Hello Wrenches,<br><br>
Looking through the archives on using a Megger&nbsp; for testing modules,
it appears that it is best to keep voltages to 500VDC.&nbsp; I read all
that I could find. <br><br>
Talking to a Sanyo representative, I was told that keeping test voltage
under 600 would not void the warranty or be an issue with UL.&nbsp; He
said they have tested Sanyo modules up to 1000 VDC with no
problems.<br><br>
As a final test on a system, I want to Megger test the array from the
terminations at the inverter.&nbsp; The approach I'd plan to use is:
<ul>
<li>Clamp the Fluke 1587 negative to the enclosuer ground.
<li>Put the positive test lead to the negative conductor from the array
and test
<li>Put the positive test lead to the positive conductor from the array
and test
</ul>All tests would be done at 500 V.&nbsp; The modules are illuminated,
but there is no significant reading from either positive or negative
terminal to ground. 
<ul>
<li>The conductors would be removed from their terminals at the inverter
and be in free air.
<li>The conductors would be continuous through the string of 10 Sanyo 210
modules.
</ul>My questions are:
<ul>
<li>Does anyone see a problem in this approach?
<li>Since the array often has 500 VDC open circuit readings and shows no
indication of a fault whatever, would this test accomplish anything more
than the standard voltage to ground tests I've already done?
<li>Is there any danger to diodes or other PV components?
</ul>Thanks in advance.<br><br>
Drake&nbsp; </body>