<font size=3>Dan:<br><br>
Just to be clear, I am not suggesting that Kirk draw anything. I suggest
he refer to the drawing identified as Figure 690.1(B) in the 2008
NEC.<br><br>
If the inspector will still not accept the facts, there is usually an
appeal process.<br><br>
I'm all for being polite, but I am also in favor of not letting an
ignorant inspector take advantage of me or my clients.<br><br>
William<br><br>
<br><br>
At 05:50 AM 4/10/2011, you wrote:<br><br>
<blockquote type=cite class=cite cite>William's suggestion for a clearly
drawn one-line<br>
is also excellent.<br><br>
In the end, however, as we all know, it's the AHJ's<br>
interpretation that prevails (right or wrong).<br><br>
<br>
Dan<br><br>
<br>
--- On Sun, 4/10/11, Kirk Herander, VSE &lt;kirk@vtsolar.com&gt;
wrote:<br><br>
&gt; From: Kirk Herander, VSE &lt;kirk@vtsolar.com&gt;<br>
&gt; Subject: Re: [RE-wrenches] 690.4 (B) ???<br>
&gt; To: conradg@cape.com, &quot;'RE-wrenches'&quot;<br>
&gt; &lt;re-wrenches@lists.re-wrenches.org&gt;<br>
&gt; Date: Sunday, April 10, 2011, 7:26 AM<br>
&gt; My situation does not concern AC and DC in the same<br>
&gt; raceway. It concerns an AC conductor from the utility<br>
&gt; main panel to a load subpanel, and a separate AC<br>
&gt; inverter output from an inverter combiner panel, back<br>
&gt; to the main panel, not being allowed in the same<br>
&gt; conduit - at least that's the interpretation<br>
&gt; of 690.4(B) of the 2008 NEC by my inspector.<br>
&gt; <br>
&gt; Kirk Herander<br>
&gt; Vermont Solar Engineering<br>
&gt; 802.863.1202<br>
&gt; NABCEP(tm) Certified Solar Installer<br>
&gt; NYSERDA-eligible Installer<br>
&gt; VT Solar Incentive Program Partner<br><br>
<br><br>
&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; <br>
_______________________________________________<br>
</blockquote>
<x-sigsep><p></x-sigsep>
William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>