<div>At 14:52 -0700 28/4/11, Starlight Solar, Larry Crutcher
wrote:</div>
<blockquote type="cite" cite><font face="Arial"
size="-1">....&quot;Until now&quot;?.....</font></blockquote>
<blockquote type="cite" cite><font face="Arial" size="-1">For
proper&nbsp;VRLA battery charging, once it is full, you MUST reduce
the voltage. It does not matter that you are opportunity charging.
What if your turbine is making power 24/7?&nbsp;The voltage will still
need to be reduced after a few hours or have a fixed&nbsp;voltage
setting. I don't think you are ungrateful but&nbsp;again I encourage
you to re-read this thread and the manufacturers instructions. It's
all there.</font></blockquote>
<blockquote type="cite" cite>&nbsp;</blockquote>
<div><br></div>
<div>OK thanks for driving that home.&nbsp; My previous message was
maybe a bit provocative, trying to get to the key issues.&nbsp; The
manufacturers instructions are a bit confusing in places &quot;The
charger can maintain the current I1 indefinitely or until the charger
is shut off or unplugged. This stage is ideal to maintain battery
state of charge....&quot;(Rolls FAQ)&nbsp; The Fullriver instructions
offer two methods where the final voltage is either below or above the
absorb level.&nbsp; In both methods there are criteria that are
unusual for small system charge controllers.</div>
<div><br></div>
<div>It's not going to be possible to follow these instructions
accurately with opportunity charging.&nbsp; For example the initial
charge will likely be outwith (below) the specified range of
currents.&nbsp; It is unlikely that there will be a shunt to measure
current, or a system to monitor dV/dt to determine the transition
points between stages in the process.&nbsp; Nothing will be constant&nbsp;
(except for a programmable voltage limit, given adequate wind/sun) and
there is no assurance that the battery will be fully charged or
discharged to any known level.</div>
<div><br></div>
<div>&nbsp;You state that &quot;<font face="Arial" size="-1">Once you
have programmed the 2512iX charge controller from the IPN Pro, the
controller retains the information and can be installed as a
stand-alone unit</font>&quot;&nbsp; However this does not come with a
battery shunt that I can see.&nbsp; And it's primarily a MPPT solar
controller, with some sort of load control that may or may not be
suitable for wind diversion (which can be done with the 'duo' I
know).&nbsp; The Tristar offers simple diversion load control suitable
for both wind and solar inputs, with a float setting that takes over
(by default) after one hour of absorb time.&nbsp; Whist this is not
likely to fit the manufacturers curves exactly it does seem likely to
do a reasonable job of charging the battery whilst preventing the
balloon of gas in your dramatic photo.</div>
<div><br></div>
<div>I will read the document that you reference (about thermal
runaway) carefully.&nbsp; I am sorry if I seem a slow learner.&nbsp;
This list is an invaluable resource for the industry.&nbsp; I like to
ask naive questions and I get a deeper understanding as a result.
Thanks to all.</div>