<html><body><div style="color:#000; background-color:#fff; font-family:arial, helvetica, sans-serif;font-size:12pt"><div><span>The interupting rating has to do with the equipment.&nbsp; Each piece of switch gear&nbsp;or breaker has an interupt rating.&nbsp; The service from the utility is capable of delivering a certian amount of current under short circuit conditions.&nbsp; In a large metro area like a downtown loop it may be 200,000 amps&nbsp;at a residenice it is typically less than 10,000 amps.&nbsp; Most residenitial equipment is rated to interupt a short circuit current of 10,000 amps that would occur if a bolted short happened.&nbsp; If the short circuit current exceeds the rating it is possible the equipment could explode and the current would keep flowing.&nbsp;&nbsp;</span></div><div><span></span>&nbsp;</div><div><span>When I was a young man I was working in downtown Mpls, a working man droped a wrench accross some 480 volt bus bars, the
 upstream switch gear exploded, the fuses may have opened but the current keep flowing the transformers blewup two men were killed,&nbsp; the fuses could not interupt the about 200,000 amps &nbsp;</span></div><div><br></div><div style="font-family: arial, helvetica, sans-serif; font-size: 12pt;"><div style="font-family: times new roman, new york, times, serif; font-size: 12pt;"><font size="2" face="Arial"><div style="margin: 5px 0px; padding: 0px; border: 1px solid rgb(204, 204, 204); height: 0px; line-height: 0; font-size: 0px;" class="hr" contentEditable="false" readonly="true"></div><b><span style="font-weight: bold;">From:</span></b> James Rudolph &lt;jamesrudolph99@gmail.com&gt;<br><b><span style="font-weight: bold;">To:</span></b> RE-wrenches &lt;re-wrenches@lists.re-wrenches.org&gt;<br><b><span style="font-weight: bold;">Sent:</span></b> Monday, October 3, 2011 12:53 PM<br><b><span style="font-weight: bold;">Subject:</span></b> [RE-wrenches]
 interrupting current calculations used to determine the interrupting of the AC equipment.<br></font><br><div id="yiv475207067">Dearest Wenches,<br><br>&nbsp;&nbsp;&nbsp; I received an e-mail from PE reviewing one of our projects to build, and this is what they wrote-<br><span style="color: black; font-size: 11pt;"><br>No
interrupting current calculations were included. &nbsp;It is suggested the
utility company be consulted for available at the service entrance and these
values be used to determine the interrupting of the AC equipment.</span><br><br>Does any one out there have experience dealing with this issue, or have the ability to shed some light on this subject.<br><br>Many thanks in advance,<br clear="all">
<br>-- <br><b>James B Rudolph<br>NABCEP Certified PV Installer<br><br></b><br>
</div><br>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br><br><br></div></div></div></body></html>