<DIV>In the Navy we used to use DC-4, which was a silicone grease made by Dow 
Corning. It has a high melting point. Any of the similar silicone greases would 
probably work, but rather expensive in small quantities  but you only need a 
very thin coat. We used to use it to fill up RF transmitter coax connectors that 
were exposed to salt water  which was almost anyplace on the ship that was 
outside. <A title=http://www4.dowcorning.com/DataFiles/090007c8801e254b.pdf 
href="http://www4.dowcorning.com/DataFiles/090007c8801e254b.pdf">http://www4.dowcorning.com/DataFiles/090007c8801e254b.pdf</A>&nbsp; 
Available also from most electrical, or online at many places. Here in Arizona, 
EVERYTHING gets over 100 ;p</DIV>
<DIV>&nbsp;</DIV>
<DIV>Getting a good seal on the heat shrink is a problem, and there is no real 
good solution  even if you start with a good seal, sharp flexing can break it 
and all you need is a pinhole.</DIV>
<DIV 
style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">
<DIV style="FONT: 10pt tahoma">
<DIV>&nbsp;</DIV>
<DIV style="BACKGROUND: #f5f5f5">
<DIV style="font-color: black"><B>From:</B> <A title=ray@solarray.com 
href="mailto:ray@solarray.com">R Ray Walters</A> </DIV>
<DIV><B>Sent:</B> Tuesday, November 30, 2010 12:53 PM</DIV>
<DIV><B>To:</B> <A title=re-wrenches@lists.re-wrenches.org 
href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
<DIV><B>Subject:</B> Re: [RE-wrenches] Battery Cable REvistied</DIV></DIV></DIV>
<DIV>&nbsp;</DIV></DIV>
<DIV 
style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">We 
use the same inner melt heat shrink, I think. You don't know you have a problem, 
until you cut that pretty heat shrink off 5 years later, and see what is 
happening underneath. 
<DIV>The reason we use the vaseline, is that it remains conductive, so we can 
precoat the connectors before assembling and tightening. (Windy Dankoff taught 
us that one) 
<DIV>I would see the 3M coating as something to spray on after, but I would be 
concerned about using it on contact surfaces before.</DIV>
<DIV>I agree, heat can be an issue, so we use a high temp grease for 
applications were the temp might get over 100 deg F.</DIV>
<DIV>Maybe a combination might work best:&nbsp; grease on the contact surfaces 
before, and 3M spray outside after?</DIV>
<DIV>
<DIV>&nbsp;</DIV>
<DIV><SPAN 
style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-SPACING: 0px 0px; BORDER-COLLAPSE: separate; FONT: 12px helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; COLOR: rgb(0,0,0); WORD-SPACING: 0px; -khtml-text-decorations-in-effect: none; -apple-text-size-adjust: auto" 
class=Apple-style-span>
<DIV>R. Walters</DIV>
<DIV><A href="mailto:ray@solarray.com">ray@solarray.com</A></DIV>
<DIV>Solar Engineer</DIV>
<DIV>&nbsp;</DIV>
<DIV>&nbsp;</DIV><BR class=Apple-interchange-newline></SPAN></DIV>
<DIV>&nbsp;</DIV>
<DIV>
<DIV>On Nov 30, 2010, at 9:47 AM, Warren Lauzon wrote:</DIV><BR 
class=Apple-interchange-newline>
<BLOCKQUOTE type="cite">
  <DIV 
  style="WORD-WRAP: break-word; -webkit-nbsp-mode: space; -webkit-line-break: after-white-space" 
  dir=ltr>
  <DIV dir=ltr>
  <DIV style="FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: 12pt">
  <DIV>We use the inner melt type of heat shrink and have had few problems 
  with it compared to the standard heat shrink. As far as Lead plated lugs, I am 
  not sure I see much advantage to them. Also as far as coatings go, most 
  Vaseline and other standard grease type are way too temperature sensitive, and 
  in hot weather they just melt away  and they are also great dust/bug/dirt 
  gatherers. 3M and others make a spray on coating that hardens somewhat that we 
  have found to be much better. From the 3M website <FONT 
  face="Times New Roman">Scotch Insulating Sprays 1601 and 1602 are 
  electrical-grade, fast-drying enamel sealers and insulators in pressurized 
  cans. 
  <DIV style="DISPLAY: inline" id=learn0><SPAN style="DISPLAY: none" 
  id=full_desc><A onclick="toggleMe('longdescDiv');" 
  href="javascript:void(0);">Full Description <SPAN 
  class=caret></SPAN></A>&nbsp; </SPAN></DIV></FONT><FONT 
  face="Times New Roman">These sealers protect surfaces against weather, 
  moisture, corrosion, oil, alkalies and acids. The sprays can afford easy 
  access to hard-to-reach spots. Use Insulating Spray sealers to spray over 
  insulation on wire and cable splices, as a general-purpose sealer, or for 
  touch-up insulation on motor windings and frames. Sprays are available in 
  clear, red or black.</FONT></DIV>
  <DIV><FONT face="Times New Roman"></FONT>&nbsp;</DIV>
  <DIV><FONT face="Times New Roman">The local Home Depot carries it here, also 
  some electrical distributors.</FONT></DIV>
  <DIV>&nbsp;</DIV>
  <DIV 
  style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">
  <DIV style="FONT: 10pt tahoma">
  <DIV>&nbsp;</DIV>
  <DIV style="BACKGROUND: #f5f5f5">
  <DIV style="font-color: black"><B>From:</B> <A title=ray@solarray.com 
  href="mailto:ray@solarray.com">R Ray Walters</A> </DIV>
  <DIV><B>Sent:</B> Tuesday, November 30, 2010 9:26 AM</DIV>
  <DIV><B>To:</B> <A title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV><B>Subject:</B> Re: [RE-wrenches] Battery Cable 
  REvistied</DIV></DIV></DIV>
  <DIV>&nbsp;</DIV></DIV>
  <DIV 
  style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">HI 
  Mark; 
  <DIV>&nbsp;</DIV>
  <DIV>Where do you get the lead plated lugs? We used to special order tin 
  plated lugs from Del City, but they quit carrying them. 
  <DIV>I found that the grease or vaseline coating was the most important issue, 
  though. Tin plated lugs would corrode just like the unplated ones, except they 
  first would lose their plating.</DIV>
  <DIV>Lead plated lugs might just be the ticket, except you would still have to 
  keep the corrosion from creeping up under the heat shrink to the copper 
  cable.</DIV>
  <DIV>I've had cables with corrosion going up the cable strands for over 6" 
  past the lug. And yes we use heat shrink with the sealing adhesive inside; the 
  corrosion just travels right under it along the surface of the metal. I 
  actually found electrical tape seals better, it just doesn't look near as 
  good, so we still use heat shrink, and coat over the heat shrink with the 
  vaseline (or grease).</DIV>
  <DIV>
  <DIV>&nbsp;</DIV>
  <DIV><SPAN 
  style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: 12px helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto" 
  class=Apple-style-span>
  <DIV>R. Walters</DIV>
  <DIV><A href="mailto:ray@solarray.com">ray@solarray.com</A></DIV>
  <DIV>Solar Engineer</DIV>
  <DIV>&nbsp;</DIV>
  <DIV>&nbsp;</DIV><BR class=Apple-interchange-newline></SPAN></DIV>
  <DIV>&nbsp;</DIV>
  <DIV>
  <DIV>On Nov 30, 2010, at 9:09 AM, Mark Frye wrote:</DIV><BR 
  class=Apple-interchange-newline>
  <BLOCKQUOTE type="cite"><SPAN 
    style="WIDOWS: 2; TEXT-TRANSFORM: none; TEXT-INDENT: 0px; BORDER-COLLAPSE: separate; FONT: medium helvetica; WHITE-SPACE: normal; ORPHANS: 2; LETTER-SPACING: normal; WORD-SPACING: 0px; -webkit-border-horizontal-spacing: 0px; -webkit-border-vertical-spacing: 0px; -webkit-text-decorations-in-effect: none; -webkit-text-size-adjust: auto; -webkit-text-stroke-width: 0px" 
    class=Apple-style-span>
    <DIV lang=EN-US vlink="purple" link="blue">
    <DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
    class=109580316-30112010>I recently worked with a telecom specification that 
    required lead plated copper lugs on the battery side and I have been using 
    the same on my own systems for some time now.</SPAN></FONT></DIV>
    <DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
    class=109580316-30112010></SPAN></FONT>&nbsp;</DIV>
    <DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
    class=109580316-30112010>How important is it to use lead plated lugs on the 
    battery side? Is tin plated copper just as good so long as you coat well 
    with grease etc.?</SPAN></FONT></DIV>
    <DIV dir=ltr align=left><FONT color=#0000ff size=2 face=Arial><SPAN 
    class=109580316-30112010></SPAN></FONT><BR><SPAN lang=en-us><FONT size=2 
    face=Arial>Mark Frye</FONT></SPAN><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><BR><SPAN lang=en-us><FONT size=2 
    face=Arial>Berkeley Solar Electric Systems</FONT></SPAN><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><BR><SPAN lang=en-us><FONT size=2 
    face=Arial>303 Redbud Way</FONT></SPAN><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><BR><SPAN lang=en-us><FONT size=2 
    face=Arial>Nevada City,&nbsp; CA 95959</FONT></SPAN><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><BR><SPAN lang=en-us><FONT size=2 
    face=Arial>(530) 401-8024</FONT></SPAN><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><BR><SPAN lang=en-us></SPAN><A 
    style="COLOR: blue; TEXT-DECORATION: underline" 
    href="http://www.berkeleysolar.com/"><SPAN lang=en-us><U><FONT color=#0000ff 
    size=2 face=Arial>www.berkeleysolar.com</FONT></U></SPAN></A><SPAN 
    lang=en-us><FONT size=2 face=Arial>&nbsp;</FONT></SPAN></DIV>
    <DIV>&nbsp;</DIV>
    <DIV>&nbsp;</DIV>
    <DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
    <HR tabIndex=-1>
    <FONT size=2 face=Tahoma><B>From:</B><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><A 
    style="COLOR: blue; TEXT-DECORATION: underline" 
    href="mailto:re-wrenches-bounces@lists.re-wrenches.org">re-wrenches-bounces@lists.re-wrenches.org</A><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN>[mailto:re-wrenches-bounces@lists.re-wrenches.org]<SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><B>On Behalf Of<SPAN 
    class=Apple-converted-space>&nbsp;</SPAN></B>Glenn Burt<BR><B>Sent:</B><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN>Monday, November 29, 2010 6:03 
    PM<BR><B>To:</B><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN>'RE-wrenches'<BR><B>Subject:</B><SPAN 
    class=Apple-converted-space>&nbsp;</SPAN>Re: [RE-wrenches] Battery Cable 
    REvistied<BR></FONT><BR></DIV>
    <DIV></DIV>
    <DIV style="page: wordsection1" class=WordSection1>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-FAMILY: cambria, serif; FONT-SIZE: 10pt">Hi 
    Ray,<o:p></o:p></SPAN></DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-FAMILY: cambria, serif; FONT-SIZE: 10pt"><o:p></o:p></SPAN>&nbsp;</DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-FAMILY: cambria, serif; FONT-SIZE: 10pt">I have for my last 2 
    battery jobs used the Cobra X-Flex in 2/0 size with MTW 
    rating.<o:p></o:p></SPAN></DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-FAMILY: cambria, serif; FONT-SIZE: 10pt"><BR>At the battery end 
    I have found the Thomas &amp; Betts 54163-TB lugs, available at my local 
    Grainger store to be a good match both mechanically and specification wise 
    (also the correct hole size for M8 terminals in my Concorde AGMs).<BR>On 
    the usual electrical equipment end, I use a Greaves Shoo-Pin<SPAN 
    class=Apple-converted-space>&nbsp;</SPAN></SPAN><SPAN 
    style="FONT-FAMILY: cambria, serif; FONT-SIZE: 10pt">PT131FX20 as the 
    appropriate reducer to a THHN stranding #</SPAN><SPAN 
    style="FONT-SIZE: 10pt">2/0 size (available through our local Graybar store, 
    drop shipped to my office). Because I am using a Sunny Island, of course 
    nothing #2 fits so I have two Polaris style connectors in the trough below 
    the SI where I switch from the Shoo-Pins to four #1 THHN to go up into the 
    SI batt terminals (two conductors per pole).<o:p></o:p></SPAN></DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-SIZE: 10pt"><o:p></o:p></SPAN>&nbsp;</DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-SIZE: 10pt">In fact, I am wrapping up one of these installs 
    right now.<o:p></o:p></SPAN></DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-SIZE: 10pt"><o:p></o:p></SPAN>&nbsp;</DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-SIZE: 10pt">Dont know if this helps,<o:p></o:p></SPAN></DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-SIZE: 10pt"><o:p></o:p></SPAN>&nbsp;</DIV>
    <DIV 
    style="MARGIN: 0in 0in 0pt; FONT-FAMILY: 'Times New Roman', serif; FONT-SIZE: 12pt"><SPAN 
    style="FONT-SIZE: 10pt">-Glenn</SPAN></DIV></DIV>_______________________________________________<BR>List 
    sponsored by Home Power magazine<BR><BR>List Address:<SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><A 
    style="COLOR: blue; TEXT-DECORATION: underline" 
    href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
    &amp; settings:<BR><A style="COLOR: blue; TEXT-DECORATION: underline" 
    href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive:<SPAN 
    class=Apple-converted-space>&nbsp;</SPAN><A 
    style="COLOR: blue; TEXT-DECORATION: underline" 
    href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</A><BR><BR>List 
    rules &amp; etiquette:<BR><A style="COLOR: blue; TEXT-DECORATION: underline" 
    href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</A><BR><BR>Check 
    out participant bios:<BR><A style="COLOR: blue; TEXT-DECORATION: underline" 
    href="http://www.members.re-wrenches.org/">www.members.re-wrenches.org</A><BR><BR></DIV></SPAN></BLOCKQUOTE></DIV>
  <DIV>&nbsp;</DIV></DIV></DIV>
  <DIV>&nbsp;</DIV>
  <HR>
  _______________________________________________<BR>List sponsored by Home 
  Power magazine<BR><BR>List Address: <A 
  href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
  &amp; settings:<BR><A 
  href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant bios:<BR>www.members.re-wrenches.org<BR><BR></DIV>
  <DIV style="FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: 12pt">
  <P>Northern Arizona Wind &amp; Sun - Electricity from the sun since 
  1979<BR>--------------------------------------------------------------------<BR><A 
  href="http://store.solar-electric.com/">Online Solar Store</A><BR><A 
  href="http://www.wind-sun.com/ForumVB/">Free Solar Discussion 
  Forum</A><BR>--------------------------------------------------------------------</P></DIV></DIV></DIV></DIV>_______________________________________________<BR>List 
  sponsored by Home Power magazine<BR><BR>List Address: <A 
  href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</A><BR><BR>Options 
  &amp; settings:<BR><A 
  href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</A><BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></DIV>
<DIV>&nbsp;</DIV></DIV></DIV>
<P>
<HR>
_______________________________________________<BR>List sponsored by Home Power 
magazine<BR><BR>List Address: RE-wrenches@lists.re-wrenches.org<BR><BR>Options 
&amp; 
settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
participant bios:<BR>www.members.re-wrenches.org<BR><BR></DIV>
<DIV style="FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: 12pt">
<P>Northern Arizona Wind &amp; Sun - Electricity from the sun since 
1979<BR>--------------------------------------------------------------------<BR><A 
href="http://store.solar-electric.com/">Online Solar Store</A><BR><A 
href="http://www.wind-sun.com/ForumVB/">Free Solar Discussion 
Forum</A><BR>--------------------------------------------------------------------</P></DIV></DIV></DIV></BODY></HTML>