<font size=3>Phil, Mick and everyone else that replied:<br><br>
Thanks.&nbsp; Great advice and I really appreciate all of you.<br><br>
William Miller<br><br>
<br>
At 10:03 PM 12/22/2010, you wrote:<br><br>
<blockquote type=cite class=cite cite>This was one of the limitations of
the SW. If you want to have an EQ where the generator shuts off when its
finished, you need to do a little trick. Setting the cursor to EQ just
means the system will perform an EQ the next time the genny runs, and
that might be some random time in the future. Setting the cursor to EQ
and manually starting the genny works sort of, but somebody has to stay
around and babysit the system to manually turn the genny off once the
charge is done. Not ideal. <br><br>
If you set the cursor to EQ and then temporarily adjust the two minute
start voltage up to any voltage higher than actual current voltage,
you'll get an auto-start. Since it was started under the inverter's
command, it will turn off once the EQ is finished. <br><br>
Once the genny's running reset the two minute start voltage back to
original. <br><br>
Phil Undercuffler</font></blockquote></body>