<html><body><div style="color:#000; background-color:#fff; font-family:arial, helvetica, sans-serif;font-size:12pt"><div><span>Hi rebecca, I assume the inverters are all true 3 phase, to check 20 kW/480/1.73 = 24 amps this is what you expect on each leg.&nbsp; You have 10 of these therefore 240 amps on each leg.&nbsp; Solar is continous so you need x1.25 this is of course 301 amps you need to select a 301 breaker, but I think NEC&nbsp;240.6 will allow a 300 amp.&nbsp; ((sorry I do not have my code book and I am on the road))&nbsp;&nbsp;</span></div><div><span>Good Luck</span></div><div><span>Darryl&nbsp;</span></div><div><br></div><div style="font-family: arial, helvetica, sans-serif; font-size: 12pt;"><div style="font-family: times new roman, new york, times, serif; font-size: 12pt;"><font size="2" face="Arial"><div style="margin: 5px 0px; padding: 0px; border: 1px solid rgb(204, 204, 204); height: 0px; line-height: 0; font-size: 0px;" class="hr"
 contentEditable="false" readonly="true"></div><b><span style="font-weight: bold;">From:</span></b> Mark Frye &lt;markf@berkeleysolar.com&gt;<br><b><span style="font-weight: bold;">To:</span></b> 'Rebekah Hren' &lt;bekahhren@yahoo.com&gt;; 'RE-wrenches' &lt;re-wrenches@lists.re-wrenches.org&gt;<br><b><span style="font-weight: bold;">Sent:</span></b> Wednesday, November 16, 2011 11:43 AM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [RE-wrenches] Sizing 3 phase OCPD - main<br></font><br>
<div id="yiv1192680486">

 
 
<div>
<div dir="ltr" align="left"><span class="yiv1192680486093484017-16112011"><font color="#0000ff" size="2" face="Arial">Rebekah,</font></span></div>
<div dir="ltr" align="left"><span class="yiv1192680486093484017-16112011"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="yiv1192680486093484017-16112011"><font color="#0000ff" size="2" face="Arial">If you knew only the power and voltage, then you would use the 
root of 3 to determine the amps. But since you know the amps, you don't need to 
use the root.</font></span></div>
<div dir="ltr" align="left"><span class="yiv1192680486093484017-16112011"><font color="#0000ff" size="2" face="Arial"></font></span>&nbsp;</div>
<div dir="ltr" align="left"><span class="yiv1192680486093484017-16112011"><font color="#0000ff" size="2" face="Arial">The second equation would be the correct 
one.</font></span></div>
<div dir="ltr" align="left"><span class="yiv1192680486093484017-16112011"></span>&nbsp;<br><span lang="en-us"><font size="2" face="Arial">Mark Frye</font></span> <br><span lang="en-us"><font size="2" face="Arial">Berkeley Solar Electric Systems</font></span> 
<br><span lang="en-us"><font size="2" face="Arial">303 Redbud Way</font> 
<br><span lang="en-us"><font size="2" face="Arial">Nevada City,&nbsp; CA 
95959</font></span></span> <br><span lang="en-us"><font size="2" face="Arial">(530) 
401-8024</font></span> <br><span lang="en-us"></span><a href="http://www.berkeleysolar.com/" rel="nofollow" target="_blank"><span lang="en-us"><u><font color="#0000ff" size="2" face="Arial">www.berkeleysolar.com</font></u></span></a><span lang="en-us"><font size="2" face="Arial">&nbsp;</font></span> </div>
<div>&nbsp;</div><br>
<div dir="ltr" lang="en-us" class="yiv1192680486OutlookMessageHeader" align="left">
<div style="margin: 5px 0px; padding: 0px; border: 1px solid rgb(204, 204, 204); height: 0px; line-height: 0; font-size: 0px;" class="hr" contentEditable="false" readonly="true"></div>
<font size="2" face="Tahoma"><b>From:</b> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <b>On Behalf Of </b>Rebekah 
Hren<br><b>Sent:</b> Wednesday, November 16, 2011 9:36 AM<br><b>To:</b> 
RE-wrenches@lists.re-wrenches.org<br><b>Subject:</b> [RE-wrenches] Sizing 3 
phase OCPD - main<br></font><br></div>
<div></div>
<div style="color: rgb(0, 0, 0); font-family: times new roman, new york, times, serif; font-size: 12pt; background-color: rgb(255, 255, 255);">
<div><span>
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>Hi 
wrenches,&nbsp;</span></div>
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'><br></span></div>
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>I have a 
question about sizing the main OCP breaker for a panel combining the output of 
several true three-phase output inverters. To be precise - 10 of the&nbsp; 
Refusol 20kW, which connect to &nbsp;480V/277 Y with a max output of 24.1 amps, 
each inverter has a 3 pole breaker, line a, b, c and a neutral, which doesn\u2019t 
apparently carry any current. </span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'></span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>Recommended 
interconnection breaker is 35 Amps. Ok fine, but what should the main breaker 
and main panel busbar rating be? </span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'></span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>What I\u2019m not 
sure about is if this is the right equation for the main breaker in a panel 
combining all ten inverter outputs: </span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>10 &nbsp;x 
24.1A x \u221a3 x 1.25&nbsp; = 521.8 A</span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'></span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>or is this the 
right equation:</span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>10 x 24.1A x 
1.25 = 301.25 A</span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'></span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>The busbar 
rating should be easy, once I get the main disco OCPD figured out. 
</span></div> 
<div class="yiv1192680486MsoNormal"><span style='font-family: "Times New Roman";'>Main OCPD + 
(10 x 35)&nbsp; \u2264 120% busbar 
rating</span></div></span></div> 
<div><br></div>
<div><br></div>
<div>Thanks for the help!<br>Rebekah Hren</div></div></div>
</div><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br><br><br></div></div></div></body></html>