<html><head></head><body style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><div>Kent,</div><div><br></div><div>Situations vary but this one line helps a lot, thanks.</div><div><br></div><div>So, &nbsp;"To PV System" would go to the output of a grid tie inverter and "To Backed Up Loads" would go to the AC IN (transfer switch) of a battery inverter.&nbsp;</div><div><br></div><div>I have been going to homes with existing 100A gen/utility ATS and wondering if I could keep it as is and be able to add a grid tie battery backup to it (using same backup loads). This schematic would work in that situation as well but wouldn't have the "To Non-Backed UP Loads" tap.</div><div><br></div><div><br></div><div><div><div>
<span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: medium; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-align: auto; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; "><span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: medium; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; "><span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: medium; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><span class="Apple-style-span" style="border-collapse: separate; color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px; "><div style="word-wrap: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space; "><div>Larry Liesner</div><div>Wirewiz</div><div>Westport, CT</div><div>Phone: 203-644-2404</div><div>Fax: 203-557-0556</div><div><a href="mailto:wirewiz@gmail.com">wirewiz@gmail.com</a></div><div><a href="http://www.wire-wiz.com">www.wire-wiz.com</a></div><div><span class="Apple-style-span" style="font-size: medium; "><br></span></div></div></span></div></span></div></span></div></span></span></span><br class="Apple-interchange-newline">
</div>
<br><div><div>On Mar 27, 2011, at 2:36 PM, Kent Osterberg wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite">
<div bgcolor="#ffffff" text="#000000">
Larry,<br>
<br>
Situations vary so much that this might not be very useful. But here
you go. The attached sketch shows how we recently connected a customer
that had a backup generator and transfer switch that wasn't service
rated. There were nice gutters existing from the original install so
accessing points to tap conductors wasn't difficult. We could have
connected the inverters to the non-backed upped loads panel instead,
but the utility requires an accessible disconnect by the meter so it
was more convenient to just get into the gutter.<br>
<br>
Kent Osterberg<br>
Blue Mountain Solar<br>
<br>
<br>
<br>
<a class="moz-txt-link-abbreviated" href="mailto:wirewiz@gmail.com">wirewiz@gmail.com</a> wrote:
<blockquote cite="mid:D2B833A6-683E-4066-9FD7-42FA905103AC@gmail.com" type="cite">Kent, Jason, or anyone else
  <div><br>
  </div>
  <div>Would you a have a simple one-line you could share for wiring
the inverter on the utility side of the transfer switch?&nbsp;</div>
  <div><br>
  </div>
  <div>Thank you.</div>
  <div><br>
  <div><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-size: medium; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; "><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-size: medium; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; "><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-size: medium; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; ">
  <div style=""><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; ">
  <div style=""><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; ">
  <div style=""><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-size: 12px; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; ">
  <div style="">
  <div>Larry Liesner</div>
  <div>Wirewiz</div>
  <div>Westport, CT</div>
  <div>Phone: 203-644-2404</div>
  <div>Fax: 203-557-0556</div>
  <div><a moz-do-not-send="true" href="mailto:wirewiz@gmail.com">wirewiz@gmail.com</a></div>
  <div><a moz-do-not-send="true" href="http://www.wire-wiz.com/">www.wire-wiz.com</a></div>
  <div><span class="Apple-style-span" style="font-size: medium;"><br>
  </span></div>
  </div>
  </span></div>
  </span></div>
  </span></div>
  </span></span></span><br class="Apple-interchange-newline">
  </div>
  <br>
  <div>
  <div>On Mar 26, 2011, at 6:04 PM, Jason Szumlanski wrote:</div>
  <br class="Apple-interchange-newline">
  <blockquote type="cite"><span class="Apple-style-span" style="border-collapse: separate; font-family: Helvetica; font-style: normal; font-variant: normal; font-weight: normal; letter-spacing: normal; line-height: normal; orphans: 2; text-indent: 0px; text-transform: none; white-space: normal; widows: 2; word-spacing: 0px; font-size: medium;">
    <div bgcolor="white" link="blue" vlink="purple" lang="EN-US">
    <div class="WordSection1" style="page: WordSection1;">
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);">Weve
explored this strategy many times due to all of the whole house and
critical load generators in Florida. Weve stayed away from the
contactor solution because of the potential for the NC contactor
failing to open, keeping the inverters online when transferred to
generator power. While unlikely, this is a possibility that must be
considered.<o:p></o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);"><o:p>&nbsp;</o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);">The
other issue presented here is that the inverters will shut down every
time the generator exercises.<o:p></o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);"><o:p>&nbsp;</o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);">The
only sure-fire way seems to be wiring the inverter on the utility side
of the transfer switch, as Kent said.<o:p></o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);"><o:p>&nbsp;</o:p></span></div>
    <div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-family: Calibri,sans-serif; color: rgb(31, 73, 125);">Jason
Szumlanski<o:p></o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);">Fafco
Solar</span><span style="font-size: 4pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);"><o:p></o:p></span></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);"><o:p>&nbsp;</o:p></span></div>
    </div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 11pt; font-family: Calibri,sans-serif; color: rgb(31, 73, 125);"><o:p>&nbsp;</o:p></span></div>
    <div>
    <div style="border-style: solid none none; border-top: 1pt solid rgb(181, 196, 223); padding: 3pt 0in 0in;">
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><b><span style="font-size: 10pt; font-family: Tahoma,sans-serif; color: windowtext;">From:</span></b><span style="font-size: 10pt; font-family: Tahoma,sans-serif; color: windowtext;"><span class="Apple-converted-space">&nbsp;</span><a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org" style="color: blue; text-decoration: underline;">re-wrenches-bounces@lists.re-wrenches.org</a><span class="Apple-converted-space">&nbsp;</span>[<a class="moz-txt-link-freetext" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]<span class="Apple-converted-space">&nbsp;</span><b>On Behalf Of<span class="Apple-converted-space">&nbsp;</span></b>Kent Osterberg<br>
    <b>Sent:</b><span class="Apple-converted-space">&nbsp;</span>Saturday,
March 26, 2011 5:56 PM<br>
    <b>To:</b><span class="Apple-converted-space">&nbsp;</span>RE-wrenches<br>
    <b>Subject:</b><span class="Apple-converted-space">&nbsp;</span>Re:
[RE-wrenches] Generator and Enphase<o:p></o:p></span></div>
    </div>
    </div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><o:p>&nbsp;</o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">Mark,<br>
    <br>
I agree it is best to wire the inverters on the utility side of the
transfer switch. When that isn't easy, a normally closed contactor that
is opened by generator voltage, will isolate the inverters from the
generator and allow automatic return to utility operation when the
generator is off.<br>
    <br>
Kent Osterberg<br>
Blue Mountain Solar<br>
    <br>
    <br>
    <br>
Mark Frye wrote:<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">Eric,</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">I
do not have direct experience with this but have been exploring the
issue for a project I am currently doing.</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">My
response will be to take the trouble to interconnect the Enphase
inverters on the line side of the tranfer switch so that the inverters
can never be&nbsp;connected to the generator.</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">Here
are the reasons why:</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">1
- Enphase states that any such application is considered an "off-grid"
application which voids their warrenty. As I am installing under the
California CSI program, I am required to provide a 10 year manufacture
equipment warranty so I cannot afford to install the inverters in a
dis-allowed manner.</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">2
- Enphase states that the waveform of the generator may be "clean"
enough such that the inverter may attempt to syncornize and connect to
it as if it were the utility. If this were to happen Enphase believes
the inverters will ruin the generator regulator before the generator
ruin the inverter. I don't want to be the one to run the experiment to
find out which would be which.</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><span style="font-size: 10pt; font-family: Arial,sans-serif; color: blue;">3
- I considered a contactor on the output of the inverters, such that
the inverters would isolated by a loss of line voltage, requiring some
form of reset. Ulitmately my customer agreed with me that this was an
undesirable constraint on the operation of an otherwise&nbsp;reliable
grid-tied system and it was not clear that this would satify the
warranty issue.</span><o:p></o:p></div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<br>
    <span style="font-size: 10pt; font-family: Arial,sans-serif;">Mark
Frye</span><span class="Apple-converted-space">&nbsp;</span><br>
    <span style="font-size: 10pt; font-family: Arial,sans-serif;">Berkeley
Solar Electric Systems</span><span class="Apple-converted-space">&nbsp;</span><br>
    <span style="font-size: 10pt; font-family: Arial,sans-serif;">303
Redbud Way</span><span class="Apple-converted-space">&nbsp;</span><br>
    <span style="font-size: 10pt; font-family: Arial,sans-serif;">Nevada
City,&nbsp; CA 95959</span><span class="Apple-converted-space">&nbsp;</span><br>
    <span style="font-size: 10pt; font-family: Arial,sans-serif;">(530)
401-8024</span><span class="Apple-converted-space">&nbsp;</span><br>
    <a moz-do-not-send="true" href="http://www.berkeleysolar.com/" style="color: blue; text-decoration: underline;"><span style="font-size: 10pt; font-family: Arial,sans-serif;">www.berkeleysolar.com</span></a><span style="font-size: 10pt; font-family: Arial,sans-serif;">&nbsp;</span><o:p></o:p></div>
    <div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">&nbsp;<o:p></o:p></div>
    </div>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><o:p>&nbsp;</o:p></div>
    <div class="MsoNormal" style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black; text-align: center;" align="center">
    <hr align="center" size="2" width="100%"></div><p class="MsoNormal" style="margin: 0in 0in 12pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;"><b><span style="font-size: 10pt; font-family: Tahoma,sans-serif;">From:</span></b><span style="font-size: 10pt; font-family: Tahoma,sans-serif;"><span class="Apple-converted-space">&nbsp;</span><a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org" style="color: blue; text-decoration: underline;">re-wrenches-bounces@lists.re-wrenches.org</a><span class="Apple-converted-space">&nbsp;</span>[<a moz-do-not-send="true" href="mailto:re-wrenches-bounces@lists.re-wrenches.org" style="color: blue; text-decoration: underline;">mailto:re-wrenches-bounces@lists.re-wrenches.org</a>]<span class="Apple-converted-space">&nbsp;</span><b>On Behalf Of<span class="Apple-converted-space">&nbsp;</span></b>Eric Thomas<br>
    <b>Sent:</b><span class="Apple-converted-space">&nbsp;</span>Saturday,
March 26, 2011 2:09 PM<br>
    <b>To:</b><span class="Apple-converted-space">&nbsp;</span><a moz-do-not-send="true" href="mailto:re-wrenches@lists.re-wrenches.org" style="color: blue; text-decoration: underline;">re-wrenches@lists.re-wrenches.org</a><br>
    <b>Subject:</b><span class="Apple-converted-space">&nbsp;</span>[RE-wrenches]
Generator and Enphase</span><o:p></o:p></p>
    <div style="margin: 0in 0in 0.0001pt; font-size: 12pt; font-family: 'Times New Roman',serif; color: black;">I
have a customer with a "30A Mechanically Interlocked Breaker" for their
generator feed at the main panel. My question is: If the home power is
transferred from utility to generator power, will the backfed PV see
the generator as grid power and sync up and produce? This is a nice
Honda Generator so the power should be fairly clean. Any experiences
are appreciated.<br>
    <br>
Take Care,<br>
    <br>
    <br>
Eric Thomas<br>
Solar Epiphany LLC<br>
(206) 919-3014<br>
    <a moz-do-not-send="true" href="http://www.solarepiphany.com/" target="_blank" style="color: blue; text-decoration: underline;">www.solarepiphany.com</a><br>
    <br>
    <o:p></o:p></div>
    <pre style="margin: 0in 0in 0.0001pt; font-size: 10pt; font-family: 'Courier New'; color: black;"><o:p>&nbsp;</o:p></pre>
    </div>
_______________________________________________<br>
List sponsored by Home Power magazine<br>
    <br>
List Address:<span class="Apple-converted-space">&nbsp;</span><a moz-do-not-send="true" href="mailto:RE-wrenches@lists.re-wrenches.org" style="color: blue; text-decoration: underline;">RE-wrenches@lists.re-wrenches.org</a><br>
    <br>
Options &amp; settings:<br>
    <a moz-do-not-send="true" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" style="color: blue; text-decoration: underline;">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
    <br>
List-Archive:<span class="Apple-converted-space">&nbsp;</span><a moz-do-not-send="true" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" style="color: blue; text-decoration: underline;">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
    <br>
List rules &amp; etiquette:<br>
    <a moz-do-not-send="true" href="http://www.re-wrenches.org/etiquette.htm" style="color: blue; text-decoration: underline;">www.re-wrenches.org/etiquette.htm</a><br>
    <br>
Check out participant bios:<br>
    <a moz-do-not-send="true" href="http://www.members.re-wrenches.org/" style="color: blue; text-decoration: underline;">www.members.re-wrenches.org</a><br>
    <br>
    </div>
    </span></blockquote>
  </div>
  <br>
  </div>
  <pre wrap=""><hr size="4" width="90%">
_______________________________________________
List sponsored by Home Power magazine

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org/">www.members.re-wrenches.org</a>

  </pre>
</blockquote>
</div>

<span>&lt;OneLine.JPG&gt;</span>_______________________________________________<br>List sponsored by Home Power magazine<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>Options &amp; settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br><br>List rules &amp; etiquette:<br>www.re-wrenches.org/etiquette.htm<br><br>Check out participant bios:<br>www.members.re-wrenches.org<br><br></blockquote></div><br></div></div></body></html>