On a couple of Enphase systems I monitor regularly, the modules are
oversized compared to the inverters.&nbsp; One system has Sharp 224 W
modules and M-190s (capable of producing 199 W).&nbsp; The array is a
ground mount at a 30 degree tilt at 39+ degrees latitude.&nbsp; <br><br>
When the system was new in the autumn, I noticed two days of some
clipping.&nbsp; Since then, none.&nbsp; In the summer, when the sun angle
is better, the heat will keep the wattage down so clipping will very
seldom occur.&nbsp; The modules will not be close to STC, so the
inverters should not be pushed to their maximum.<br><br>
The same is true of string inverters.&nbsp; Since real power of the
modules in generally significantly below the nameplate, inverters will
generally not run at maximum power.&nbsp;&nbsp; When we take in all the
factors affecting the actual array power, I think that 120% over sizing
from nameplate wattage is generally safe. <br><br>
Drake<br><br>
<br>
At 09:14 PM 1/19/2011, you wrote:<br>
<blockquote type=cite class=cite cite="">David,<br>
<br>
Thanks for sharing that paper.&nbsp; The labeling the graphs for the
10-second and 1-minute data in Freiburg appears to be reversed - the one
minute averaging seems to have more data in all of the bins above 1000
W/sq m.&nbsp; Basically, these graphs show that irradiance observations
above 1100 watts per square meter are fleeting and disappear in hourly
averages.&nbsp;&nbsp; Such occurrences are also masked to a small extent
by 1-minute averages.<br>
&nbsp;<br>
Kent Osterberg<br>
Blue Mountain Solar, Inc.<br><br>
<br><br>
David Brearley wrote: <br>
<blockquote type=cite class=cite cite=""><font face="Calibri">This
reminds me of a scholarly article I came across about a year ago while
doing some research. Heres a link to it if anyone is
interested:<br><br>
<a href="http://www.lepten.ufsc.br/publicacoes/solar/eventos/2005/PSC/burger_ruther.pdf">
www.lepten.ufsc.br/publicacoes/solar/eventos/2005/PSC/burger_ruther.pdf</a>
<br><br>
David Brearley, Senior Technical Editor<br>
<i>SolarPro</i> magazine <br>
NABCEP Certified PV Installer <br>
<a href="david.brearley@solarprofessional.htm">
david.brearley@solarprofessional.com</a><br>
Direct: 541.261.6545<br><br>
On 1/19/11 12:29 PM, &quot;Bill Brooks&quot;
&lt;<a href="billbrooks7@yahoo.htm">billbrooks7@yahoo.com</a>&gt;
wrote:<br><br>
</font>
<dl>
<dd><font face="Calibri" color="#1F497D">Kent,<br>

<dd>&nbsp;<br>

<dd>How often were your data records? To capture edge of cloud effects,
you need one-second data. Not many people gather that fast or that much
data on inverters. I dont think there is that much energy in these
spikes, but they are real and make some difference. 15-minute average
data will completely wash out this data.<br>

<dd>&nbsp;<br>

<dd>This is also a deficiency in modeling software since most models are
using hourly data.<br>

<dd>&nbsp;<br>

<dd>Bill.<br>

<dd>&nbsp;<br>
</font><br>

<dd><font face="Tahoma" size=2>From:</b>
<a href="re-wrenches-bounces@lists.re-wrenches.htm">
re-wrenches-bounces@lists.re-wrenches.org</a>
[<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" eudora="autourl">
mailto:re-wrenches-bounces@lists.re-wrenches.org</a>] On Behalf Of
</b>Kent Osterberg<br>

<dd>Sent:</b> Tuesday, January 18, 2011 1:18 PM<br>

<dd>To:</b> Wrenches; Marco Mangelsdorf<br>

<dd>Subject:</b> [RE-wrenches] Inverter oversizing<br>
</font><font face="Times New Roman, Times"><br><br>

<dd>Attached is a graph that I produced to document the effect of various
ratios between the PV array size and the inverter size.&nbsp; I extracted
output power data for a 1020-watt system located in NE Oregon that is on
the Sunny Portal
&lt;<a href="http://www.sunnyportal.com/Templates/PublicPageOverview.aspx?page=85820a73-a347-48fb-b8d1-92e5f9b78ab3&amp;plant=608681a7-ef60-4edb-84ff-07110db0ab6a&amp;splang=en-US">
http://www.sunnyportal.com/Templates/PublicPageOverview.aspx?page=85820a73-a347-48fb-b8d1-92e5f9b78ab3&amp;plant=608681a7-ef60-4edb-84ff-07110db0ab6a&amp;splang=en-US</a>
&gt; . The data are publicly accessible so feel free to run your own
analysis.&nbsp; Better yet, analyze the data for a system near you.&nbsp;
<br><br>

<dd>Using 2009 data, I looked at how much energy would have been lost if
the output was clipped at 800W, 810W, .... 1020W.&nbsp; I used 2009 data
because there was a period in 2010 when the Sunny Webbox didn't have
internet access.&nbsp; At 800 watts, power clipping would have happened
on about 25% of the days.&nbsp; Yet the energy that would have been lost
was only 0.38% of the annual total.&nbsp; <br><br>

<dd>The results shown on this graph aren't universal, results would be a
little different in 2010, it would be different in some other climate, it
would have been different at another elevation, it would be different
with a different array angle, ..., and the module tolerance and inverter
efficiency also effect the results.&nbsp; Modules in this system are
Suntech 170-watt +/-3%.&nbsp; The inverter is Sunnyboy 1800 that&nbsp;
should be operating at close to 93% efficiency.<br><br>

<dd>Kent Osterberg<br>

<dd>Blue Mountain Solar. Inc.<br><br>
</font>
</dl><br>
<pre>


_______________________________________________
List sponsored by Home Power magazine

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a>

Options &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a>

Check out participant bios:
<a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a>

&nbsp;
</pre><font face="Courier New, Courier"></font></blockquote>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">
www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">
www.members.re-wrenches.org</a></blockquote></body>
</html>