<html>
<body>
<font size=3>boB:<br><br>
I'd like to run the inverters in the normal fashion with generator input
(no PV):&nbsp; (I'd thought these were SW inverters but they are PS
series).<br><br>
1. The inverters power 120 only loads (shared neutral on two feeders) so
the inverters need to be stacked.<br>
2. When the batteries get low, the inverters start the generator.&nbsp;
The inverters transfer through from the generator power to the loads and
charge batteries.<br><br>
Can the PS pair do this with a three phase generator?&nbsp;&nbsp; I am
beginning to think not...<br><br>
William<br><br>
<br>
At 10:56 AM 7/28/2011, you wrote:<br><br>
<br>
<blockquote type=cite class=cite cite>Do you just want to charge
batteries&nbsp; and are these regular&nbsp; 120VAC SWs ??&nbsp;&nbsp;
120/208 ??<br><br>
If so, you should just be able to connect each&nbsp; SW from neutral to
hot. No stacking necessary.<br><br>
A regular SW stacking cable won't work for delta connections because that
assumes<br>
the phases are going to be 180 degrees (120/240) and not 120 degrees
as&nbsp; for 208V delta.<br><br>
There was a 3 phase version of the SWs which required a separate 3-way
cable and<br>
different software in the SW itself.<br><br>
boB<br><br>
<br><br>
<br>
<blockquote type=cite class=cite cite>On Thu, Jul 28, 2011 at 12:23 AM,
William Miller
&lt;<a href="mailto:william@millersolar.com">william@millersolar.com</a>&gt;
wrote:<br>
</font>
<dl>
<dd>Friends:<br><br>

<dd>Is there any way to connect two SW series inverters to two phases of
a three phase generator?&nbsp; It seems to me that one could connect
three SW inverters with the right stacking cable (or am I confusing
Outback inverters with the hub jumper set properly).<br><br>

<dd>Any input is appreciated.<br><br>

<dd>Thanks,<br><br>

<dd>William<br><br>

<dd>William Miller <br>

<dd>Miller Solar<br>

<dd>Voice :<a href="tel:805-438-5600">805-438-5600</a><br>

<dd>email:
<a href="mailto:william@millersolar.com">william@millersolar.com</a><br>

<dd><a href="http://millersolar.com/" eudora="autourl">http://millersolar.com</a><br>

<dd>License No. C-10-773985<br>
</blockquote>
</dl>_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br><br>
No virus found in this message.<br>
Checked by AVG - <a href="'http://www.avg.com'">www.avg.com</a><br>
Version: 10.0.1390 / Virus Database: 1518/3793 - Release Date:
07/28/11</blockquote>
<x-sigsep><p></x-sigsep>
<font size=3>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</font></body>