<font size=3>Mick:<br><br>
You must have a different manual than I do.&nbsp; Paragraph 5, page 12 of
the 4.01 manual I have does not discuss this subject at all.<br><br>
The passage I have, from page 68 says the following:<br><br>
</font><font size=2>To manually equalize the batteries, AC power must be
available at the <b><i>AC HOT IN 1 </i></b>(utility power) or
<b><i>AC<br>
HOT IN 2 </i></b>(generator) terminals. If utility power is not
available, the generator must be manually started.<br>
The inverter uses this power to start the battery charger and begin the
equalization process. Equalization<br>
will continue to run for the amount of time programmed. When the
equalization process finishes, the<br>
<b><i>FLOAT </i></b>LED will come on (as long as utility or generator
power is still available).<br><br>
</font><font size=3>I thought I could start the generator using the
&quot;ON&quot; function in the Generator menu, but when I do that and
then engage EQ, the generator stops in a few minutes.&nbsp; It is not a
big problem to start from the gen set itself, I just want to know
why.<br><br>
Thanks,<br><br>
William<br><br>
<br><br>
<br><br>
At 03:10 PM 12/22/2010, you wrote:<br>
<blockquote type=cite class=cite cite>I'm not sure which part of the
manual to which you refer, but below is how I interpret the middle of the
fifth paragraph on page 12 of Version 4.01 of the book:<br><br>
If the inverter is set up to remotely control the generator, select
<b><i>ON</i></b> from the <b><i>SET GENERATOR</i></b> menu item. Once the
machine is running, move the cursor beneath the <b><i>EQ</i></b> marker.
The unit should then implement the EQ charge parameters which can be
reviewed under menu heading 10 before shutting the generator
down.<br><br>
The last part of this paragraph confirms that the <b><i>EQ</i></b>
setting can be pre-selected so the controlled overcharge will occur with
the next auto-crank but I agree with you that it's better for the end
user to manually trigger the EQ charge.<br><br>
The first part of this same paragraph confirms that if AC1 is energized
(which could be courtesy of a manually started generator in an off grid
situation) the green button cursor can be moved over to <b><i>EQ</i></b>
as another way of revving up the charge parameters but in this case the
inverter cannot turn off the generator when the EQ charge is completed.
<br><br>
Jolliness,<br><br>
Mick Abraham, Proprietor<br>
<a href="http://www.abrahamsolar.com">www.abrahamsolar.com</a><br><br>
Voice: 970-731-4675<br><br>
<br>
On Wed, Dec 22, 2010 at 3:48 PM, William Miller
&lt;<a href="mailto:william@millersolar.com">william@millersolar.com</a>&gt;
wrote:<br>
</font>
<dl>
<dd>Friends:<br><br>

<dd>I have managed to confuse myself on the proper steps for equalizing
batteries with the SW inverter and I am hoping I can get some
clarification.&nbsp; The instructions indicate you can't start an
equalization manually.&nbsp; Instead it says that you must wait until the
inverter starts automatically after setting the control to EQ.<br><br>

<dd>I very much prefer to have my customers equalize at a time specific
so they monitor the process was successful and know it was
successful.&nbsp; I thought I remembered that you could start the
generator from the control panel and then engage EQ, but with at least
one client, the generator shuts down right away.&nbsp; We made a brief
experiment with starting the generator from the gen set itself and then
engaging EQ.&nbsp; My client was leaving the premises shortly after I
gave these new instructions so we aborted the EQ until another day.&nbsp;
In the meantime, I'd appreciate any input any of you may have as to the
best way to EQ with an SW inverter using the generator input.<br><br>

<dd>Thanks,<br><br>

<dd>William Miller<br><br>
<br>

<dd>PS:&nbsp; This inverter requires a three-wire start connection with
the &quot;glow-stop&quot; setting.<br><br>

<dd>Wm<br><br>
<br>

<dd>Please note new e-mail address and domain:<br><br>
</u>
<dd>William Miller <br>

<dd>Miller Solar<br>

<dd>Voice :805-438-5600<br>

<dd>email:
<a href="mailto:william@millersolar.com">william@millersolar.com</a><br>

<dd><a href="http://millersolar.com/" eudora="autourl">http://millersolar.com</a><br>

<dd>License No. C-10-773985<br><br>

<dd>_______________________________________________<br>

<dd>List sponsored by Home Power magazine<br><br>

<dd>List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br><br>

<dd>Options &amp; settings:<br>

<dd><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>

<dd>List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>

<dd>List rules &amp; etiquette:<br>

<dd><a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a><br><br>

<dd>Check out participant bios:<br>

<dd><a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a><br><br>
<br>

</dl><br>
_______________________________________________<br>
List sponsored by Home Power magazine<br><br>
List Address: RE-wrenches@lists.re-wrenches.org<br><br>
Options &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>
List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" eudora="autourl">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" eudora="autourl">www.re-wrenches.org/etiquette.htm</a><br><br>
Check out participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl">www.members.re-wrenches.org</a><br><br>
<br>
No virus found in this incoming message.<br>
Checked by AVG -
<a href="http://www.avg.com/" eudora="autourl">www.avg.com</a> <br>
Version: 8.5.449 / Virus Database: 271.1.1/3331 - Release Date: 12/22/10
07:34:00</blockquote>
<x-sigsep><p></x-sigsep>
<font size=3><u>Please note new e-mail address and domain:<br><br>
</u>William Miller <br>
Miller Solar<br>
Voice :805-438-5600<br>
email: william@millersolar.com<br>
<a href="http://millersolar.com/" eudora="autourl">http://millersolar.com<br>
</a>License No. C-10-773985<br>
</font></body>
</html>