<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=453300802-01042011>Sigh...</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=453300802-01042011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=453300802-01042011>After talking with Generac today I went ahead and 
ordered the ~$1,200 worth of 400A fused disconnect to put upstream of their 400A 
ATS to protect it from the 480A of combined main breaker/PV back feed breaker 
that I want to install. Of course their literature says that with a 600A circuit 
breaker installed on the line side, the switch will withstand a hard short on 
the load side just fine. But let us not even think about letting 480A run 
through it for a few hours ever other blue moon. (Well that's what I get for 
saying we should look more at overload than short circuit conditions in these PV 
systems.)</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=453300802-01042011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=453300802-01042011>Still&nbsp;it's not like the&nbsp;my customer has been 
plagued for the last 13 years with nuisance tripping of the existing 400A main 
breaker because they tend to plug in one too many hair dryers....but...future 
load expansion and uncontrolled recpticals loads...they can be a problem, so 
better safe than sorry.</SPAN></FONT></DIV>
<DIV><FONT color=#0000ff size=2 face=Arial></FONT>&nbsp;</DIV>
<DIV><SPAN class=453300802-01042011><FONT color=#0000ff size=2 face=Arial>So now 
I see,&nbsp;I have to do what I have to do if I want to be even half as good an 
electrican as my NABCEP certification says I am.</FONT></SPAN></DIV>
<DIV><SPAN class=453300802-01042011></SPAN>&nbsp;<BR><SPAN lang=en-us><FONT 
size=2 face=Arial>Mark Frye</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
face=Arial>Berkeley Solar Electric Systems</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT size=2 face=Arial>303 Redbud Way</FONT></SPAN> <BR><SPAN 
lang=en-us><FONT size=2 face=Arial>Nevada City,&nbsp; CA 95959</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT size=2 face=Arial>(530) 401-8024</FONT></SPAN> 
<BR><SPAN lang=en-us></SPAN><A href="http://www.berkeleysolar.com/"><SPAN 
lang=en-us><U><FONT color=#0000ff size=2 
face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN lang=en-us><FONT 
size=2 face=Arial>&nbsp;</FONT></SPAN> </DIV>
<DIV>&nbsp;</DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> re-wrenches-bounces@lists.re-wrenches.org 
[mailto:re-wrenches-bounces@lists.re-wrenches.org] <B>On Behalf Of </B>Mark 
Frye<BR><B>Sent:</B> Sunday, March 27, 2011 8:38 AM<BR><B>To:</B> 
'RE-wrenches'<BR><B>Subject:</B> Re: [RE-wrenches] Generator and 
Enphase<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>Larry,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>There are alot of ways to skin that 
cat.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>Here is what I am doing on my job.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>I have a 400A main disconnect with a feeder running 
directly to a 400 ATS then to a 400A main lug dedicated load center under the 
switch. All conductors are double - 250 mcm.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>I am going to tap the feeder on the line side, inside 
the ATS cabinet, using a ten foot feeder tap of #3 running to a new 100A breaker 
enclosure with an 80A breaker. From there I will go to a new 150A main lug load 
center with 95A worth of PV backfeed breakers.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>I really am enjoying this one because it brings up so 
many interesting Code quandaries.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>In my mind I am extending the premise wiring and 
interconnecting at the new load center which is on the line side of the ATS. 
Some folks might take issue with this, arguing that the "PV" circuit begins at 
the tap in the ATS and as such is not at a dedicated OCPD. Some folks have 
argued that feeder tap rules themselve do not apply to PV circuits. In any case, 
the new 150A load center is not dedicated solely to backfeeding the PV, there 
are other loads connected there. This is why I see it as an extension of the 
premise wiring and as the point of interconnect of the PV 
circuit.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>Interestingly enough, in order to follow NEC 2008, I 
will have to place the PV backfeed breakers at the bottom of the new 150A load 
center.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>But here is where it gets interesting. Taking the ATS 
out of the picture for a moment, the existing 400A main lug load center is now 
feed with through the main lug with a total of 480A of supply breakers. This 
complies with NEC 2008 vis-a-vis the 120% allowance for conductors and busbars. 
In this case it does sort of make it seem silly to go through the trouble of 
putting the backfeed breakers on the bottom of the 150A load center. Especially 
when thinking back, the whole idea of putting the breaker at the bottom of the 
load center was that you could then have PV backfeed equal to the full rating of 
load center busbar. Funny how things work out.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011></SPAN></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
class=546440715-27032011>Anyway, the real question comes up when we bring the 
ATS back into the picture. The 400A ATS will see the same 480A of supply 
breakers as the conductors and busbar of the 400A load center. Here is where I 
am taking&nbsp;leap of faith that the AHJ will agree with me that the same 120% 
allowance given to the conductors and load center will be given to ATS 
itself.</SPAN></FONT></DIV>
<DIV><BR><SPAN lang=en-us><FONT size=2 face=Arial>Mark Frye</FONT></SPAN> 
<BR><SPAN lang=en-us><FONT size=2 face=Arial>Berkeley Solar Electric 
Systems</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>303 Redbud 
Way</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 face=Arial>Nevada 
City,&nbsp; CA 95959</FONT></SPAN> <BR><SPAN lang=en-us><FONT size=2 
face=Arial>(530) 401-8024</FONT></SPAN> <BR><SPAN lang=en-us></SPAN><A 
href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
lang=en-us><FONT size=2 face=Arial>&nbsp;</FONT></SPAN> </DIV></BODY></HTML>