Allen,<br><br>As far as best practices go, I would route all those conductors and GEC/ECG in the same raceway.&quot; To maintain the shortest electrical time constant in each circuit, the ECG should be routed as closely as possible to the circuit conductors. This routing facilitates the operation on over-current devices&quot;(2011 Nec Handbook). And as far as safety goes I would never rely on the continuity of the conduit to be my EGC. What if it seperatres some how due to thremal expansion or some other unforeseen calamity? I do think SolarPro just ran a great grounding article recently too in regards to the 2011 code changes.<br>
There is also a provision in 690 to combine the EGC&amp;GEC into one conductor (690.47(c)(3).<br><br>I hope this helps,<br><br><br><br><br><div class="gmail_quote">On Tue, Dec 6, 2011 at 3:29 AM, Allen Frishman <span dir="ltr">&lt;<a href="mailto:amfrish@aeonsolar.com">amfrish@aeonsolar.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;"><div style="word-wrap:break-word">Fellow Wrenchers,<div>I know this topic has come up before and I have a understanding but I am looking for best practices advice.</div>
<div><br></div><div>When installing a 50KW or larger 3 phase 208V (WYE Service) Inverter on a roof do you run your Grounding Electrode Conductor in a separate conduit from the 3 hots, and the Equipment Grounding Conductor or do you run it all in the same conduit together.</div>
<div><br></div><div>My thought is to run it all in the same conduit and utilize the metalic conduit as the Equipment Ground instead of running a actual conductor for the EGC.</div><div><br></div><div>All feedback is appreciated.<br>
<div>
<span style="border-collapse:separate;color:rgb(0,0,0);font-family:Helvetica;font-style:normal;font-variant:normal;font-weight:normal;letter-spacing:normal;line-height:normal;text-align:auto;text-indent:0px;text-transform:none;white-space:normal;word-spacing:0px;font-size:medium"><div>
<p class="MsoNormal"><i><span style="font-size:10.5pt;color:black">Al Frishman</span></i><span style="font-size:13.5pt;color:black"><br></span><span style="font-size:13.5pt;color:rgb(3,1,0)">Aeon</span><span style="font-size:13.5pt;color:rgb(255,151,0)">Solar</span><span style="font-size:13.5pt;color:black"></span></p>
<p class="MsoNormal"><i><span style="font-size:10.5pt;color:black"><a href="tel:%28917%29%20699-6641" value="+19176996641" target="_blank">(917) 699-6641</a>- cell</span></i><span style="font-size:10.5pt;color:black"><br>
</span><i><span style="font-size:10.5pt;color:black"><a href="tel:%28888%29%20460-2867" value="+18884602867" target="_blank">(888) 460-2867</a></span></i><span style="font-size:10.5pt;color:black"><br></span><i><span style="font-size:10.5pt;color:black"><a href="http://www.aeonsolar.com/" target="_blank">www.aeonsolar.com</a></span></i></p>
</div></span>
</div>
<br></div></div><br>_______________________________________________<br>
List sponsored by Home Power magazine<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a><br>
<br>
<br></blockquote></div><br><br clear="all"><br>-- <br><b>James B Rudolph<br>NABCEP Certified PV Installer<br><br></b><br>