspector would route wire from the top of a pole down into a trench
while passing through a concrete footer. </blockquote><br><br>
The instruction was to install the elbow above the footer and run pipe
along the top of the concrete, then LB into the trench.&nbsp; This was
not directly told to me by an inspector, but by a NABCEP certified
installer who said he has been forbidden to run pipe through the concrete
by &quot;building departments&quot;.&nbsp; The theory was that the
conduit would weaken the anchor.&nbsp; <br><br>
I've got another pole mount coming up, and wanted to make sure that there
wasn't something I was missing, possibly from the UBC.&nbsp; <br><br>
Thanks to all who helped clear this up.&nbsp; I plan to run the pipe
through the concrete, as always. <br><br>
Drake <br><br>