    Drake,<br>
    I have never seen significant damage due to rust, but ours is a dry
    climate. But we had a real scary pole issue a few years ago.<br>
    <br>
    In 1997, just starting out and before I was licensed, we hired
    another PV pro to install a SW4024 GTWB system for us. He used a
    Romex connector for strain relief on some USE-2 array wiring into an
    array combiner box. The PV input conductors were direct-burial USE,
    not in conduit and without a bonding conductor between the array and
    the BOS. There was a #6 bare from the combiner to a ground rod at
    the array.<br>
    <br>
    The Romex connector pinched through the insulation on one array
    conductor, causing a low-voltage ground fault. This leakage couldn't
    be detected from the BOS in the house. The ground #6 carried this to
    the rod for maybe ten years. It finally failed from electrolytic
    corrosion and weather exposure, and once it did the 6" sch. 40 array
    pole had the electrolytic reaction and began aggressively rusting
    out from the inside. We discovered bubbling of the steel around the
    base of the pole and the tech that day stuck a screwdriver right
    through the pole at the base.<br>
    <br>
    Needless to say, that array was taken down that day. The customer
    poured a base up a foot around the pole, and filled it with rebar
    and concrete, and it's good.<br>
    Allan<br>
    <br>
    <div class="moz-signature">
      <meta http-equiv="content-type" content="text/html;
        charset=ISO-8859-1">
      <title></title>
      <font face="Times New Roman, Times, serif"><b>Allan Sindelar</b></font><br>
      <small><a href="mailto:Allan@positiveenergysolar.com"><font
            color="#000099" face="Times New Roman, Times, serif"><u>Allan@positiveenergysolar.com</u></font></a></small><font
        face="Times New Roman, Times, serif"><br>
        <span style="font-size: 10pt;">NABCEP Certified Photovoltaic
          Installer<br>
          NABCEP Certified Technical Sales Professional<br>
          New Mexico EE98J Journeyman Electrician<br>
          <b>Positive Energy, Inc.</b><br>
          3201 Calle Marie<br>
          Santa Fe, New Mexico 87507<br>
          <b>505 424-1112</b><br>
          <a href="http://www.positiveenergysolar.com/" target="_blank"><u>www.positiveenergysolar.com</u></a><o:p></o:p></span></font>
      <p class="MsoNormal" style="margin-right: 722.25pt;"><span
          style="font-size: 10pt;"><font face="Times New Roman, Times,
            serif"><st1:place w:st="on"><st1:city w:st="on"></st1:city><st1:state
                w:st="on"></st1:state><st1:postalcode w:st="on"></st1:postalcode></st1:place></font><b
            style=""><br>
          </b></span></p>
      <span style="font-size: 10pt;"><br>
      </span> </div>
    <br>
    On 7/27/2011 3:40 PM, Drake wrote:
    <blockquote
      cite="mid:20110727214124.3965DA8061@homiemail-a81.g.dreamhost.com"
      type="cite">
      I've not personally seen any pole mount pipes that were bent or
      broken.&nbsp; Has anyone seen this?&nbsp; How common is it?&nbsp; What
      sort of damage to pole mount arrays is common? <br>
      <br>
      <br>
      At 05:25 PM 7/26/2011, you wrote:<br>
      <blockquote type="cite" class="cite" cite="">I can confirm that
        quite a bit
        of water builds up inside the pipe. <br>
        A few times on rewiring old systems, we used self tapping screws
        to
        attach conduit and combiner boxes to the existing pole, and
        we've had
        water start running out the hole when it was close to the
        ground. This
        was in a dry climate (New Mexico) This was with a rack that
        didn't cap
        the pole, but I was still surprised how much water was in there.
        (gallons)<br>
        Filling with concrete does seem to be a good idea, but I'll
        point out its
        not as easy as it sounds.<br>
        The concrete just pours out the bottom into the footing, as you
        keep
        filling it from the top. Pouring in a foot of gravel in the
        bottom first
        would help, or filling the pipe after the footing dried some
        would do it
        too.<br>
        <br>
        No free lunch,<br>
        <br>
        R. Walters<br>
        <a class="moz-txt-link-abbreviated" href="mailto:ray@solarray.com">ray@solarray.com</a><br>
        Solar Engineer<br>
        <br>
        <br>
        <br>
        <br>
        On Jul 26, 2011, at 2:08 PM, Dave Palumbo wrote:<br>
        <br>
        &gt; Roy, <br>
        &gt; <br>
        &gt; I have heard that the small amount of water from
        condensation will
        be absorbed by the concrete itself. Don't know for an absolute
        fact that
        this is true though.<br>
        &gt; <br>
        &gt; Dave<br>
        &gt; <br>
        &gt; -----Original Message-----<br>
        &gt; From: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a>
        [<a moz-do-not-send="true"
          href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
          eudora="autourl">
          mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On
        Behalf Of Roy
        Rakobitsch<br>
        &gt; Sent: Tuesday, July 26, 2011 3:17 PM<br>
        &gt; To: RE-wrenches<br>
        &gt; Subject: Re: [RE-wrenches] pole mounts<br>
        &gt; <br>
        &gt; I would think that adding concrete partially up the pole
        would cause
        water<br>
        &gt; and condensation to collect near the bottom and not drain
        properly.
        This<br>
        &gt; could possibly lead to freezing and the pipe being blown
        out or
        damaged,<br>
        &gt; even if the top is completely capped. I would think that
        you should
        either<br>
        &gt; completely fill the pipe, or leave it empty with a good
        layer of
        gravel at<br>
        &gt; the bottom to allow it to drain properly. I also have no
        studies to
        back<br>
        &gt; this up, but it was just a thought.<br>
        &gt; <br>
        &gt; Roy Rakobitsch<br>
        &gt; NABCEP Certified Small Wind Installer&reg;<br>
        &gt; NABCEP Certified Solar PV Installer&reg;<br>
        &gt; NYSERDA eligible Small Wind installer<br>
        &gt; Wind/PV Design Engineer<br>
        &gt; Windsine Inc.<br>
        &gt; 631-514-4166<br>
        &gt;
        <a moz-do-not-send="true" href="http://www.windsine.org/"
          eudora="autourl">www.windsine.org</a>
        <br>
        &gt; <br>
        &gt; On Tue, July 26, 2011 3:05 pm, Dave Palumbo wrote:<br>
        &gt;&gt; Todd,<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; We add concrete inside of our steel pipe masts, up to
        grade
        level, in the<br>
        &gt;&gt; interest of having more weight below ground level. I
        wouldn&acirc;&#8364;&#8482;t
        say that<br>
        &gt;&gt; it made the pipe stronger (that better be strong enough
        as is)
        but more<br>
        &gt;&gt; weight down low will help keep it rooted in a big wind
        event.<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; Dave<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; From: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</a><br>
        &gt;&gt;
        [<a moz-do-not-send="true"
          href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
          eudora="autourl">
          mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On
        Behalf Of<br>
        &gt;&gt; <a class="moz-txt-link-abbreviated" href="mailto:toddcory@finestplanet.com">toddcory@finestplanet.com</a><br>
        &gt;&gt; Sent: Tuesday, July 26, 2011 2:50 PM<br>
        &gt;&gt; To: RE-wrenches<br>
        &gt;&gt; Subject: [RE-wrenches] pole mounts<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; Wrenches,<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; Fact or fiction: Adding concrete to the inside of a
        pole mount
        pipe makes<br>
        &gt;&gt; it stronger.<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; Thanks,<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; Todd<br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt;&gt; Sent from Finest Planet WebMail.<br>
        &gt;&gt; <br>
        &gt;&gt; _______________________________________________<br>
        &gt;&gt; List sponsored by Home Power magazine<br>
        &gt;&gt; <br>
        &gt;&gt; List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
        &gt;&gt; <br>
        &gt;&gt; Options &amp; settings:<br>
        &gt;&gt;
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
        <br>
        &gt;&gt; <br>
        &gt;&gt; List-Archive:<br>
        &gt;&gt;
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
        &gt;&gt; <br>
        &gt;&gt; List rules &amp; etiquette:<br>
        &gt;&gt;
        <a moz-do-not-send="true"
          href="http://www.re-wrenches.org/etiquette.htm"
          eudora="autourl">
          www.re-wrenches.org/etiquette.htm</a><br>
        &gt;&gt; <br>
        &gt;&gt; Check out participant bios:<br>
        &gt;&gt;
        <a moz-do-not-send="true"
          href="http://www.members.re-wrenches.org/" eudora="autourl">
          www.members.re-wrenches.org</a><br>
        &gt;&gt; <br>
        &gt;&gt; <br>
        &gt; <br>
        &gt; <br>
        &gt; <br>
        &gt; <br>
        &gt; <br>
        &gt; <br>
        &gt; _______________________________________________<br>
        &gt; List sponsored by Home Power magazine<br>
        &gt; <br>
        &gt; List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
        &gt; <br>
        &gt; Options &amp; settings:<br>
        &gt;
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
        <br>
        &gt; <br>
        &gt; List-Archive:
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
        &gt; <br>
        &gt; List rules &amp; etiquette:<br>
        &gt;
        <a moz-do-not-send="true"
          href="http://www.re-wrenches.org/etiquette.htm"
          eudora="autourl">
          www.re-wrenches.org/etiquette.htm</a><br>
        &gt; <br>
        &gt; Check out participant bios:<br>
        &gt;
        <a moz-do-not-send="true"
          href="http://www.members.re-wrenches.org/" eudora="autourl">
          www.members.re-wrenches.org</a><br>
        &gt; <br>
        &gt; _______________________________________________<br>
        &gt; List sponsored by Home Power magazine<br>
        &gt; <br>
        &gt; List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
        &gt; <br>
        &gt; Options &amp; settings:<br>
        &gt;
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
        <br>
        &gt; <br>
        &gt; List-Archive:
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
        &gt; <br>
        &gt; List rules &amp; etiquette:<br>
        &gt;
        <a moz-do-not-send="true"
          href="http://www.re-wrenches.org/etiquette.htm"
          eudora="autourl">
          www.re-wrenches.org/etiquette.htm</a><br>
        &gt; <br>
        &gt; Check out participant bios:<br>
        &gt;
        <a moz-do-not-send="true"
          href="http://www.members.re-wrenches.org/" eudora="autourl">
          www.members.re-wrenches.org</a><br>
        &gt; <br>
        <br>
        _______________________________________________<br>
        List sponsored by Home Power magazine<br>
        <br>
        List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
        <br>
        Options &amp; settings:<br>
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
        <br>
        <br>
        List-Archive:
        <a moz-do-not-send="true"
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
          eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
        <br>
        List rules &amp; etiquette:<br>
        <a moz-do-not-send="true"
          href="http://www.re-wrenches.org/etiquette.htm"
          eudora="autourl">
          www.re-wrenches.org/etiquette.htm</a><br>
        <br>
        Check out participant bios:<br>
        <a moz-do-not-send="true"
          href="http://www.members.re-wrenches.org/" eudora="autourl">
          www.members.re-wrenches.org</a></blockquote>
      <x-sigsep>
        <p>
          <font size="2">Drake
            Chamberlin<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab>
            <br>
            ATHENS ELECTRIC<br>
            OH License
            44810<x-tab>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;</x-tab><br>
            CO license 3773<br>
            NABCEP Certified PV<br>
          </font></p>
        <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
      </x-sigsep></blockquote>
  </body>
</html>