<DIV><FONT size=2 face=Arial>Hello Drake,</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT>&nbsp;</DIV>
<DIV><FONT size=2 face=Arial>I think you should talk to a Sanyo Solar 
engineer&nbsp;to&nbsp;get accurate information. Every Sanyo and other brand UL 
listed modules must be dielectric voltage-withstand factory tested to 2 times 
system voltage plus 1,000 volts. I hi-pot test modules&nbsp;in the factory at 
3,000 volts so they will meet UL and also IEC standards. I megger field test 
arrays at 1,000 volts to find module, connector, and wiring problems. Megging at 
500 volts is ok, but it may not reveal wire insulation problems.</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT>&nbsp;</DIV>
<DIV><FONT size=2 face=Arial>Joel Davidson</FONT></DIV>
<DIV><FONT size=2 face=Arial></FONT>&nbsp;</DIV>
<BLOCKQUOTE 
style="BORDER-LEFT: #000000 2px solid; PADDING-LEFT: 5px; PADDING-RIGHT: 0px; MARGIN-LEFT: 5px; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="FONT: 10pt arial; BACKGROUND: #e4e4e4; font-color: black"><B>From:</B> 
  <A title=drake.chamberlin@redwoodalliance.org 
  href="mailto:drake.chamberlin@redwoodalliance.org">Drake</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=re-wrenches@lists.re-wrenches.org 
  href="mailto:re-wrenches@lists.re-wrenches.org">RE-wrenches</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Wednesday, November 17, 2010 7:36 
  AM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> [RE-wrenches] Megger for array 
  testing</DIV>
  <DIV><BR></DIV>Hello Wrenches,<BR><BR>Looking through the archives on using a 
  Megger&nbsp; for testing modules, it appears that it is best to keep voltages 
  to 500VDC.&nbsp; I read all that I could find. <BR><BR>Talking to a Sanyo 
  representative, I was told that keeping test voltage under 600 would not void 
  the warranty or be an issue with UL.&nbsp; He said they have tested Sanyo 
  modules up to 1000 VDC with no problems.<BR><BR>As a final test on a system, I 
  want to Megger test the array from the terminations at the inverter.&nbsp; The 
  approach I'd plan to use is: 
  <UL>
    <LI>Clamp the Fluke 1587 negative to the enclosuer ground. 
    <LI>Put the positive test lead to the negative conductor from the array and 
    test 
    <LI>Put the positive test lead to the positive conductor from the array and 
    test </LI></UL>All tests would be done at 500 V.&nbsp; The modules are 
  illuminated, but there is no significant reading from either positive or 
  negative terminal to ground. 
  <UL>
    <LI>The conductors would be removed from their terminals at the inverter and 
    be in free air. 
    <LI>The conductors would be continuous through the string of 10 Sanyo 210 
    modules. </LI></UL>My questions are: 
  <UL>
    <LI>Does anyone see a problem in this approach? 
    <LI>Since the array often has 500 VDC open circuit readings and shows no 
    indication of a fault whatever, would this test accomplish anything more 
    than the standard voltage to ground tests I've already done? 
    <LI>Is there any danger to diodes or other PV components? </LI></UL>Thanks in 
  advance.<BR><BR>Drake&nbsp; 
  <P>
  <HR>

  <P></P>_______________________________________________<BR>List sponsored by 
  Home Power magazine<BR><BR>List Address: 
  RE-wrenches@lists.re-wrenches.org<BR><BR>Options &amp; 
  settings:<BR>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<BR><BR>List-Archive: 
  http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<BR><BR>List 
  rules &amp; etiquette:<BR>www.re-wrenches.org/etiquette.htm<BR><BR>Check out 
  participant 
bios:<BR>www.members.re-wrenches.org<BR><BR></BLOCKQUOTE></BODY></HTML>