    On 8/15/2011 6:34 PM, Darryl Thayer wrote:
    <blockquote
      cite="mid:1313458461.78456.YahooMailNeo@web39311.mail.mud.yahoo.com"
      type="cite">
      <div style="color: rgb(0, 0, 0); background-color: rgb(255, 255,
        255); font-family: arial,helvetica,sans-serif; font-size: 12pt;">
        <div style="RIGHT: auto"><span style="RIGHT: auto">Hi wrenches,
            I have been informed off list that my system is not a
            supported configuration, that one <var id="yui-ie-cursor"></var>phase
            can be paralelled, but the other two can not, one only on
            each of the other legs.&nbsp; So unless Outback comes back with
            more&nbsp;info, I was wrong.&nbsp;&nbsp;(mine still works, it was suggested
            I am very lucky)&nbsp; </span></div>
        <div style="RIGHT: auto"><span style="RIGHT: auto"></span>&nbsp;</div>
        <div style="RIGHT: auto"><span style="RIGHT: auto">I have used
            the Apollo in different configurations, stacked in single
            phase, but I have not tried 3 phase stacks.&nbsp;&nbsp;Maybe you could
            conact Apollo.&nbsp;&nbsp;&nbsp;</span></div>
        <div style="RIGHT: auto"><span style="RIGHT: auto"></span>&nbsp;</div>
        <div style="RIGHT: auto"><span style="RIGHT: auto">Darryl&nbsp;</span></div>
        <div style="RIGHT: auto"><br style="RIGHT: auto">
        </div>
      </div>
    </blockquote>
    <br>
    <br>
    If you mean your system in Minneapolis, that is OK because they are
    only paralleled on the input (grid) side.<br>
    <br>
    You can have as many inverters as you want selling back to the grid
    (even on 3 phase) as you did...&nbsp; Just can't parallel<br>
    their outputs for off grid use when the power goes down.&nbsp;&nbsp; Each
    inverter CAN drive its own AC branch load<br>
    though.<br>
    <br>
    boB<br>
    <br>
    <br>
    <br>
    <br>
    <br>
    <br>
    <blockquote
      cite="mid:1313458461.78456.YahooMailNeo@web39311.mail.mud.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:arial,
        helvetica, sans-serif;font-size:12pt">
        <div style="FONT-FAMILY: arial, helvetica, sans-serif;
          FONT-SIZE: 12pt">
          <div style="FONT-FAMILY: times new roman, new york, times,
            serif; FONT-SIZE: 12pt"><font face="Arial" size="2">
              <b><span style="FONT-WEIGHT: bold">From:</span></b> Darryl
              Thayer <a class="moz-txt-link-rfc2396E" href="mailto:daryl_solar@yahoo.com">&lt;daryl_solar@yahoo.com&gt;</a><br>
              <b><span style="FONT-WEIGHT: bold">To:</span></b>
              RE-wrenches <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org">&lt;re-wrenches@lists.re-wrenches.org&gt;</a><br>
              <b><span style="FONT-WEIGHT: bold">Cc:</span></b> Julie
              Haugh <a class="moz-txt-link-rfc2396E" href="mailto:jfh@greenhousepc.com">&lt;jfh@greenhousepc.com&gt;</a><br>
              <b><span style="FONT-WEIGHT: bold">Sent:</span></b>
              Monday, August 15, 2011 10:43 AM<br>
              <b><span style="FONT-WEIGHT: bold">Subject:</span></b> Re:
              [RE-wrenches] Large, off grid<br>
            </font><br>
            <div id="yiv1098454153">
              <div style="BACKGROUND-COLOR: #fff; FONT-FAMILY: arial,
                helvetica, sans-serif; COLOR: #000; FONT-SIZE: 12pt">
                <div><span>Another method is to use the 120 volt VFX
                    3648, with one&nbsp;master and 14 slaves. (15 total, 5&nbsp;in
                    paralled on each leg)&nbsp; Check this with Outback as
                    the 3 phase is different now than it was back in
                    2003.&nbsp; The three phase was the master generated a
                    square wave and each slave would use this to lag
                    either 120 or&nbsp;240 degrees.&nbsp; For standalone not grid
                    tie.&nbsp; I did a multi inverter on standalone 3
                    phase.&nbsp;&nbsp;</span></div>
                <div><span></span>&nbsp;</div>
                <div><span>Also a good source for this might be&nbsp;&nbsp;Julie
                    Haugh &lt;<a moz-do-not-send="true"
                      href="mailto:jfh@greenhousepc.com" rel="nofollow"
                      target="_blank"
                      ymailto="mailto:jfh@greenhousepc.com">jfh@greenhousepc.com</a>&gt;;
                    She has done a lot of work with Outbacks </span></div>
                <div><span>Darryl</span></div>
                <div><br>
                </div>
                <div style="FONT-FAMILY: arial, helvetica, sans-serif;
                  FONT-SIZE: 12pt">
                  <div style="FONT-FAMILY: times new roman, new york,
                    times, serif; FONT-SIZE: 12pt"><font face="Arial"
                      size="2">
                      <b><span style="FONT-WEIGHT: bold">From:</span></b>
                      jay peltz <a class="moz-txt-link-rfc2396E" href="mailto:jay@asis.com">&lt;jay@asis.com&gt;</a><br>
                      <b><span style="FONT-WEIGHT: bold">To:</span></b>
                      RE-wrenches
                      <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org">&lt;re-wrenches@lists.re-wrenches.org&gt;</a><br>
                      <b><span style="FONT-WEIGHT: bold">Sent:</span></b>
                      Friday, August 12, 2011 1:02 PM<br>
                      <b><span style="FONT-WEIGHT: bold">Subject:</span></b>
                      Re: [RE-wrenches] Large, off grid<br>
                    </font><br>
                    Hi Daryl,<br>
                    <br>
                    You might look at the new Outback 8kw 120/240v<br>
                    <br>
                    I know that you can connect up to 10 in parallel,&nbsp; i
                    don't know if you can do it 3 phase however.<br>
                    <br>
                    jay <br>
                    <br>
                    peltz power<br>
                    <br>
                    <br>
                    <br>
                    <br>
                    <br>
                    <br>
                    On Aug 12, 2011, at 8:42 AM, <a
                      moz-do-not-send="true"
                      href="mailto:penobscotsolar@midmaine.com"
                      rel="nofollow" target="_blank"
                      ymailto="mailto:penobscotsolar@midmaine.com">penobscotsolar@midmaine.com</a>
                    wrote:<br>
                    <br>
                    &gt; Hello wrenches,<br>
                    &gt;&nbsp; We have an opportunity to install a very large
                    (60 kw) off grid system<br>
                    &gt; in Mexico. It is currently three phase. I do
                    have the option of<br>
                    &gt; changing out the air conditioners (36 of them)
                    to 120 single phase, but<br>
                    &gt; it is an added layer of complexity/cost that it
                    would be nice to avoid.<br>
                    &gt;&nbsp; The largest off grid system I've done is 21 kw
                    so far, and it was<br>
                    &gt; single phase and fairly straightforward.<br>
                    &gt;&nbsp; Does anyone know of a three phase, off grid
                    inverter than can be<br>
                    &gt; paralleled for 500 (possibly 450) amps oputput.
                    I am currently dealing<br>
                    &gt; with three 120 volt lines (2/0) and a neutral,
                    running to a transformer<br>
                    &gt; to "clean up" the power from the gennie a bit.
                    The client is determined<br>
                    &gt; to do this as he has spent about $500,000.00
                    USD in diesel over the<br>
                    &gt; last 5 years.I would very much like to get that
                    transformer out of the<br>
                    &gt; picture...<br>
                    &gt;&nbsp; I am well versed in the complexities/pitfalls
                    of battery systems this<br>
                    &gt; large. I'm planning on using the Surrette
                    YS-31series to minimize the<br>
                    &gt; footprint, as well as use Water Miser caps and
                    install three separate<br>
                    &gt; deionizing water systems. My issue is the
                    inverters. I have seen a<br>
                    &gt; Korean inverter, Sunsine (<a
                      moz-do-not-send="true"
                      href="http://www.dongeiecos.com/" rel="nofollow"
                      target="_blank">http://www.dongeiecos.com/</a>)
                    that is capable<br>
                    &gt; of this, but I am not sure I want my first
                    install of this inverter to<br>
                    &gt; be 3000 miles away....<br>
                    &gt;&nbsp; Anyone?<br>
                    &gt; <br>
                    &gt; Thanks,<br>
                    &gt; Daryl DeJoy<br>
                    &gt; NABCEP Certified PV installer<br>
                    &gt; Penobscot Solar Design<br>
                    &gt; <br>
                    &gt; _______________________________________________<br>
                    &gt; List sponsored by Home Power magazine<br>
                    &gt; <br>
                    &gt; List Address: <a moz-do-not-send="true"
                      href="mailto:RE-wrenches@lists.re-wrenches.org"
                      rel="nofollow" target="_blank"
                      ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                    &gt; <br>
                    &gt; Options &amp; settings:<br>
                    &gt; <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                      rel="nofollow" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    &gt; <br>
                    &gt; List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                      rel="nofollow" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                    &gt; <br>
                    &gt; List rules &amp; etiquette:<br>
                    &gt; <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
                    &gt; <br>
                    &gt; Check out participant bios:<br>
                    &gt; <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
                    &gt; <br>
                    <br>
                    _______________________________________________<br>
                    List sponsored by Home Power magazine<br>
                    <br>
                    List Address: <a moz-do-not-send="true"
                      href="mailto:RE-wrenches@lists.re-wrenches.org"
                      rel="nofollow" target="_blank"
                      ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
                    <br>
                    Options &amp; settings:<br>
                    <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                      rel="nofollow" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                      rel="nofollow" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List rules &amp; etiquette:<br>
                    <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
                    <br>
                    Check out participant bios:<br>
                    <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
                    <br>
                    <br>
                    <br>
                  </div>
                </div>
              </div>
            </div>
            <br>
            _______________________________________________<br>
            List sponsored by Home Power magazine<br>
            <br>
            List Address: <a moz-do-not-send="true"
              href="mailto:RE-wrenches@lists.re-wrenches.org"
              ymailto="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Options &amp; settings:<br>
            <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out participant bios:<br>
            <a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br>
            <br>
            <br>
            <br>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>