<html><body><span style="font-family:Verdana; color:#000000; font-size:10pt;"><div>William, the only explanation that I have found for using THWN-2 in conduit run through the attic is that during the day as the temperature in the attic increases, the air in the conduit expands, at night the opposite effect&nbsp;happens, the temperature in the attic decreases and the volume of air in the conduit contracts&nbsp;with the potential to bring&nbsp;in what ever climate conditions exist outside the conduit (In FL this could be humid air).</div>
<div>&nbsp;</div>
<div>Over time if there is humid air present, this could form condensation in the conduit or NEMA 4 rated enclosure, hence the need for wire and connections rated for a wet location.</div>
<div>&nbsp;</div>
<div>I have seen photos at inspectors meetings&nbsp;of NEMA 4 enclosures and conduit that contained water although I am not sure how often this would normally happen.<BR></div>
<div><BR></div>
<div><SPAN style="FONT-SIZE: 8pt"><SPAN style="COLOR: #3366ff"><STRONG><SPAN style="COLOR: #0000ff">Jamie Johnson<BR>NABCEP Certified PV Technical Sales Professional<BR>NABCEP Certified Solar PV Installer<BR><BR>General Manager</SPAN></STRONG></SPAN></SPAN></div>
<div><SPAN style="FONT-SIZE: 8pt"><SPAN style="COLOR: #3366ff"><STRONG><SPAN style="COLOR: #0000ff">SOLAR POWER ELECTRIC</SPAN></STRONG></SPAN></SPAN></div>
<div><SPAN style="FONT-SIZE: 8pt"><SPAN style="COLOR: #3366ff"><STRONG></STRONG></SPAN></SPAN></div>
<div><SPAN style="FONT-SIZE: 8pt"><SPAN style="COLOR: #3366ff"><STRONG><SPAN style="COLOR: #0000ff"><IMG title="signature image" border=0 alt="" src="cid:sigimg1@93beb42850e9a2ad2cfdd26bd2e296d5"></SPAN></STRONG></SPAN></SPAN></div>
<div>&nbsp;</div>
<div>&nbsp;</div>
<BLOCKQUOTE style="BORDER-LEFT: blue 2px solid; PADDING-LEFT: 8px; FONT-FAMILY: verdana; COLOR: black; MARGIN-LEFT: 8px; FONT-SIZE: 10pt" id=replyBlockquote webmail="1">
<DIV id=wmQuoteWrapper>-------- Original Message --------<BR>Subject: [RE-wrenches] Wet locations: (was Push-in Wire Connectors)<BR>From: William Miller &lt;<a href="mailto:william@millersolar.com">william@millersolar.com</a>&gt;<BR>Date: Fri, October 21, 2011 10:51 am<BR>To: RE-wrenches &lt;<a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<BR><BR><X-SIGSEP>
<P></X-SIGSEP><FONT size=3>Friends:<BR><BR>I have had plan checkers insist I use wet rated wire on rooftops even though the wire was in either liquid tight or EMT with raintight connectors.&nbsp; I did not need to dispute this because we had specified THHN wire that is also rated THWN for wet locations.&nbsp; This discussion makes me think I should have contradicted the requirement because I am not sure wet rated wire is required inside dry conduit.&nbsp; I will be looking this up.<BR><BR>I feel that you should not let an AHJ impose a requirement that is not in the code because then you become bound to the new stricture.&nbsp; I realize that an AHJ can impose stricter requirements, but I insist that it be in writing, required in advance of the job in question and that it be required universally.&nbsp; Otherwise, it's anarchy.<BR><BR>William Miller<BR><BR><BR>Miller Solar<BR>Voice :805-438-5600<BR>email: <a href="mailto:william@millersolar.com">william@millersolar.com</a><BR><A href="http://millersolar.com/" target=_blank eudora="autourl">http://millersolar.com<BR></A>License No. C-10-773985<BR></FONT>
<HR>
_______________________________________________<BR>List sponsored by Home Power magazine<BR><BR>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><BR><BR>Options &amp; settings:<BR><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><BR><BR>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><BR><BR>List rules &amp; etiquette:<BR><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><BR><BR>Check out participant bios:<BR><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><BR><BR></DIV></BLOCKQUOTE></span></body></html>