<font size=3>Lars:<br><br>
I have been dealing with the same issue for an on-grid scenario.&nbsp; We
were asked to bid a large installation to cover the idle losses of poorly
selected transformers.&nbsp; Before we bid the project, we first looked
at why the client's electric bills were so high.&nbsp; We found that
changing out his transformers would save him considerable power.&nbsp; We
are waiting for that to be accomplished and then we will bid on a smaller
system.&nbsp; Here is the scenario:<br><br>
The customer built a new straw bale home 2,000 feet from his meter.&nbsp;
The electrician ordered two large (75KVA), standard-wound transformers to
step up to 600 VAC and then down to 120/240.&nbsp; The customer's
electric bill went from ~$50/month to ~$200/month and he has yet to move
his laundry equipment into his new house.<br><br>
Turns out the transformers had a large idle loss.&nbsp;&nbsp; Using less
electricity did not help this customer.&nbsp; We had an electrical
engineer do an analysis. Answer:&nbsp; Changing the large&nbsp;
transformers to custom-wound 15KVA units would reduce the monthly bill
enough to pay-off in 5.4 years.<br><br>
Installing standard transformers in step-up / step-down configuration is
a mistake.&nbsp; Voltage drop and in-rush problems occur (I have
experienced the in-rush problems and they can be difficult to
resolve).&nbsp; I have attached a white paper that explains.<br><br>
Good luck,<br><br>
William Miller<br><br>
<br>
At 07:42 AM 7/25/2011, you wrote:<br><br>
<blockquote type=cite class=cite cite>Wrenches,<br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
I recently installed three \u201cultra -efficient\u201d step up-down transformers
on an off grid micro grid project with a 1500\u2019 wire run. The grid is
powered by a an old SW4024(120v) output, stepped up to 480v, and stepped
down to 240v at two locations. I was told by the manufacturer that they
were \u201c99% efficient under a full load\u201d, but upon firing up the system, I
found a NO LOAD AMPEREAGE OF 15.6 amps!!! Needless to say, a completely
unworkable situation for an off grid scenario, as the 840ah battery would
be drained in a couple of hours before anything was turned on. I\u2019m
wondering if anyone out there has either found off grid friendly step
up-down transformers, or if I\u2019m just screwed and need to pull parallel
4/0 runs (probably the price of a new car) to fix the problem. 
HELP!<br>
&nbsp;<br>
<b><i>Lars Ortegren<br>
</i></b>&nbsp;</blockquote>