    I started using the wet rated wire nuts, because I've found some
    corrosion in old connectors in outdoor boxes. BTW, why don't you
    like the goo filled wire nuts? They seem a decent and cost effective
    solution.<br>
    &nbsp;I agree with your idea that condensation and moisture buildup can
    occur even in a NEMA 4 box, and the issue that I have is that
    breakers and fuse holders in combiner boxes are definitely not wet
    rated. I wonder what happens to the internal workings of a breaker
    after decades in an outdoor box, but considering there are an awful
    lot of them around (at least AC) I guess I'll get&nbsp; another night's
    sleep in our less than perfect world of PV wiring.<br>
    <br>
    Ray<br>
    <br>
    On 10/21/2011 9:05 AM, Jamie Johnson wrote:
    <blockquote
cite="mid:20111021080507.cbd8bec484907cf1a9d3a5fb1ad0b5d1.fa84f31d96.wbe@email03.secureserver.net"
      type="cite"><span style="font-family:Verdana; color:#000000;
        font-size:10pt;">
        <div>William, the only explanation that I have found for using
          THWN-2 in conduit run through the attic is that during the day
          as the temperature in the attic increases, the air in the
          conduit expands, at night the opposite effect&nbsp;happens, the
          temperature in the attic decreases and the volume of air in
          the conduit contracts&nbsp;with the potential to bring&nbsp;in what ever
          climate conditions exist outside the conduit (In FL this could
          be humid air).</div>
        <div>&nbsp;</div>
        <div>Over time if there is humid air present, this could form
          condensation in the conduit or NEMA 4 rated enclosure, hence
          the need for wire and connections rated for a wet location.</div>
        <div>&nbsp;</div>
        <div>I have seen photos at inspectors meetings&nbsp;of NEMA 4
          enclosures and conduit that contained water although I am not
          sure how often this would normally happen.<br>
        </div>
        <div><br>
        </div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong><span
                  style="COLOR: #0000ff">Jamie Johnson<br>
                  NABCEP Certified PV Technical Sales Professional<br>
                  NABCEP Certified Solar PV Installer<br>
                  <br>
                  General Manager</span></strong></span></span></div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong><span
                  style="COLOR: #0000ff">SOLAR POWER ELECTRIC</span></strong></span></span></div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong></strong></span></span></div>
        <div><span style="FONT-SIZE: 8pt"><span style="COLOR: #3366ff"><strong><span
                  style="COLOR: #0000ff"><img title="signature image"
                    alt=""
                    src="cid:part1.09030106.00020307@solarray.com"
                    border="0"></span></strong></span></span></div>
        <div>&nbsp;</div>
        <div>&nbsp;</div>
        <blockquote style="BORDER-LEFT: blue 2px solid; PADDING-LEFT:
          8px; FONT-FAMILY: verdana; COLOR: black; MARGIN-LEFT: 8px;
          FONT-SIZE: 10pt" id="replyBlockquote" webmail="1">
          <div id="wmQuoteWrapper">-------- Original Message --------<br>
            Subject: [RE-wrenches] Wet locations: (was Push-in Wire
            Connectors)<br>
            From: William Miller &lt;<a moz-do-not-send="true"
              href="mailto:william@millersolar.com">william@millersolar.com</a>&gt;<br>
            Date: Fri, October 21, 2011 10:51 am<br>
            To: RE-wrenches &lt;<a moz-do-not-send="true"
              href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
            <br>
            <x-sigsep>
              <p><font size="3">Friends:<br>
                  <br>
                  I have had plan checkers insist I use wet rated wire
                  on rooftops even though the wire was in either liquid
                  tight or EMT with raintight connectors.&nbsp; I did not
                  need to dispute this because we had specified THHN
                  wire that is also rated THWN for wet locations.&nbsp; This
                  discussion makes me think I should have contradicted
                  the requirement because I am not sure wet rated wire
                  is required inside dry conduit.&nbsp; I will be looking
                  this up.<br>
                  <br>
                  I feel that you should not let an AHJ impose a
                  requirement that is not in the code because then you
                  become bound to the new stricture.&nbsp; I realize that an
                  AHJ can impose stricter requirements, but I insist
                  that it be in writing, required in advance of the job
                  in question and that it be required universally.&nbsp;
                  Otherwise, it's anarchy.<br>
                  <br>
                  William Miller<br>
                  <br>
                  <br>
                  Miller Solar<br>
                  Voice :805-438-5600<br>
                  email: <a moz-do-not-send="true"
                    href="mailto:william@millersolar.com">william@millersolar.com</a><br>
                  <a moz-do-not-send="true"
                    href="http://millersolar.com/" target="_blank"
                    eudora="autourl">http://millersolar.com<br>
                  </a>License No. C-10-773985<br>
                </font>
              </p>
              <hr>
              _______________________________________________<br>
              List sponsored by Home Power magazine<br>
              <br>
              List Address: <a moz-do-not-send="true"
                href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Options &amp; settings:<br>
              <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
              <br>
              List rules &amp; etiquette:<br>
              <a moz-do-not-send="true"
                href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out participant bios:<br>
              <a moz-do-not-send="true"
                href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
              <br>
            </x-sigsep></div>
        </blockquote>
      </span>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>